    Quote Originally Posted by hj View Post
    I have never heard of the UFER being used a a "ground rod". Basically, every building has a UFER, but every building also has a ground rod, or two, or a metallic water service line.
    Well, a Ufer is a grounding electrode, not a ground rod.
    Like I said, even with a non-metallic water entrance, with a Ufer NO other electrodes are required or needed.

    It's all in the code.

  2. #17
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    Quote Originally Posted by Speedy Petey View Post
    Well, a Ufer is a grounding electrode, not a ground rod.
    Like I said, even with a non-metallic water entrance, with a Ufer NO other electrodes are required or needed.

    It's all in the code.
    I ground rod is a electrode, but a electrode is not necessarily a ground rod.

    I got the picture.

    Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe.

    And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #18
    DIY Junior Member Chris DeLong's Avatar
    Join Date
    May 2012
    Location
    New Jersey
    Posts
    2

    Default

    Quote Originally Posted by DonL View Post

    Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe.

    And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not.
    Why would a warning on the gas meter be required?

    The grounding electrode conductor must terminate in accordance with (1), (2), or (3).

    (1) Buildings or Structures With an Intersystem Bonding Termination. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the intersystem bonding terminal [Art. 100 and 250.94], as shown in Fig. 1. Bonding all systems to the intersystem bonding termination helps reduce induced potential (voltage) differences between the power and the radio and television systems during lightning events.

    (2) In Buildings or Structures Without Intersystem Bonding Termination. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the nearest accessible location on the following:

    • Building or structure grounding electrode system [250.50].

    • Interior metal water piping system, within 5 ft from its point of entrance [250.52(A)(1)].

    • Accessible means external to the building, as covered in 250.94.

    • Metallic service raceway.

    • Service equipment enclosure.

    • Grounding electrode conductor or the grounding electrode conductor metal enclosure.

    (3) In Buildings or Structures Without a Grounding Means. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the nearest accessible location on the following:

    • Any individual electrodes described in 250.52

    • Structural steel grounded in accordance with 250.52(A)(2)

  4. #19
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    Quote Originally Posted by DonL "Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe. And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not."

    Quote Originally Posted by Chris DeLong View Post
    Why would a warning on the gas meter be required?

    Because Many People do not follow code and have know clue what you are talking about.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Grounding gas line to panel...
    By deerme in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 04-18-2009, 04:02 PM
  2. Changing oil furnace to 2 line
    By thunderhead in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 04-05-2009, 03:17 PM
  3. Changing From Plastic To Copper
    By Boyertown_Casket in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 09-07-2006, 02:21 PM
  4. Replacing Water Service Line
    By xd2005 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 20
    Last Post: 07-05-2006, 06:38 AM
  5. Water Service Line Piping
    By gwright in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-20-2005, 02:14 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •