    Default Connect apartment to main house well?

    I have an 8yr old house with a drilled well (185'/30gpm) and typical pressure tank & switch. We have a new freestanding garage-top apartment very near our well head and quite far from the pressure tank of the main house (125'). I assume we need to dedicate a pressure tank & switch to the new apartment and it seems sensible to connect to the well head for the new supply. I replaced the main house pressure tank and installed a water softener last year so I should be capable of hooking up the new supply to the apartment. What I need help with is how make the power connection and if I need any special valves in either line because both houses will use the same well simultaniously at times. Curious how the power works, if one tank needs to run the pump and say the other runs low and needs to turn on the pump, how will this work? Maybe I'm complicating things. I appreciate any and all help and instruction! Thank you

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    You are complicating things! Just make sure there are no check valves anywhere above ground and tee in the apartment to the well line. You don't need another tank or switch.

  3. #3
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by DIY Ray View Post
    I have an 8yr old house with a drilled well (185'/30gpm) and typical pressure tank & switch. We have a new freestanding garage-top apartment very near our well head and quite far from the pressure tank of the main house (125'). I assume we need to dedicate a pressure tank & switch to the new apartment and it seems sensible to connect to the well head for the new supply. I replaced the main house pressure tank and installed a water softener last year so I should be capable of hooking up the new supply to the apartment. What I need help with is how make the power connection and if I need any special valves in either line because both houses will use the same well simultaniously at times. Curious how the power works, if one tank needs to run the pump and say the other runs low and needs to turn on the pump, how will this work? Maybe I'm complicating things. I appreciate any and all help and instruction! Thank you
    How is the new apartment going to be fed hot water? New water heater? If so thermal expansion needs to be controlled. This is typically done by installing an expansion tank. Well bladder tanks are not considered as thermal expansion control.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,945

    Default

    You can't have two separate pressure switches both controlling the same pump, well, yes you probably could but it would require a whole lot of wiring and controls.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by Tom Sawyer View Post
    You can't have two separate pressure switches both controlling the same pump, well, yes you probably could but it would require a whole lot of wiring and controls.
    Why would you need to? Seriously,I dont work on the "things". I've replaced a pressure switch,primed them and removed them while on a job.....but thats about it. We usually leave it to the well drillers.

    Seems like with one pump all you would ever need is one pressure switch.

  6. #6
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    490

    Default

    That's basically what he's saying.

    Explain the water heater expansion tank thing to me please. I've seen them but I don't understand the purpose.

  7. #7
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,687

    Default

    Quote Originally Posted by Hackney plumbing View Post
    Well bladder tanks are not considered as thermal expansion control.
    Really? Is this a code versus common sense thing?

  8. #8
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,945

    Default

    LLigggy, it is a code thing. Yes indeed, a well tank will certainly work as an expansion tank but no plumbing code that I am aware of allows it to be substituted for a thermal expansion tank. Probably because the well tank is not tested and certified for that use and as we all know it's all about the testing and certification.....oh yes and the money too
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  9. #9
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    The three craftsman 75' garden hoses that I leave on all year round are my thermal expansion tank.

    As to the original question, 125' of pipe? Some guys can pee that far. Take softened water to the apartment with 1" pipe.

  10. #10
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    I have never seen a house with a pump system that needed an expansion tank. But if you put a PRV after the pressure tank, the house would need an expansion tank the same as a house on a city line with a PRV.

  11. #11
    DIY Junior Member DIY Ray's Avatar
    Join Date
    Feb 2012
    Location
    Asheville, NC
    Posts
    7

    Default

    Thanks, sorry for the delay been out of town. So if I understand, I can simply tee off from well head and the pressure to the apartment will be maintained by the main house switch. I have a hose hooked up to the main line at the well which I assume simulates how the apartment will receive water. I can feel the pump kick on when using the hose which will be like someone turning on the water in the apartment, right?

    I thought the pressure tank allowed an certain amount of stored water to stay under pressure so the pump does not run constantly whenever you turn on the water. If so would it be wise to add a pressure tank to the apartment?

    Thanks so much for your advice and patience.

  12. #12
    DIY Junior Member DIY Ray's Avatar
    Join Date
    Feb 2012
    Location
    Asheville, NC
    Posts
    7

    Default

    Still figuring out the details of how the apartment will be fed water. Likely directly from the well head. There will be a new water heater in the apartment. Thermal expansion is a new term for me, will have to study up on this. Anything advised is most appreciated.

  13. #13
    DIY Junior Member DIY Ray's Avatar
    Join Date
    Feb 2012
    Location
    Asheville, NC
    Posts
    7

    Default

    good advice thanks, I'll have ditch this weekend from the apartment to the septic tank for the septic tie-in and won't be far from the main house water supply. Any major rules broken by running a water line in the same ditch as the septic line? Clean water and black water running side by side, seems wrong???

  14. #14
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    Make sure there are no check valves anywhere above ground, and just tee the apartment into the well line anywhere you can. The pump should not come on until the pressure tank is empty, no mater where you are using water. But a 40 gallon pressure tank only holds about 12 gallons of water, so the pump will come on shortly after you open a faucet.

    Another pressure tank is not needed and will not work properly unless you install a CSV before the tee to the apartment. Without a CSV, the pressure tank closest to the well will fill first, and will overpressure before the farthest tank fills, so the pressure switch can shut off the pump.

    As long as there are no check valves anywhere above ground, I would not have a problem with the fresh water line being in the same ditch as the septic line. But there maybe some code violation that I am not aware of.

    And as long as there are no check valves, I don't see needing an expansion tank either.

  15. #15
    DIY Junior Member DIY Ray's Avatar
    Join Date
    Feb 2012
    Location
    Asheville, NC
    Posts
    7

    Default

    Thanks so much, everything makes sense to me now. l'll post some pics of the rough-in seeking critics!

Similar Threads

  1. house main shutoff
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 05-05-2010, 09:16 AM
  2. Main house wiring
    By pheonix1061 in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 04-09-2008, 05:30 PM
  3. Connect house to water heater with PEX?
    By Mikey in forum Solar and Geothermal Water Heating Forum
    Replies: 2
    Last Post: 02-24-2008, 07:07 PM
  4. Connect house to water heater with PEX?
    By Mikey in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-24-2008, 07:07 PM
  5. main service to the house
    By mike.schwank in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 07-10-2007, 06:17 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •