you don't need to vent the floor drain provided:
it is not less than 3"
length of fixture drain (trap arm) is not less than 18"
the fall does not exceed the size of pipe (3" fall for 3" pipe)
it is connected to horizontal drain that terminates at its upstream end in a 3" stack