Thread: Marathon should the lower element run all the time

  1. #1
    DIY Junior Member fcbclan's Avatar
    Join Date
    Mar 2012
    Location
    Forest City, Iowa
    Posts
    12

    Default Marathon should the lower element run all the time

    I have a marathon question should the lower element run all the time, upper element cycles on and off but lower element never seems to stop, except when upper element cycles on. Maybe I should turn up top thermostat to above the lower one to see if the lower thermostat ever reaches temp and trips off. I am thinking the thermostat is bad and stuck on. Any help would be appreciated.

  2. #2
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Has the T&P valve operated? Do you have a leak on the hot side water system? How are you determining the lower element continues to run? Do you have a voltage/clamp around volt meter? Are all the screw terminals tight and corrosion free? Dont electrocute yourself.

    Has the high limit tripped on the top thermostat?

    lets play 50 questions. LOL
    Last edited by Hackney plumbing; 03-24-2012 at 12:01 PM.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    If the lower element was always on, the safety relief T&P valve would be open since you'd eventually boil the water in the tank, and before that, you'd notice that it was VERY hot. On most electric WH, only one element is on at a time, but that doesn't mean you can't measure voltage, just like you can at a switch that is off.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Lets say they can be both on by design. I have 5000 watt elements in a little 30 gallon rig and keep them both on with their thermostats at 145 or so. heats the house.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,632

    Default

    If both elements operate at the same time, without rewiring the thermostats, it will draw about 40+ amps which will overload the common wiring for a water heater. If the lower element did not turn off, then the ECO would trip and shut the entire heater down. If you diagnosis is correct, the lower element is heating water, but it is going somewhere, the most common place is under the floor because of a a cracked hot water pipe. But if your lower element is burned out, it will ALWAYS have voltage to it, but it is NOT USING it. How are you testing it, with a voltmeter or a clamp around ammeter. You need both to test a water heater element.
    Licensed residential and commercial plumber

Similar Threads

  1. GE electric water heater, lower element not in use?
    By Mastiff in forum Water Heater Forum, Tanks
    Replies: 5
    Last Post: 01-29-2012, 08:52 PM
  2. Thermostats : Dual Element in a Single Element Water Heater
    By Synicasm in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 11-09-2009, 01:35 PM
  3. Single element thermostat on dual element heater
    By garycase in forum Water Heater Forum, Tanks
    Replies: 9
    Last Post: 07-31-2009, 04:51 PM
  4. Lower Power element for small GE water heater?
    By sedin26 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 06-02-2008, 09:12 PM
  5. New sink is lower...need to lower drain?
    By plumbbob in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 11-07-2004, 02:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •