    Any thoughts on these?
    I haven't used one to date. Am considering using one for a system consisting of two zone infloor heat (concrete basement slab and garage slab) and DHW requirements, and possibly hydronic air handler in future if second story requires supplemental heat...
    thanks
    Jan 2009
    What is your design condition heat load? What's the BTU/hr out of the proposed air handler?
    The minimum nominal output of the would be about my peak design heat load, in a climate similar to most southern Ontario locations, and I'd almost never get the benefits of modulation out of a beast that size. It's almost certainly oversized for any one of your zones, but the thermal mass of the slabs may protect it from short-cycling it to death on zone calls. At max output it's more than 4x oversized for my 99% design condition whole house heat load, and enough heat to run 3 low-flow showers continuously forever.
    All good heating designs start with a room-by-room/zone-by-zone heat loss calculation at the outside design temperature for your location. Sizing the boiler appropriately for both the peak & average loads as well as the output of the heat-emitters can make a huge difference in comfort & efficiency, and oversizing the boiler is the enemy of both.
    New construction, or retrofit?
  1. Bosch Greenstar Boilers
    By Maxadine1 in forum Boiler Forum
    Last Post: 03-23-2012, 07:01 AM
  2. Bradford White Combi M2CTW75T10CN12
    By dan87951 in forum Water Heater Forum, Tanks
    Last Post: 01-11-2011, 11:28 PM
  3. Recommendation to replace Heatmaker Combi Boiler
    By sagepatrol in forum Boiler Forum
    Last Post: 10-08-2009, 10:50 AM
  4. bradford white combi anode
    By ginahoy in forum Water Heater Forum, Tanks
    Last Post: 09-13-2009, 05:09 PM
  5. Adding booster pump to combi boiler?
    By dubman in forum Boiler Forum
    Last Post: 03-15-2009, 05:21 AM