Originally Posted by
Plumber111
Behind the horizontal 2" Long Sweep 90 there is a vertical 2" Long Sweep 90 that continues through the floor. The pipe that connects to that must continue as a combination drain/vent. Simply put a Charlotte 440X in the vertical pipe above the floor or in the cabinet. However the pipe is ran, the finished floor should have no bearing as the vertical 2" piping is continuing somewhere.
Yes, a 22' run should such as this should have a cleanout in my opinion regardless if it is minimum code or not.