Thread: Bathroom remodel > Horizontal wet venting questions with drawings

  1. #1
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default Bathroom remodel > Horizontal wet venting questions with drawings

    Hi,

    i'm about to remodel my master bathroom and will be re-doing plumbing. The layout will be the following:
    Name:  ScreenHunter_01 Mar. 09 13.24.jpg
Views: 1657
Size:  38.3 KB
    Shower, sink, WC and bathtub.

    Here are drawings of what i was thinking of for the rough-in:
    Name:  ScreenHunter_02 Mar. 09 13.48.jpg
Views: 1285
Size:  28.8 KB
    Name:  ScreenHunter_02 Mar. 09 13.25.jpg
Views: 1302
Size:  42.7 KB

    *** btw, i know the wye fittings for shower and lavatory are 3x3x3in while they should not. I could not find/draw.

    The 3 inches drain cannot be moved and sits below a window. For that reason, there's a 3inches horizontal wet vent that goes left until it meets a thick wall then straight up through the roof. This is the actual drainage setup except we don't have a separate shower and fixtures are moved around a little.

    So the plan is:
    Shower: horizontal connection to 3 in wet vent through Wye, vented by the 3 in vent.
    Sink: horizontal connection to 3 in wet vent through Wye, vented with the use of an AAV. The reason is that there's an exterior wall behind and i live in a cold climate where it can drop to -30 in winter. I think a vent in an exterior wall is not a good idea.
    WC: horizontal connection to 3 in wet vent through Wye.
    All of the above connected to 3 in drain through a double sanitary tee. The shower is about 7 feet from the 3in stack.

    The bathub is on the other side of the 3in stack and would be connected in the 3in sanitary tee with a 1 1/2 to 3in adaptor. It would have a proper vent going 45degrees up until it reaches a wall then up in the attic. The vent would then go horizontal until it meets the 3in vent going through the roof.

    I would like to know if this design make sense, what could i do to improve or am i completly wrong?

    More specific questions:
    1. is the 3in vent going straight up is too far (8 feet) from the stack to act as part of a wet vent?
    2. Can i connect the WC the way it is in the drawing?
    3. Is the double sanitary tee the proper fitting to allow the wet vented section AND the bathub to drain in the 3in stack? Can i cap the double sanitary tee as there is no pipe going up?
    3. is it ok if i use an AAV for the lavatory or i should make some kind of plumbing loop like this:
    Name:  FH03OCT_ISLANSI_01.jpg
Views: 3172
Size:  76.6 KB

    Thanks

    Father or a 3rd baby (2 weeks old)... the bathroom needs help.
    Attached Images Attached Images  
    Last edited by Bruno Carozza; 03-09-2012 at 12:04 PM.

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    If the stack to the far left has waste from the floor above then nothing is right. You can't wet vent downstream of a vertical waste stack
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    Quote Originally Posted by Tom Sawyer View Post
    If the stack to the far left has waste from the floor above then nothing is right. You can't wet vent downstream of a vertical waste stack
    The stack going up go straight across the roof. This is a second floor bathroom.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    OK, it's hard to make out but..... the lav will need it's own vent because if you drop to the floor like that you will have an S trap. Remember, anytime waste goes down, vent goes up. The shower may or may not be too far from the stack depending on your code but IPC says 6' for 2" and the UPC says 5' IIRC. The double san tee is Ok and is really OK if you use the top of it for a clean out otherwise I would rather see a double elbow there. Provided the vent next to the tub runs as you have drawn it, it will serve the tub and toilet but it's way too far from the shower.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    Quote Originally Posted by Tom Sawyer View Post
    OK, it's hard to make out but..... the lav will need it's own vent because if you drop to the floor like that you will have an S trap. Remember, anytime waste goes down, vent goes up. The shower may or may not be too far from the stack depending on your code but IPC says 6' for 2" and the UPC says 5' IIRC. The double san tee is Ok and is really OK if you use the top of it for a clean out otherwise I would rather see a double elbow there. Provided the vent next to the tub runs as you have drawn it, it will serve the tub and toilet but it's way too far from the shower.
    OK for the lav, will figure out a way to vent.
    I measured the distance from the shower wye to the stack and it is exacly 6 foot so i guess i'm "OK".

    For the remaining question, are the fittings i used to drain the toilet ok? 90 elbow to a wye then the sanitary tee... one after the other.

    Thansk a bunch!

  6. #6
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    The shower drain starts at the trap weir not the wye.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  7. #7
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    I don't know about aav in Canada. I can't believe any inspector would allow the island vent at the lav. Such techniques are reserved for situations where no proper vent is possible. Being hard to do or inconvenient does NOT qualify as "not possible".

  8. #8
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    Would it be ok to run a vent pipe in the exterior wall considering winter gets pretty cold around here?!

    What other options would i have?

    Thanks

  9. #9
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    Yep, exterior wall for a vent is fine. Most kitchen sinks have an exterior vent
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  10. #10
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    Ok, thanks!

    Do someone know about floor access panels for plumbing? I'd put one over the stack double sanitary tee for servicing. I can't find anything suitable at home depot.

    Thanks again! The old bathroom destruction starts in 3 weeks.

  11. #11
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Having proper cleanouts installed is one thing. Access through the floor to drain pipe does not make any sense. Water and drain installations should be considered "life-of-the-house" and planning for access probably causes more problems than it would solve.

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,622

    Default

    That sanitary cross would not be acceptable in most jurisdictions, and a cleanout at the second floor level is usually cosmetic, but not practical. The vent for the shower is the one going up the wall, so unless the shower is over 5' wide it is acceptable, although, some areas would have a problem with it being a horizontal vent.
    Licensed residential and commercial plumber

  13. #13
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    Ok, i guess i'll forget that idea. It really is my first big reno project and the plumbing part scares me a little. I want to DIY for the satisfaction of it. The answers i got on the post are very helpful.

  14. #14
    DIY Junior Member Bruno Carozza's Avatar
    Join Date
    Mar 2012
    Location
    Quebec, Canada
    Posts
    8

    Default

    what should i use in place of the sanitary cross? A 3in double elbow? I can only find a 2in double elbow on the HD website.

    Thanks

  15. #15
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    Yes and you will probably only find one at a plumbing supply house, not the big box stores
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. Please help me plan the DWV for my bathroom remodel... toilet venting etc
    By coalminecanary in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 08-23-2010, 02:39 PM
  2. questions about wet venting during a remodel
    By Master Brian in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 18
    Last Post: 11-15-2008, 09:42 AM
  3. Bathroom Remodel - venting questions
    By The old college try in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 02-21-2007, 06:41 PM
  4. Bathroom remodel DWV Venting
    By dw in forum Remodel Forum & Blog
    Replies: 5
    Last Post: 01-22-2007, 09:06 AM
  5. Bath remodel - venting questions
    By remodelingit in forum Remodel Forum & Blog
    Replies: 9
    Last Post: 05-22-2005, 02:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •