Thread: Electrical Wiring Capacity / HEAT

  1. #1
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default Electrical Wiring Capacity / HEAT

    OK. Boxes have max capacity fill, conduit, etc.

    What about MC/AC wire. Is the *clad* good enough on how much *capacity* the wire inside needs.


    I plan to put a 4" square box on a wall that has been mudded/rocked over.
    It's roughly 1 1/4"+ in depth so to make this fairly seamless, I plan to channel out the wall, run the BX in the channel and then plaster the BX in place. I plan to take a chipping hammer and chip out the area where the box will be so it sits flush with the wall (poured concrete wall).

    Is is ~okay~ to bury the wire in plaster ?
    Or does it need room/air around it.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    If you do not overload it, it should NOT overheat or need ventilation other than what flows through the armored covering.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member michielsemma's Avatar
    Join Date
    Mar 2012
    Location
    Utah
    Posts
    6

    Default

    Breaker needs to be a 40 amp and wire needs to be 8 AWG. A 30 amp breaker will nuisance trip on hard starts. Full load amps is when it's running at full capacity. Starting current is a lot higher than FLA.

    Check to see what size the main wires are on the unit where you are supposed to make your connection from the breaker panel. If the wires are bigger than 10awg or add up to be bigger than 10awg then you cannot use a 30 amp breaker.

    Look for a rating of minimum circuit ampacity on the unit as well.

    Your fuses or breakers are designed to protect the wiring in your home from short circuits and overheating and starting a fire. They are not designed to protect your appliances. You cannot legally run a 10awg wire to a 50 amp breaker.

  4. #4
    In the Trades Jerome2877's Avatar
    Join Date
    Aug 2009
    Location
    BC
    Posts
    384

    Default

    http://answers.yahoo.com/question/in...2072140AAb12T7

    Busted again copy/paste man..... Your a joke!

  5. #5
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by michielsemma View Post
    Breaker needs to be a 40 amp and wire needs to be 8 AWG. A 30 amp breaker will nuisance trip on hard starts. Full load amps is when it's running at full capacity. Starting current is a lot higher than FLA.

    Check to see what size the main wires are on the unit where you are supposed to make your connection from the breaker panel. If the wires are bigger than 10awg or add up to be bigger than 10awg then you cannot use a 30 amp breaker.

    Look for a rating of minimum circuit ampacity on the unit as well.

    Your fuses or breakers are designed to protect the wiring in your home from short circuits and overheating and starting a fire. They are not designed to protect your appliances. You cannot legally run a 10awg wire to a 50 amp breaker.
    And what does that have to do with ChefWong's question anyway? he never mentioned the load as far as I can see.

    As jerome said, just a copy and paste job from you
    I am definitely not a pro plumber, but I am a pro crastinator

Similar Threads

  1. Faulty Wiring - Electrical Fire
    By Dan W in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 08-17-2008, 09:18 AM
  2. electrical wiring deficiency?
    By trackerxx in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 02-28-2008, 10:35 PM
  3. Best Drill Bit for Electrical Wiring
    By Lakee911 in forum Electrical Forum discussion & Blog
    Replies: 20
    Last Post: 01-19-2008, 09:37 PM
  4. Dryer wiring = no heat.
    By MuckSavage in forum Electrical Forum discussion & Blog
    Replies: 18
    Last Post: 07-11-2007, 05:14 PM
  5. Heat pump selection (electrical)
    By Jendoyle in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 03-21-2007, 07:46 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •