Thread: outdoor to indoor wiring question.

  1. #1

    Default outdoor to indoor wiring question.

    I have mounted an outdoor box on an exterior wall and have drilled a hole for a conduit nipple to go through the wall. Can I put Romex through that hole and continue the Romex to the nearest electrical box inside? The wire would be coming stright through the nipple and then immediately by stapled to the nearest studs on the way to the electrical source. Thanks.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    The nipple will create a "sharp edge" and the Romex® will not be anchored so it could rub against the raw edge. Use a shorter nipple, then a threaded coupling, and a wire clamp/connector into it. Slide the wire through it and tighten the clamp screws.
    Licensed residential and commercial plumber

  3. #3
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    HJ is right, but:

    There are two considerations when wire enters a box, generally speaking.

    Abrasion must be avoided. On MC there are little red plastic anti-short bushings. For MC (the stuff you are asking about) there are rated plastic and metal devices that will fit the box and protect the sheathing from abrasion. There must be a dozen different concepts on the market.

    The other issue when any wire or cable comes into a box is that it cannot be pulled back out. For MC the various devices that prevent abrasion also clamp the cable.

    Some of the plastic boxes on the market have no provision to hold the wire from being pulled out, and when used it is expected that the wire be stapled to the framing within 8".

    There are anti-short bushings (collars) that screw over the threads of rigid conduit and present the wires or cable with a much smoother surface to work against.

    All that said, I could imagine replacing the metal conduit that you have with some plastic, and stapling the wire down if you can get at it. Or use a plastic nipple for the second box (the source) that has a good grab on the wire.

    Make sure that you have enough room in the source box,

    Remember: the sheathing must be visible in the box. 1/4 to 1/2 inch is expected.

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,134

    Default

    If the nipple is EMT conduit, there is a standard EMT to NM (Romex®) fitting which clamps the NM cable and circumvents the need to use bushings. They are not uncommon, as I get them from the local big-box store.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Homeownerinburb View Post
    HJ is right, but:

    There are two considerations when wire enters a box, generally speaking.

    Abrasion must be avoided. On MC there are little red plastic anti-short bushings. For MC (the stuff you are asking about) there are rated plastic and metal devices that will fit the box and protect the sheathing from abrasion. There must be a dozen different concepts on the market.
    First the original poster is talking about Non-Metallic cable not Metal-Clad cable

    Second there is not requirement to use the anti-short bushing for MC. They are required for Armored Cable or AC cable
    See 320.40 and 330.40

  6. #6
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    WHY the nipple at all?? Just bring the NM into the back of the box. Make sure to seal around the box really well.

  7. #7
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    First the original poster is talking about Non-Metallic cable not Metal-Clad cable

    Second there is not requirement to use the anti-short bushing for MC. They are required for Armored Cable or AC cable
    See 320.40 and 330.40
    No "requirement", but personally, I would not skip them. And the fact that there is always a bag of bushings with the stuff when I buy it suggests to me that I am not alone.

    I brought up the MC in order that the OP would understand that each system has its requirements; I could have been more verbose, but my post was pretty long as it stood.

  8. #8
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by Speedy Petey View Post
    WHY the nipple at all?? Just bring the NM into the back of the box. Make sure to seal around the box really well.
    Broadly speaking, there needs to be SOME sort of chafe protection and strain relief, to be legitimate. I assume you mean to use a connector of some sort. The OP might not understand that if you are not explicit.

    If the box is some sort of cast Bell box with threaded holes, a chase nipple could be screwed in and that would resolve the chafe requirement. A staple to framing within 8" would give you strain relief, I suppose. This would permit a pretty discrete hole in the wall.

    Are we talking about what is safe, or what is perfectly to code? I am sure there are inspectors who would OK the above, and others who would flag it.

    Heck, if the hole in the wall is big enough for a metal connector with a screwed down strap to grab the NM, then all is good, your point to seal the hole in the wall is the necessary cherry on the sundae.

  9. #9
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    When I say "just bring the NM into the back of the box" I mean properly, with an NM connector.

  10. #10
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by Speedy Petey View Post
    When I say "just bring the NM into the back of the box" I mean properly, with an NM connector.
    And I assumed as much.

  11. #11
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Homeownerinburb View Post
    Are we talking about what is safe, or what is perfectly to code? I am sure there are inspectors who would OK the above, and others who would flag it.
    And those outlined in red above would be wrong and wouldn't have ground to stand on

  12. #12
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    And those outlined in red above would be wrong and wouldn't have ground to stand on
    Yes. And some days it is just easier to give the damned inspector what he wants and get on with the job. As long as it is not going to cost me real money and time, and the job is going to be just as safe, I have been known to swallow it. You, jw, are qualified to teach people stuff. I have yet to meet an inspector who was ready to accept that I was going to teach him or her anything.

    Actually, I did have a pretty good back and forth with a woman who worked for Los Angeles. We agreed on a solution to a problem that cut the distance I was running a service conduit for a 90 amp circuit from about 250' to about 100'. But I would not say that I taught her anything.

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    1. I have been teaching licensing prep and inspectors for more than 12 years now. In each class I tell the students that when the contractor and inspector disagee that the learning process begains for one or the other if not both.

    With inspectors they take an oath to uphold the codes as written and are not allowed to inject their opinions for any reason.

    I also explain that the remark that it is easier to just agree with the inspector is a good way to land oneself in court. As a licensed contractor I am bound by law to make a compliant installation weather the inspector agrees with me or not.

    The use of antishort bushings on MC cable is not required therefore I do not use them. Using them can impede the heat of the conductors as the MC already comes with a liner in the jacket of the sheathing.
    Should someone tell me that I have to use them I promise they will be standing in front of the board that issued them their certification.

    My profession is not up to give away to please an inspector when that inspector is wrong. My profession mandates that I address an inspector that is wrong and not to give in to his/her wishes. I address the inspector in a professional manner and do not ever give them something they want just because they want it.

    I demand that any inspector show me in writing just what they say I have done wrong and if they can't then I am not wrong. This is a two way street that humans walk and as humans we are all subject to mistakes, therefore when two disagree it is part of a learning process.
    Last edited by jwelectric; 04-19-2012 at 10:38 AM. Reason: speling

  14. #14
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    JW,

    You're persuasive. I'll keep that in mind.

Similar Threads

  1. Outdoor Shower/Indoor Bathroom Problem...
    By geosbride in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 09-14-2011, 06:08 AM
  2. Best solution for outdoor wiring
    By TequilaMB in forum Lawn Care/Landscaping
    Replies: 3
    Last Post: 06-19-2010, 08:05 AM
  3. Outdoor spa wiring questions
    By MJ32V in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 05-07-2008, 04:10 PM
  4. Outdoor wiring of Christmas lights
    By Needing Advice in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 01-19-2008, 01:07 PM
  5. Outdoor faucet won't drain even indoor valve is shut off
    By goldfish_tt in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-28-2006, 07:57 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •