    Question Testing CPVC. How long should the pressure stay at initial PSI?

    I am trying to test some new CPVC plumbing I installed. If I pump the PSI up to 100lbs, it holds at that PSI for a few hours, but by the next day it is down to around 80psi. All of this plumbing is in an unheated area for now, so the temp in the building is between 20 to 35 degrees. Would the temp cause the PSI to drop over night? I have checked all of the fittings and can't seem to find any kind of leaks.

  2. #2
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    What are you using to pressure it up with? I personally wouldn't use air.

  3. #3
    DIY Junior Member OHIOresident's Avatar
    Join Date
    Sep 2010
    Location
    Ohio
    Posts
    15

    Default

    Yes, air. That is the norm for around here. It is just not advisable to pressure it any higher than 100psi.

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    If the temperature is constant, the pressure should be constant also. There will be roughly 1 psi difference for every 10 degree change in temperature.

    More often than not, one of the leaks is in the test fitting.

  5. #5
    DIY Junior Member OHIOresident's Avatar
    Join Date
    Sep 2010
    Location
    Ohio
    Posts
    15

    Default

    Thanks for the info. I guess I need to look at my plumbing job again. The temp is only varying by 20 degrees either way, so my pressure change should be nowhere near 10-15 lbs. I will check the test fittings first. The decrease in psi is so slow I can't seem to locate it. Thanks again.

  6. #6
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    I always install a ballvalve then install the schrader air valve into it. After I fill the system I turn the ballvalve off. This way my schrader air valve cant leak....and its common that they do.

    catcher chick is giving good advice.

Similar Threads

  1. pressure testing well casing
    By cabincrazy in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 03-07-2011, 06:21 PM
  2. Pressure Testing Gas Line
    By cloves in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 04-16-2010, 08:33 PM
  3. Pressure testing DWV
    By jar546 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 12-22-2008, 04:04 PM
  4. Venting and Pressure Testing
    By maxprophet in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 06-12-2008, 04:32 PM
  5. What pressure for air testing copper?
    By seaneys in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-12-2008, 08:24 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •