Thread: basement floor XPS foam

  1. #16
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Well.. if you think the Barricade® system you linked to supports your arguement, it falls way short. They claim 1% heat loss through the floor. Their product does not laminate two inches of XPS, not even one inch.

    http://www.ovrx.com/subfloor-comparison.html

    Don't get me started on engineers and marketeers. Maybe you could design something and then get Vince to pitch it for you. I hear he lost a lot of business after the hooker bit his lip.

  2. #17
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Like I mentioned I'm not fond of any of the 2' square products.

  3. #18
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Quote Originally Posted by diyfun View Post
    My unfinished basement has a 87" ceiling height right now. I don't know I should use 1", 1.5" or 2" XPS foam on the floor? The whole basement floor plan will be 6mil poly + XPS foam + 23/32" T&G plywood + engineered wood floor.
    Since you're not spanning 16" o.c. joists, there's no rationale for going with 23/32" plywood subfloor- XPS hard-sandwiched between even half-inch t&g sheathing for the sub-floor and a concrete slab has PLENTY of structural strength, and flexes far less than 23/32" plywood spanning joists. You don't want to go thinner than 7/16" though (for fastener retention reasons.)

    There's an economic rationale for R5 (1") XPS on space heating savings (as well as a comfort rationale) in a MA climate zone & subsoil temp. There's a long term economic rationale for R7.5 (1.5"), but R10 only makes economic sense if

    A: It's a DIY and you discount you fully discount the value of your labor

    B: You use reclaimed XPS at 25-30% of virgin-stock costs

    C: You are stuck only with very high space heating fuel options (propane, or oil, or >12 cent electricity & no heat pumps)

    D: You are installing radiant floor to heat the place (in which case R12-R15 might even make sense.)

    If you stagger the seams of the subflooring with that of the foam by at least a foot or so for least mechanical creepage you can just float the floor, using foam board construction adhesive between the foam & subfloor. If there's any detectable flex to it you can throw in a few tapcons through-screwed to the floor per panel of subfloor.

  4. #19
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Quote Originally Posted by LLigetfa View Post
    PFFT! We are talking about a basement below grade were the temps are nothing like a room over the garage. Try some
    ROLAIDS®.
    Take it from some people who actually do the math:


    http://www.buildingscience.com/documents/reports/rr-1005-building-america-high-r-value-high-performance-residential-buildings-all-climate-zones


    MA is US zone 5. (See the R recommendations in Table 2, p10, but read the first chapter to understand the rationale.)

    See also: http://www.buildingscience.com/docum...study-analysis

    There's more to it than simply blocking ground moisture or heating season utility savings (but those all count too.) Putting real R-value between the subfloor and slab further reduces the mold & rot potential of the subfloor by increasing it's summertime temp to above the summertime dew point of the ventilation air. At MA outdoor summertime dew points R3 would be the minimum in central MA to mitigate summertime moisture accumulation and mold on the subfloor under a padded carpet finish floor (or area-rug over wood flooring), and the labor cost of putting down 1" or 1.5" is the same as for putting down 1/2-3/4". Without the under-floor R the mechanical dehumidification requirements to protect against mold are much higher than they would be otherwise.

  5. #20
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    One thing to remember is that you will probably have to do something with the basement stairs (probably for any of these options). Your last step will be too short, otherwise. Doors can also be an issue with the increased floor height.

  6. #21
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Thank you Dana, our friend LLigetfa tends to spew his opinions out as fact.

  7. #22
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Quote Originally Posted by Dana View Post
    Take it from some people who actually do the math:


    http://www.buildingscience.com/documents/reports/rr-1005-building-america-high-r-value-high-performance-residential-buildings-all-climate-zones


    MA is US zone 5. (See the R recommendations in Table 2, p10, but read the first chapter to understand the rationale.)

    See also: http://www.buildingscience.com/docum...study-analysis

    There's more to it than simply blocking ground moisture or heating season utility savings (but those all count too.) Putting real R-value between the subfloor and slab further reduces the mold & rot potential of the subfloor by increasing it's summertime temp to above the summertime dew point of the ventilation air. At MA outdoor summertime dew points R3 would be the minimum in central MA to mitigate summertime moisture accumulation and mold on the subfloor under a padded carpet finish floor (or area-rug over wood flooring), and the labor cost of putting down 1" or 1.5" is the same as for putting down 1/2-3/4". Without the under-floor R the mechanical dehumidification requirements to protect against mold are much higher than they would be otherwise.
    I skimmed over both docs and didn't find anything compelling but I do agree that condensation could be an issue in high humidity with carpet if there is no dehumidification. The OP stated engineered wood. The approx. R2 of DRIcore + flooring seems to be adequate for many folks that don't have much headroom and the stairs could probably be easily modified to factor for it. The OP may not mind the low ceilings, but come time to resell, others might.

    Around here, we pour our slabs over coarse stone and the air spaces somewhat reduce the conductivity to the soil if kept dry.

  8. #23
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    The OP did specify engineered wood, but the likelihood of throw-rugs/area rugs being used at some point in the future, especially on an uninsulated slab with maritime zone-damp soil with a subsoil temp of ~9C (like this poster's location) is quite high, and would a mold hazard at MA type summertime dew points. He also lives in a 30-50% higher-than-US-average-cost natural-gas & electricity market, which makes the economic rationale on the space heating end more compelling than in some other places.

    Insulated slabs aren't necessarily the best investment for every retrofit, but IIRC code-min for new construction is now R10 subslab in Maine (which is probably warmer than where you live.) If the goal is to lower the energy use profile every time the house is remodeled or upgraded, skipping the foam now makes upgrading it in future cost-prohibitive. The high-R home rule of thumb for this area is R-10/20/40/60 or sub-slab/foundation-wall/above-grade-whole-wall/attic-roof R values. (With air sealing and not-too-many & better grade windows houses built to that prescriptive standard would likely meet the Canadian R-2000 standard in most of Ontario too.) Code minimums are about half that (or less), but building only to code minimum on new housing is crap, IMHO. The comfort factor of code x 1.5 and air sealing to <2ACH/50 is enough of a payback in itself for the people living there, even if there's no margin in it on resale value. (Better to spend the money on the granite counters and the 6 sidespray marble master-bath shower if the intent is to flip it in 5 years, eh? ;-) )

    In a well designed home the cost of going code-min x 1.5 can be relatively cost-neutral using an iterative design process, using best-value materials & techniques to attain those whole-assembly R values, and applying the savings on the reduced cost of the smaller-simpler mechanicals to the R values. Clearly using 5" of 2lb foam cavity fill to raise the whole-wall R of a 2x6 studwall from R14 using fiber insulation to R17 isn't going to cut it in a present-value analysis of the utility savings any energy market. But adding 1-1.5" of 2lb foam to the exterior of a cellulose filled 2x6 wall for a whole wall R in the R20+ range would in most markets, as would taking it to the R25-R30 range with 3-4" of exterior EPS at ~$1/R/square meter in colder climates. The combined annual mortgage + utility payments for tight code-min x 1.5 homes in cold climates is usually lower than a code-min home, if some care was taken on how the whole-assembly R values were achieved. (Code min walls in MA are R20-2x6 or R13 2x4 + R5 exterior foam, either of which comes in at about R15-ish for a whole wall assembly. Foundation walls are required to be at least R15 if continuous foam, or R19 if open-cell in 2x6 studwall, again about R15-ish. Taking that to R20-25 isn't a huge stretch or huge expense.)

    Slabs are required by code in my area to be poured over coarse stone primarily for the capillary break against ground moisture, not the paltry insulation value of the air spaces although it does add about R1-R2 if you go deep enough. But the porosity of the stone and the foundation backfill can in some cases create surprisingly significant air leaks at slab penetrations, notably sumps, which may require air-tight lids for homes to meet even IRC2012 air tightness levels.

  9. #24
    DIY Junior Member mhmmofro's Avatar
    Join Date
    Sep 2011
    Location
    staten island
    Posts
    14

    Default

    I have no real comment on payback time etc. . .
    I am diy not a pro.

    I used 1/2 inch xps then a double layer of 1/2 ply over that for comfort and i love it. We use the basement as a tv / play room and are often sitting on the floor. It way more comfortable for both temp and softness compared to every other finished basement i have ever been in.

    I went with 1/2 because i was concerned with height issues. I am rite at 7ft. I think they say 1/2 is r3 so its not a great temperature difference but its a heck of a lot better then sitting on carpet on cement.

    mark

  10. #25
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    R2.5-R3 is plenty for mold-protection in a Staten Island climate, and is a HUGE improvement in comfort. Your total sub-finish stackup including the R value of the ply is about R4. You'd able to feel the difference between R3foam and R7.5 though.

  11. #26
    DIY Senior Member diyfun's Avatar
    Join Date
    May 2011
    Location
    MA
    Posts
    131

    Default

    Quote Originally Posted by mhmmofro View Post
    I used 1/2 inch xps then a double layer of 1/2 ply over that for comfort and i love it. We use the basement as a tv / play room and are often sitting on the floor. It way more comfortable for both temp and softness compared to every other finished basement i have ever been in.
    mark
    why not use 1" XPS + one layer 1/2" ply which is the same thickness as the 1/2" XPS + two layers of 1/2" ply? I assume the "ply" means plywood.

  12. #27
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Quote Originally Posted by diyfun View Post
    why not use 1" XPS + one layer 1/2" ply which is the same thickness as the 1/2" XPS + two layers of 1/2" ply? I assume the "ply" means plywood.

    I suspect they mhmmofro assumed more than 1/2" of plywood was necessary for the sub-floor, which it WOULD be were it spanning joists, but not if fully supported by XPS & slab. As long as 1/2" fastener penetration is sufficient mechanical retention the finish floor (usually is), 1" XPS with half-inch subfloor is fine. Half-inch plywood or OSB on an XPS/slab base flexes less than 3/4" plywood on 16" o.c. joists, so the nail/staple loosening forces are already lower.

Similar Threads

  1. Basement floor redo
    By cmw in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 01-27-2010, 12:09 PM
  2. Basement floor
    By idoc4u in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 11-21-2009, 08:10 AM
  3. How to level a basement floor
    By woog in forum Remodel Forum & Blog
    Replies: 7
    Last Post: 02-17-2009, 12:00 PM
  4. Basement floor raised????
    By lovec55 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 04-30-2008, 03:36 PM
  5. Basement floor drains
    By dx in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 07-04-2005, 03:35 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •