Thread: What components would you recommend?

  1. #1
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default What components would you recommend?

    I recently had our water retested because of a problem with our current Master NS-10T acid neutralizer / softener combination unit. The main problem with our well is an acidic pH, which has resulted in pin holes in our copper pipes that precede the softener. The NS-10 originally had calcite and it only got the pH up to 6.8, so I unscientifically added calcite / corrosex mix (I didn't spot the ratio on the bucket) and some remaining calcite from the original cube of mineral each time I filled the neutralizer. No blue stains in the sinks, but I haven't measured the pH after the treatment unit for years. Here are the test results.

    pH 5.5
    Hardness 3 Grains / Gal
    Iron - Slight 0.2
    Solids 72
    Flow rate from well - 8.4 Gal / min
    Nobody tests for Magnesium around here.

    What components would you guys recommend?

  2. #2
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default Ps

    PS. I forgot to add that it's now just my wife and I at home, so estimated 120 gal / day total water useage. 2-1/2 baths.

  3. #3
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,792

    Default

    If your resin is the original, I suspect it should be replaced but, I would suggest replacing the equipment due to its age and built in inefficiencies.

    I'd suggest a Fleck 2510 day timer valve on an AN filter with mixed bed mineral and the same metered or a 5600 STX metered version on a new softener. Backwash a new filter every 3 days.

    You can learn about sizing and programming at the link in my signature.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  4. #4
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default

    Quote Originally Posted by Gary Slusser View Post

    You can learn about sizing and programming at the link in my signature.
    How many grains of hardness will the acid neutralizer with calcite / corrosex mix add to the water?

    What size acid neutralizer / cu ft of neutralizing material should I get?

  5. #5
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,792

    Default

    Maybe 6-8 gpg will be added to the 3 you have now.

    If you have a submersible pump and can raise the captive air pressure to 39 psi with no water in the tank and then the pressure switch to 40/60 psi, and no jetted tub or body spray shower, I'd go a 1.5 cuft. If a jet pump of any kind, a 1.0 cuft.

    Backwash every 3 days.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  6. #6
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default

    Quote Originally Posted by Gary Slusser View Post
    Backwash every 3 days.
    Why back flush every 3 days? One of the things I don't like about our current softener is that it's set to do just that, and I'm winding up using roughly 750+ lbs of salt a year, plus all the water from the well we're wasting and dumping in the septic system. If it has to be, it has to be, but I thought one of the newer systems might need to be backwashed less frequently. I had hoped it might be every 2 to 4 weeks on both the softener and the acid neutralizer.

  7. #7
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,792

    Default

    Backwashing is needed to keep the mineral from clumping and causing channeling. If that happens backwashing alone can't correct the problem and you can end up throwing the tank and mineral away. Or living with pin holes in your copper plumbing and ingesting more copper than you should. IOWs, life isn't fair.

    So the more frequent backwashing, the longer the filter continues to work as it should. And that requires water at a proper pressure and gpm, that is not wasting water anymore than you showering everyday when the human body doesn't require it... or washing the SUV, or watering a lawn.

    Your wasted water is in the softener regenerating on the same schedule as the filter when a softener should be regenerated on average once every 7-8 days and be sized and programed to do that.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  8. #8

    Default

    I don't see any need to replace the equipment or the resins without more information. I have seen no indication of the age of the equipment or that the softener resins are bad and in need of replacement. Do you any pictures of the equipment or a web link? At three grains of hardness, I doubt the softener resins are even fouled or worn out. A simple inspection can be done to help determine that. Just blindly replacing equipment or any expensive service call may be a waste of time and money. Someone commented on the age of the equipment, did I miss that information. Sometimes posts are deleted here and topics are left dangling.

    One must be very careful about raising the pressure at the pressure tank/switch, especially at your location. Simply pumping up the pressure may solve one issue but may also cause dire consequences. How long is the copper plumbing before the AN filter? Brass fittings?

  9. #9
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default

    Quote Originally Posted by water solutions View Post
    I have seen no indication of the age of the equipment or that the softener resins are bad and in need of replacement. Do you any pictures of the equipment or a web link? .
    The Master NS-10T combination acid neutralizer & softener (Pottstown, PA) is 25 years old. You can see photos of the head in my other post regarding the brine tank overflowing. From comments by others, it's an Autotrol valve. Having cleaned some screens in the head that hadn't been cleaned in 25 years, the water is now soft, but the brine level went a little higher in the tank after the back flush, so it looks like not all the brine is being sucked back during the cycle.

    Quote Originally Posted by water solutions View Post
    How long is the copper plumbing before the AN filter? Brass fittings?
    No longer than 12". After the pin holes in the feed lines to the conditioner, I had the plumber put in Pex. There's roughly 3" of Pex to the conditioner and copper after it, except for the Pex line I ran directly to the kitchen sink. Even with the conditioner on the water system, we'd have a bitter (copper?) taste in the water in the morning when it had sat in the pipe for a long time. Running a Pex line to the sink with untreated water has corrected that.

    What Gary said about flushing the acid neutralizer every 3 days is the conventional wisdom of the plumber here in PA who set up the unit 25 years ago. Since it's a combination unit, it eats salt, because that gets regenerated at the same time. We use at least 750 lbs of salt a year for water that unconditioned has only 3 grains / gal of hardness. Does anybody have any experience letting the AN regenerate on a longer cycle? If it channels, can it be easily broken up with a stick / bar through the fill hole on the tank?

    A thought that just came to me. I could keep the current combination for its acid neutralizing capability and add a new metered softener downstream from that, if the softener wouldn't need to be regenerated on such a frequent schedule. Is back flushing on softeners strictly on the basis of using up the ions, or do you need to flush softeners on a more frequent schedule to keep them from caking / channelling too?

  10. #10
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default

    Quote Originally Posted by RWL View Post
    No longer than 12". After the pin holes in the feed lines to the conditioner, I had the plumber put in Pex. There's roughly 3" of Pex to the conditioner and copper after it,
    Correction. There's about a foot of bronze valve / galvanized iron pipe before the pex begins. And the pex is about 3 FEET long, not the 3 inches that the original post had.

  11. #11
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,943

    Default

    I agree that replacing your softener with a metered demand unit is a good idea. As for the AN filter, it's a crap shoot. It does have an Autotrol head on it which was a very good head in its day and........you can still get rebuild kits and parts for it pretty cheap so it's your call whether or not to replace it. I believe Watersolutions is probably referring to high flow rates causing a break down (dezincafication) of bronze or wrot fittings that may be in the supply chain but as you say, it's all pex. Just be sure that the pex fittings are not bronze also if you raise the pressure.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  12. #12
    DIY Junior Member RWL's Avatar
    Join Date
    Mar 2012
    Location
    Central PA
    Posts
    15

    Default

    Quote Originally Posted by Tom Sawyer View Post
    I believe Watersolutions is probably referring to high flow rates causing a break down (dezincafication) of bronze or wrot fittings that may be in the supply chain but as you say, it's all pex. Just be sure that the pex fittings are not bronze also if you raise the pressure.
    Hmmm. I need some education. What is WROT? IIRC bronze is tin and copper, and brass is zinc and copper. Did you mean to say brass rather than bronze valves? I believe my current well settings are 40 and 60 psi for the cut-in and cut-out pressures. Below are photos of my valves. They're a little redder than I think of brass as being, which usually looks more yellow to me. Are these bronze valves?

    Name:  04 Valves - lower bypass to conditioner (Small).JPG
Views: 237
Size:  40.6 KB

    In the photo below, there's corrosion of the fitting carrying unconditioned water coming from the well, but not after that. Is that normal to see that corrosion? Is that something that needs to be fixed?

    Name:  05 First joint in pex (Small).JPG
Views: 224
Size:  23.2 KB

  13. #13
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,943

    Default

    Without taking a fitting apart I can't give you a definitive answer but the corrosion will be caused by a couple of things. Either the fittings are bad ( the metal composition was not correct in manufacturing ) or the installers crimping tool was not adjusted properly. But, if you look at the last photo you will see a white powdery substance that runs from the fitting joint to about half way up the tee and that there is a classic sign of dezincification so you defiantly at the very least want to have someone knowlegable come out and take that apart and see what the issue is. The valves are Souix Chief and they are fine.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  14. #14

    Default

    RWL:
    If you are is experiencing pin hole leaks, increasing the pressure would/could cause those leaks to increase in severity leading to a possible break in the plumbing.
    I would suggest replacing the lines before the treatment equipment with lines that won't corrode. And thank you for indicating that there was additional information on a post other than this one that was needed to understand; didn't make the conncetion. Equipment like yours has been known to die at a much younger age. It is possible to completely rebuild, but cost might prove better at replacement.


    OH Gary, while you're here and referring to other posts, I was still hoping for an answer to my question concerning changing the Kinetico disc to accommodate a a change in the number of persons. Perhaps you forgot about that.

  15. #15
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    I would cut that fitting out ASAP and replace it.

Similar Threads

  1. Help identifying Kinetico components and finding proper resin
    By Wayne Bailey in forum Water Softener Forum, problems, installation and reviews
    Replies: 4
    Last Post: 06-03-2011, 08:48 AM
  2. Mystery components
    By cacher_chick in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 10-09-2008, 03:54 AM
  3. Recommend toilet?
    By Nate R in forum Toilet Forum discussions
    Replies: 3
    Last Post: 02-18-2008, 11:12 AM
  4. Can someone recommend a toilet
    By xnaron in forum Toilet Forum discussions
    Replies: 7
    Last Post: 01-31-2008, 07:01 AM
  5. Proper order of irrigation components
    By gonif in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 07-09-2007, 06:25 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •