    Default PRV placement relative to ball-valve

    Does it matter if pressure reducing valve is placed before or after the building supply main on/off ball valve?

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    No, but it is easier to service and replace if it is after the valve.
    Licensed residential and commercial plumber

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Seems to me the ball valve should shut everything off, so I put my valve where the supply line enters the house which is about 4 feet above the basement floor. The PRV is a couple of feet above that. This is one reason why I can't understand why someone would put their PRV at the meter.

  4. #4
    Plumber Winslow's Avatar
    Join Date
    Dec 2005
    Location
    Hawaii
    Posts
    450

    Default

    the valve should always be placed first.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    When the PRV is at the meter it is to keep the high pressure out of the pipe to the house. SInce there is a valve at the meter, the PRV can be anywhere after the meter, regaridless of where the house valve is.
    Licensed residential and commercial plumber

  6. #6
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    HJ is of course correct, but if the supply line to the house is in such poor condition it can not withstand the high pressure, you will have a supply line problem in you very near future.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    It does not have to be "poor", the main pressure could be so high, (which is why the PRV is needed), that it exceeds the recommendation for the plastic line used. Or someone may not trust the plastic to not fail at city pressure.
    Licensed residential and commercial plumber

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,433

    Default

    While maybe not common, there are places where you need TWO PRVs, plumbed in series to drop the pressure to an acceptable level. So, if it was REALLY high, the utility might get it down to very high, then let you deal with it to drop it further, if needed. There's a limit on how much a prv can drop the pressure.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Ball valve
    By novice-man in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-06-2009, 09:28 PM
  2. Combo ball valve/check valve for ejector pump...
    By hhcibtpaun in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 06-17-2009, 12:27 PM
  3. check valve placement
    By msgale in forum Boiler Forum
    Replies: 8
    Last Post: 06-13-2009, 03:34 AM
  4. Valve placement
    By wayup in forum Irrigation / Sprinkler Forum
    Replies: 5
    Last Post: 04-27-2009, 10:10 AM
  5. Check valve placement?
    By MaxBlack in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 02-12-2007, 05:51 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •