    Installing Direct-Wired waterers in horse barn (breaker to waterer directly)....
    I want to install GFCI breakers, but I'm concerned about the distance with 1 waterer.

    2 waterers will be about 75' from subpanel.
    1 waterer will be about 350'

    Do I need to install a second subpanel for the waterer 350' away?
    What is the distance the GFCI breaker will correctly protect without false tripping/issues?

    Thanks again!

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    I very highly recommend that you get a copy of American Society of Agricultural and Biological Engineers before going any future in your endeavors for the sake of your livestock.

    To answer your question, it doesn’t matter the distance as to the tripping of the GFCI device. What distance will do is cause a voltage drop which will lead to failure of the equipment which leads to shock to the animal or even death. The installation of remote panels will have no effect on voltage drop therefore they are not needed. What is needed if a calculation for voltage drop.

    One thing to keep in mind is the fact that I have been in the electrical field for more than 40 years and have been raising horses all my life. I have had as many as 26 at one time and now own 6. I have tried every trick known to mankind and have always come back to the old way of filling the tanks and breaking ice by hand. Once you lose a couple of animals you will learn.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    You can plug directly into a GFCI outlet and get false tripping, so distance is not a consideration. What is a consideration is how far you want to walk to reset the GFCI when you discover the waterer is not working, and WILL you have anything to tell you the waterers are not functioning, such as a "pilot light", unless you check them periodically?
    Licensed residential and commercial plumber

  4. #4
    DIY Junior Member hagler's Avatar
    Join Date
    Aug 2010
    Location
    NY
    Posts
    16

    Default

    Quote Originally Posted by jwelectric View Post
    I very highly recommend that you get a copy of American Society of Agricultural and Biological Engineers before going any future in your endeavors for the sake of your livestock.

    To answer your question, it doesn’t matter the distance as to the tripping of the GFCI device. What distance will do is cause a voltage drop which will lead to failure of the equipment which leads to shock to the animal or even death. The installation of remote panels will have no effect on voltage drop therefore they are not needed. What is needed if a calculation for voltage drop.

    One thing to keep in mind is the fact that I have been in the electrical field for more than 40 years and have been raising horses all my life. I have had as many as 26 at one time and now own 6. I have tried every trick known to mankind and have always come back to the old way of filling the tanks and breaking ice by hand. Once you lose a couple of animals you will learn.
    JW...I can figure for voltage drop....I have a question for you --- would a junction box make sense here? and forget about a subpanel.....Run #6 or #8 wire from main panel to an outdoor junction box? and then wire to two more junction boxes for each waterer?
    I have three separate fenced in areas for the horses...where would you install/mount the box if you think this is an option?
    Also, would you install inline GFCIs for this configuration (or 1 inline GFCI at the first junction)...and how/where would you mount them? (would have to be outdoor inline GFCIs obviously)
    Thanks for the input

  5. #5
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Should be able to open ice with a little aquarium bubbler brought in on rubber hose. No electrical in tank issues.

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by hagler View Post
    JW...I can figure for voltage drop....I have a question for you --- would a junction box make sense here? and forget about a subpanel.....Run #6 or #8 wire from main panel to an outdoor junction box? and then wire to two more junction boxes for each waterer?
    I have three separate fenced in areas for the horses...where would you install/mount the box if you think this is an option?
    Also, would you install inline GFCIs for this configuration (or 1 inline GFCI at the first junction)...and how/where would you mount them? (would have to be outdoor inline GFCIs obviously)
    Thanks for the input
    Horses are curious by nature. Anything strange they will eventually start messing with it even chewing on it if they like the taste.

    However I wired the circuit I would ensure that no part is within their reach. Should you have a wind sucker and it can reach the post, box, or panel you are guaranteed a dead horse.

    You seem to be dead set on installing these but I come once again trying to convince you to think of other methods. When new these things work great but they age at a very fast rate and become damaged. You will spend endless hours resetting the GFCI device to the point they start to fail. At this point the horse has already been hit and it takes little current to train the horse to not use them. One horse minus water equals a vet bill.

    The ones I installed were removed in less than 6 months. I then tried the ball cock and it failed quickly. All I had was a big mud hole in front to the tub where the failures let water flow all day.
    It didn’t take me long to figure out that I was feeding the horse twice daily so he got water twice daily. His tub was emptied and washed twice daily, he like that a lot better than standing in mud or jagged ice to drink.

Similar Threads

  1. GFCI Breaker (no GFCI outlets) not working, but not tripped
    By dmotes in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 12-02-2010, 11:18 AM
  2. Pool tripping GFCI breaker
    By killavolt in forum Electrical Forum discussion & Blog
    Replies: 20
    Last Post: 08-06-2009, 07:46 PM
  3. GFCI Breaker vs. Receptacles
    By Washer Woman in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 12-28-2007, 02:25 PM
  4. GFCI outlet AND breaker?
    By hans_idle in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 12-17-2007, 01:25 PM
  5. GFCI Breaker
    By cameron in forum Pumps and Tanks Well Forum & Blog
    Replies: 20
    Last Post: 05-07-2007, 05:35 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •