Thread: Grounding or Bonding Jetted Bathtub

  1. #1
    DIY Junior Member seegee's Avatar
    Join Date
    May 2012
    Location
    CA
    Posts
    4

    Default Grounding or Bonding Jetted Bathtub

    Hi All,

    I'm sorry, this may have been asked before, but I want to make double/triple sure I have this right.

    I have a jetted Proflo tub that was installed in my new home. There is only 1 Romex cable to supply power and ground. There is no heater on the unit, and I am using aquapex for the water supply. There is what looks like a grounding/bonding bolt on the motor, but if I'm not using copper pipes, and there is no heater unit, is it necessary to connect anything to that bolt?

    Just want to be safe and sure. Thanks in advance.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    What does the installation manual say? My guess is that it does need to be grounded, if nothing else, but that is a guess.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    i would bet that the motor would have to be grounded, as well as hooked up to a GFCI outlet as well.

  4. #4
    DIY Junior Member seegee's Avatar
    Join Date
    May 2012
    Location
    CA
    Posts
    4

    Default

    It just says the following:

    In one area:

    Electrical Requirements
    1. ALL CONNECTIONS MUST BE GFCI (Ground Fault Circuit Interrupted) PROTECTED
    2. Whirlpool units require dedicated 20 amp, 115 volt service.
    3. A receptacle with a 20 amp configuration must be provided.
    4. See local codes for proper wire size, if not specified use #12 Copper only wire.

    In another area:

    DANGER: RISK OF ELECTRICAL SHOCK! Connect only to a separate circuit protected by a ground fault circuit
    interrupter (GFCI).
    • The unit must be connected to a circuit interrupter (GFCI). Such a circuit is provided by the installer and should be
    tested on a routine basis. To test the GFCI push the test button. The GFCI should interrupt power. Push the RESET
    button. Power should be restored. If the GFCI fails to operate in this manner, there is a ground current flowing, indicating
    the possibility of an electrical shock. Do not use this unit. Disconnect the unit and have the problem corrected
    by a qualified service representative before using.

    Another area:
    Electrical connection is simply made by plugging pump cord (shipped with
    cord and plug) into specified dedicated 120V/20A GFCI outlet.

    IT IS CONNECTED TO A GFCI CIRCUIT.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Well, electrically speaking, a gfci doesn't even require a ground, although it does give a safety path to trip the CB if there's some types of shorts.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    The lug on the motor has nothing to do with grounding. The grounding is accomplished by the bare copper wire in the cable supplying the receptacle.

    The lug on the motor is for bonding any and all metal parts in the area of the tub together. If there are no metal water pipes and no other metal that can be touched while in the tub then it gets hooked to nothing

  7. #7
    DIY Junior Member Chris DeLong's Avatar
    Join Date
    May 2012
    Location
    New Jersey
    Posts
    2

    Default

    The bonding lug on the motor is for bonding any metal parts in contact with the circulating water only, In my experience, I have never seen a tub plumbed with anything but plastic... so IMO you don't have to bond anything.

  8. #8
    DIY Junior Member seegee's Avatar
    Join Date
    May 2012
    Location
    CA
    Posts
    4

    Default

    Quote Originally Posted by jwelectric View Post
    The lug on the motor has nothing to do with grounding. The grounding is accomplished by the bare copper wire in the cable supplying the receptacle.

    The lug on the motor is for bonding any and all metal parts in the area of the tub together. If there are no metal water pipes and no other metal that can be touched while in the tub then it gets hooked to nothing
    Yes, there are no metal water pipes, but the plastic water pipes of course connect to the tub spout and hot/cold control knobs, which are metal. Those don't need bonding, right?

  9. #9
    DIY Junior Member seegee's Avatar
    Join Date
    May 2012
    Location
    CA
    Posts
    4

    Default

    bump... just wanted to know this last piece...

    Yes, there are no metal water pipes, but the plastic water pipes of course connect to the tub spout and hot/cold control knobs, which are metal. Those don't need bonding, right?

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    No bonding required

Similar Threads

  1. Grounding Whirlpool Tub Motor and Heater - Bonding Panel to Electric Water Heater
    By chuck b in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 02-06-2012, 09:01 AM
  2. Copper pipe grounding/bonding - how to?
    By Copper Bahamas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-31-2010, 08:56 AM
  3. bonding/grounding copper pipes
    By reed50 in forum Electrical Forum discussion & Blog
    Replies: 32
    Last Post: 11-24-2010, 10:31 AM
  4. bonding/grounding and pex
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 10-23-2009, 05:39 AM
  5. Grounding, bonding, potential??
    By hammerslammer in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 08-21-2007, 09:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •