Thread: 3 inch to 4 inch waste line

  1. #1
    DIY Member Willie Two's Avatar
    Join Date
    Jan 2011
    Location
    British Columbia
    Posts
    36

    Default 3 inch to 4 inch waste line

    At what point in the house can the drainage system go from 4 inch main drain down to a 3 inch pipe ?

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default

    The required pipe size is determined by the number of fixture units draining into the pipe. Most common single-bath, single family homes would not require a 4" drain anywhere. Local plumbing codes may require 4" from the home to the city sewer connection.

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    The way your question is worded, it sounds like you want to reduce the out going drain from 4" to 3". I hope this is how I am reading the question and not what you want to do. (sorry, I'm just an old school teacher)

  4. #4
    DIY Member Willie Two's Avatar
    Join Date
    Jan 2011
    Location
    British Columbia
    Posts
    36

    Default

    Problem solved, thanks to all who answered.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    you do not say HOW the problem was solved, but the common answer to the original question would be "you can use 3 inch up to the point where you connect a fourth toilet. Then it has to increase to 4 inch pipe". UNLESS, you live in an area which requires the vent out the roof to be the same size, undimished, as the incoming line, then you need to run 4" all the way.
    Licensed residential and commercial plumber

  6. #6
    DIY Member Willie Two's Avatar
    Join Date
    Jan 2011
    Location
    British Columbia
    Posts
    36

    Default

    The inspector allowed 3 inch as I only have 2 WC. Increase to 4 inch just before it leaves the building.

    Most codes allow three toilets on 3"
    Where the forth toilet is added, it goes to 4"
    Building sewers are 4" regardless.
    Added by Terry
    Last edited by Terry; 03-15-2012 at 09:22 AM.

  7. #7

    Default

    by code you should be 4" building drain to your 3" stack which remains 3" all the way to open air
    2 toilets on 3" if horizontal, 4" downstream of 3rd
    3" stack can be up to 6 toilets, after six must be 4" pipe

Similar Threads

  1. pressure balanced vs thermostatic valves (1/2 inch vs 3/4 inch)
    By Shawn_T in forum Shower & bathtub Forum & Blog
    Replies: 38
    Last Post: 02-18-2012, 01:01 PM
  2. we have a 16 inch rough-in andcannot find a tolet ith a 16 inch roughin anywhere
    By nancyann in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-17-2011, 04:22 PM
  3. Another 4-Inch versus 8-Inch Sink Drill Question
    By RonnyK in forum Remodel Forum & Blog
    Replies: 9
    Last Post: 01-27-2009, 09:45 AM
  4. Cable tool or bore drill? 5 inch pvc or 4 inch steel?
    By Barnes in forum Pumps and Tanks Well Forum & Blog
    Replies: 5
    Last Post: 05-16-2008, 05:48 AM
  5. Problem flowing 4 inch PVC into 3 inch cast iron?
    By skip in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 08-26-2005, 07:03 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •