Concerned over Backpressure by Adding a CSV Valve to Existing System

Users who are viewing this thread

vpr80

New Member
Messages
29
Reaction score
0
Points
0
Location
NJ
Long story short. Well ran dry in 2010, had it drilled deeper and new pump installed. Now I think that the pump is too big and cycles too often meaning a short lifetime so I am considering adding a CSV valve.

The well is 360' deep with the water table at approx 150' deep. The new pump is a Grundfos 25-S-30 and feeds a Well-X-Trol 119 Gal Tank that is 4 years old.

My biggest concern with the CSV is the back-pressure. How can I check or know whether it will be ok?
 

vpr80

New Member
Messages
29
Reaction score
0
Points
0
Location
NJ
That pump will build 130 psi back pressure. Should not be a problem.

That's it, just build to 130psi and then what happens as the pump continues to run?
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
That’s it! 3 HP motors need a CSV with a minimum of about 2 GPM to keep the motor cool. So the only time there will be 130 PSI backpressure is when you are only using 2 GPM, or after you stop using water and the pressure tank is refilling at a 2 GPM rate. During these times the 130 PSI backpressure from the CSV makes the pump think it is in a 300’ well where it can only produce 2 GPM.

When you need 30 GPM, the CSV opens up and lets the pump think it is only 150’ to water, so the pump can produce 30 GPM.

Backpressure is a good thing. That 17 amp motor will only be pulling about 8 amps when you are using 2 GPM and the backpressure is 130 PSI. Less amps means less electricity and the motor runs cooler. Most importantly, backpressure is what stops the cycling.
 

vpr80

New Member
Messages
29
Reaction score
0
Points
0
Location
NJ
Ahhh ha! Ok got thank you!

One other question, what are some common uses for the three extra ports on the CSV1A? Seems I can use one 1/2" for a pressure gauge, but what do you do with the others?
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
The CSV1A comes with plugs for those ports in case you don't need them. But they are made to attach the pressure tank, pressure switch, and pressure relief valve, the same way as in the picture to the left.
 

vpr80

New Member
Messages
29
Reaction score
0
Points
0
Location
NJ
So basically like this, right?

CSV1A .jpg
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Why on earth would he abandon a 115g tank? Cant you make it work with that so that his pump isnt running for tooth brushing? 2 hp is a lot of pump.

When I barrell test pumps and close down the valve to near off flow, and I have done several, from 1/2 to 3 HP, I never get a amp drops of more than 1/2 to maybe 2 amps. 1 seems an average.

I test a lot of motors under and off load, and from 17 amps to 8 amps? I would be looking for a new meter. Now going the other way, overloading a motor can easily make it go from 17 to 36 amps until it smokes or blows the breaker.

I certainly agree he needs to not cycle that big pump to death, especially if he can't adjust any irrigation, but this little tank has gotta bump his electric bill pretty tall.

The bad guy is the pump company that rather than SIZE the pump, sold him what made the most profit for them, or what they had left over.
 
Last edited:

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Why on earth would he abandon a 115g tank? Cant you make it work with that so that his pump isnt running for tooth brushing? 2 hp is a lot of pump.

When I barrell test pumps and close down the valve to near off flow, and I have done several, from 1/2 to 3 HP, I never get a amp drops of more than 1/2 to maybe 2 amps. 1 seems an average.

I test a lot of motors under and off load, and from 17 amps to 8 amps? I would be looking for a new meter. Now going the other way, overloading a motor can easily make it go from 17 to 36 amps until it smokes or blows the breaker.

I certainly agree he needs to not cycle that big pump to death, especially if he can't adjust any irrigation, but this little tank has gotta bump his electric bill pretty tall.

The bad guy is the pump company that rather than SIZE the pump, sold him what made the most profit for them, or what they had left over.
Again, you're letting your imagination run away. I don't read anywhere in this thread any suggestion that he abandon his existing tank.

As for a drop in amps, that will vary based on the pump design.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Yeah I never said to abandon the big tank. I just showed a picture of the CSV1A with a little tank attached. You could just as easily run a pex or any other kind of line from that port to the big tank. Although if the big tank goes bad, I would not go back with that large a tank. Even with a 2 HP the 4.4 gallon tank is enough, and I would go no larger than a 20 gallon size tank. The amount of water and pump run time used strictly for toilet flusing won't add up to two dollars a month, and will probably be made up for by eliminating cycling for other long term water uses. And I know the amps of that 25S30 Grundfos pump will drop from 17 to 8 or even better, because my own 25S20 2HP drops from 12 amps to 4amps when only using 1 or 2 GPM. If the pumps you test are not dropping at least 30% in amps, then either they are a bad design or the thrust bearing is no good.

Below is just one way to use the CSV1A as a tank cross for larger tanks. The extra ports on the CSV just give multiple possibilities for ways to plumb it in.
 
Last edited by a moderator:

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Now I see the motor is 3HP. Thats a lot of pump.

As soon as one of you guys posts a video of a good ammeter attached to a 3 HP pump dropping from 17 amps to 8 amps when throttled down from open flow to 2GPM, I'll be a believer. I have tested it, and see no chance of it, no matter the pump "design".

amps UP - easy on overload. Amps DOWN, hard to achieve. Words are easy - meters don't lie.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Pump curves don't lie either. If you know how to read a pump curve, you will see that amps decreasing as the flow rate decreases is the normal way a pump operates. Here are links to two videos. One shows a 5HP three phase pump/motor droping from 10 amps to 5 amps as the flow decreases. The other shows a 10HP single phase pump/motor working from 28 to 58 amps, depending on the flow rate. I thought I had one of my 2HP going from 12 to 4 amps, but I can't find it today. I will video it again next week and post it as soon as possible.

http://www.spatter.net/csv-video/amps-csv-vs-vfd-dsl.wmv

http://www.spatter.net/csv-video/csv-dsl.wmv

I only know of a few pumps that do not decrease amp draw with flow rate. The 10GPM Sta-Rite and a 55 GPM F&W are not good designs and do not work properly with a CSV. Those are the only pumps in 20 years that I have found that do not have a good amp drop. Any pumps that do not decrease amps with the flow rate are either badly designed or the thrust bearing is bad. Most pump companies are more concerned with reducing production cost, increasing profits, and building in planned obsolescence than they are with actually building a quality pump. Finding a pump that has the best drop in amps verses flow and using a CSV to reduce the number of cycles is the best way to beat the system. In that way you can triple or quadruple the life of your pump and beat the manufacturers plan for you to purchase a new pump regularly and often.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Depending on what you read or believe submersible well pumps average from 7 to 10 to 12 to 15 years but......sediment, installation and pump quality all effect pump life and I'm not real sure where those averages come from either. My own Goulds 1/2 - 7gpm has been in the hole close to 30 years now and still works just fine. If I had to guess I would say that the average pump that we pull for replacement is closer to 20 years old. Now if you consider the amount of work that thing has to do day in and day out, I don't think 10 to 20 years is too awful bad especially when you compare it to the other appliances in your home that work a whole lot less. Nothing lasts forever. Oh and.........I sell pumps
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
20 years ago I was told by an engineer at Franklin that the average life of a submersible is 7 years. I don't think they will admit that anymore. I confirmed that number many times by datecoding the mountain of pumps and motors I hauled to the scrap metal place every year, of which some were professionally installed and some were not. Motors that were made 30 years ago will be twice as long, twice as heavy, and last many times longer than a new motor. The only goal now is to produce a pump/motor cheaper than your competitor. Sand and sediment not withstanding, motors are designed to survive a certain number of cycles. The sooner you use up those cycles, the sooner you will need a new pump.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
My own Goulds 1/2 - 7gpm has been in the hole close to 30 years now and still works just fine.
My Goulds was still running after 12 years when I pulled it out of the hole, but the wet end was all worn out and I could not find parts to rebuild it. I'm hoping to find one with a bad motor and marry the two halves. In the meantime, I'm keeping it to overpump my well to wash out sediment.

I don't get why some folk are so determined to try and discredit the value of a CSV. Reducing cycling can't be a bad thing and constant pressure has to be better than the ups and downs of a traditional system. I wish I could use a CSV and have higher pressure and volume but the damn micronizer I have for iron fitering prevents it.

Oh and.........I don't sell pumps, I buy pumps. I also don't sell CSVs.
 

Plumber111

In the Trades
Messages
76
Reaction score
0
Points
0
Location
North Carolina
My Goulds was still running after 12 years when I pulled it out of the hole, but the wet end was all worn out and I could not find parts to rebuild it. I'm hoping to find one with a bad motor and marry the two halves. In the meantime, I'm keeping it to overpump my well to wash out sediment.

I don't get why some folk are so determined to try and discredit the value of a CSV. Reducing cycling can't be a bad thing and constant pressure has to be better than the ups and downs of a traditional system. I wish I could use a CSV and have higher pressure and volume but the damn micronizer I have for iron fitering prevents it.

Oh and.........I don't sell pumps, I buy pumps. I also don't sell CSVs.

I don't know if it is as much wanting to discredit as it is attempting to understand both systems to be able to always provide the best solution.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
I have never discredited them and when I was installing irrigation systems in Florida they were pretty much the standard but they are not necessarily a necessity in every situation. If the pump and tank were properly sized in the first place a CSV will have little if any effect on either the longevity or the cost of operation.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
I don't get why some folk are so determined to try and discredit the value of a CSV. Reducing cycling can't be a bad thing and constant pressure has to be better than the ups and downs of a traditional system. I wish I could use a CSV and have higher pressure and volume but the damn micronizer I have for iron fitering prevents it.

Not trying to discredit, but to sort out where it pays back. A 20 HP pump that replaces a water tower with a csv is a no brainer saver. At grannys cabin, looks like a stretch to me.

You can use a Pressure reducing valve and a high outside pressure to get true constant pressure for 50 bucks.

What sort of micronizer wont take a high pressure?

My csv is about 80+ psi outside and a prv at the house.

20 years ago I was told by an engineer at Franklin that the average life of a submersible is 7 years. I don't think they will admit that anymore. I confirmed that number many times by datecoding the mountain of pumps and motors I hauled to the scrap metal place every year, of which some were professionally installed and some were not.

An "average" is quickly brought down to 7 from 20 or 30 years when we count that most people dont even know where their pressure tank is at. And fewer yet care to check on them and know how to do it right. And fewer yet know how to zone their irrigation, adjust the pressure swing accordingly, and finally, to size the pump in the first place. The guy that started this got boned with a 3HP pump, unless he's got 500 apple trees on spray irrigation.

I have a pump, 1.5 hp franklin, with a shut off valve on the outlet and no tank. So it occurs to me that I can easily throttle it down and read the amp drop - I'll report back. The pump head is a Myers Rustler or something like that with a cast outlet.
 