    Default Will Water Heater Wiring Overheat with External Insulation?

    Was reading an article in my local electric co-op magazine. They recommend not setting an electric water heater over 130* if wrapped with an external insulation blanket to avoid overheating the wiring. Is this really a concern? My water heater is set at about 150* and wrapped with a blanket on the sides and top.

    Thanks
    Travis

    When I need a precise measurement of something I often use the highly technical method of eyeballing it.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Guess it would depend on the type of wire that is used...on the jacket of the wiring there is normally a rating. A call to the manufacturer might be in order to see what's internal - it's fairly easy to check the external wiring. And, yes, there is a temperature limit, not so much on the copper in the wire, but on the insulation.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member Runs with bison's Avatar
    Join Date
    Aug 2009
    Location
    Midwest
    Posts
    892

    Default

    It would have to be a really p*** poor design for the insulation to break down at 130 or 150 F. Those are well within the limits of what any competent engineer would select for the service.

  4. #4
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    I advise not to cover the external thermostat/element access panels with an external insulation blanket.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Wiring can be purchased with heat ratings from as low as 50C on up. One would hope that the thing has sufficient grade of wire, but the thing was designed and tested for NO added insulation, and to save costs, the wire they used may not support the added internal heat if you add insulation. It should be easy to check, as it should be marked on the wire. Then, you'd know. Most WH seem to tell you to not add external insulation. This could be the reason.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Senior Member TJanak's Avatar
    Join Date
    Sep 2009
    Location
    South TX
    Posts
    152

    Default

    I wonder if they meant the internal wiring on the heater or the wire from the panel to the unit. I looked the other day and it is NM (no B) so technically that is probably under-rated. But I would hope it's not 150* at the top where the splice is made...

    Hackney, why? Adjustment/service issue?
    Travis

    When I need a precise measurement of something I often use the highly technical method of eyeballing it.

Similar Threads

  1. Wiring insulation repair....
    By dizzo72 in forum Electrical Forum discussion & Blog
    Replies: 0
    Last Post: 08-12-2010, 11:51 AM
  2. Water heater insulation
    By leeelson in forum Water Heater Forum, Tanks
    Replies: 54
    Last Post: 12-21-2009, 12:17 PM
  3. Wiring and Insulation
    By ScottTENN in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 02-24-2009, 03:26 PM
  4. Advice on wiring external lighting
    By Taylor in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 07-02-2008, 05:11 AM
  5. water heater insulation
    By molo in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 09-08-2007, 05:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •