    Default Voltage drop in underground cable

    I have a problem with the underground wire feeding my cabana I run a 110 volt pump to water my lawn as I am on a river ,I have done this for the past twenty years . This year I plugged in the pump and nothing so I removed the gfi receptical and put my tester on the wires comming out of the ground and got a reading of 62 volts. I then went to the panel and tested from the breker to neutral and got 120 volts.I am wondering if maybe something has bitten through the neutral wire ? Is this possible I would appreciate any advice you can give thanx in advance Fred

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    A loose or corroded connection anywhere on the run might show up as a low voltage at the end. Does the cable have a ground wire? What's the voltage between hot and ground?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    My bet would be a break in the wire underground somewhere.

  4. #4
    DIY Junior Member silverfox52009's Avatar
    Join Date
    May 2012
    Location
    belleville ont. can.
    Posts
    3

    Default

    Quote Originally Posted by jadnashua View Post
    A loose or corroded connection anywhere on the run might show up as a low voltage at the end. Does the cable have a ground wire? What's the voltage between hot and ground?
    yes it does have a ground wire and the voltage between hot and ground is the same 62 volts

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    A high resistance on the feed would result in a voltage drop that is commensurate with the current draw. A high impedance voltmeter testing a circuit that is not under load usually does not give a true picture since it in and of itself, provides no current draw.

    My guess is that along with the high resistance, there is also a short to ground.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    quote; yes it does have a ground wire and the voltage between hot and ground is the same 62 volts

    That would imply a problem with the "hot' wire, not the neutral.
    Licensed residential and commercial plumber

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,652

    Default

    Quote Originally Posted by LLigetfa View Post
    My guess is that along with the high resistance, there is also a short to ground.
    I don't think that is correct.

    hj is correct.

    A short reading from Ground to Neutral is normal, at the source.

    The open is on the Hot leg, if there is a open.

    Or if the pump is trying to run, it may be locked up and not running. that could explain the voltage drop.

    You can use a light bulb for better testing under a small load.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Flickering lights on circuit with low voltage and line voltage bulbs
    By davidwie in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 04-18-2011, 07:34 AM
  2. voltage drop
    By ugabulldog in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 01-22-2011, 03:38 PM
  3. Service entrance cable size & voltage drop
    By curtherrin in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 08-24-2009, 12:47 PM
  4. Running low voltage in high voltage boxes
    By Ian Gills in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 08-22-2009, 07:27 PM
  5. Lights flicker and Voltage Drop Question
    By Pip in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 12-18-2008, 06:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •