    Default Double Tap Question

    I understand is it not acceptable and not to code to put multiple neutrals together on one neutral bus lug, unless the manufacturer of the box specifically allows it.
    I am a realtor and see a lot of home inspections. Almost all of the homes around here, Central NJ, that are in the 20 to 30 year age range, have all or most of the neutrals on one lug. Many of these boxes, including my own home, have not been touched since the house was built and still have the approval sticker on them from when they were originally inspected.
    So my question is, has something changed? Was it acceptable practice to do this before? Did the code change, if so when?
    I am just curious to know why I see so many homes with this that were inspected and approved.
    Anybody know? Thanks.

  2. #2

    Default

    Hello, at that time code allowed that. It is no longer code to do that, but you are grandfathered in. Should the panel be changed it wouldn't be allowed. I also, see it, too.

    You are allowed to have more than one wire but, you won't see 15 or 20 altogether. I am thinking that is what you are seeing. Some city could require one wire per lug, but that is something the city would require and not the NEC.

    I might be wrong but a double tap would be a wire connected to a part of the panel directly connected to the power pole with no protection inbetween.
    Last edited by Cookie; 04-10-2012 at 01:38 PM.

  3. #3
    DIY Junior Member centurion's Avatar
    Join Date
    Jan 2009
    Location
    New Jersey
    Posts
    10

    Default

    Quote Originally Posted by Cookie View Post
    Hello, at that time code allowed that. It is no longer code to do that, but you are grandfathered in. Should the panel be changed it wouldn't be allowed. I also, see it, too.

    You are allowed to have more than one wire but, you won't see 15 or 20 altogether. I am thinking that is what you are seeing. Some city could require one wire per lug, but that is something the city would require and not the NEC.

    I might be wrong but a double tap would be a wire connected to a part of the panel directly connected to the power pole with no protection inbetween.
    Thanks. If it is true that this was allowed by code before, does anyone know when it was changed?

  4. #4

    Default

    Other than that of the manufacturer's listing and instructions, I would think, around 2002, perhaps. I might be wrong, but, what matters is the code of today. JW would know.
    Last edited by Cookie; 04-10-2012 at 02:32 PM.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Cookie View Post
    Other than that of the manufacturer's listing and instructions, I would think, around 2002, perhaps. I might be wrong, but, what matters is the code of today. JW would know.
    And so would Cookie

    Panelboards was moved from 384 to 408 during the 2002 code cycle when 408.21 was included to mandate one neutral for one screw. Prior to 2002 we used the number of conductors outlined on the label in the panel. As long as they were the same size some panels would allow up to five under certain screws.

  6. #6
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    to mandate one neutral for one screw.
    Would it not be correct to say that the code now insists on one wire per screw in every application?

    I cannot think of any place in a residential (what I mostly work on) system where I would be permitted to have two wires at one screw, at all.

    That is not to say that I never stuff a grounding wire from a length of NM under the same screw in the buss as another. But I should not.

  7. #7
    DIY Junior Member centurion's Avatar
    Join Date
    Jan 2009
    Location
    New Jersey
    Posts
    10

    Default

    Quote Originally Posted by jwelectric View Post
    And so would Cookie

    Panelboards was moved from 384 to 408 during the 2002 code cycle when 408.21 was included to mandate one neutral for one screw. Prior to 2002 we used the number of conductors outlined on the label in the panel. As long as they were the same size some panels would allow up to five under certain screws.
    Thanks. This is the information I was looking for.

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Homeownerinburb View Post
    Would it not be correct to say that the code now insists on one wire per screw in every application?

    I cannot think of any place in a residential (what I mostly work on) system where I would be permitted to have two wires at one screw, at all.

    That is not to say that I never stuff a grounding wire from a length of NM under the same screw in the buss as another. But I should not.
    In a panel it is permissible to land more than one equipment grounding conductor under one screw. Look at the label in the panel for more information.

  9. #9
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by jwelectric View Post
    In a panel it is permissible to land more than one equipment grounding conductor under one screw. Look at the label in the panel for more information.
    OK, when next I get deep into one.

Similar Threads

  1. Double wye question
    By Cekrauss in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 04-21-2011, 05:21 PM
  2. Double Lav drain question
    By mr.t in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 01-14-2011, 02:19 PM
  3. Another double vanity sink drain question
    By suntan in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-02-2009, 05:48 AM
  4. Yet another single to double vanity question
    By lojoma in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 30
    Last Post: 08-25-2007, 08:19 AM
  5. Double kitchen sink drain question
    By SteveOr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 05-10-2006, 07:47 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •