    I can't locate where existing vent is, run vent line up to the attic means to do a lot of demolition. When you said " 6 " above the highest fixture' did you mean fixture on the same floor or all building?

  2. #17
    DIY Junior Member PapaFi's Avatar
    Join Date
    Apr 2012
    Location
    Illinois
    Posts
    10

    Default

    Will AAV solve the issue with vent?

  3. #18
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    The general rule is that once a line is used as a drain, it cannot be a vent. To keep a vent a vent, you need to connect one from below high enough so it can't inadvertently become a drain...so, code requires it to be at least 6" above the highest fixture. So, no, that isn't the fixtures in the basement...the connection point for a vent must be above the highest thing above it. Depending on how the vents are run in your house, you might have one for the first floor stuff, and a second one for the second floor stuff, or they both combine into one before going through the roof. You could make one for the basement stuff, or, combine them in an approved manner. Basically, if the first floor is properly vented, you'd only need to go the 6" above that floor's highest fixture flood plane (or 42"), since a vent is a vent. In an older house, though, they didn't always do it such that it would pass codes today, so you might have to go higher to make the new stuff pass.

    AAV's are a mechanical air vent - they let air in, not out. They are not always allowed, and even if allowed, the inspector may give you hassles if there's a way to do it 'right' (i.e., without one). depending on the layout, an AAV may or may not be acceptable. Where ever you do install one, though, it must be accessable, not hidden in a wall without an access plate, since it will eventually fail and need to be replaced.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #19
    DIY Junior Member PapaFi's Avatar
    Join Date
    Apr 2012
    Location
    Illinois
    Posts
    10

    Default

    Thanks! I can assume that they are vents behind toilets on 1st or 2nd floors, but can't see'm. All pipes in the basement are exposed and came to the main stock, but are they all drains?

  5. #20
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,157

    Default

    The easiest place to run the vent up from the basement is determined by how the walls are positioned in the floors above. The vent can go straight up pretty much anywhere from the basement, it does not have to be directly above the fixture plumbing.

    In many houses a new vent can be brought up through an existing interior wall into the attic or through the roof with no demo at all. In a 2-story, sometimes it is easier to run up through the corner of an existing closet or pantry and then box it in if needed. People run new pipes and wires through walls every day. You might need some help with the job, but it can be done.