because when you measure the voltage at that outlet, you are measuring from the Neutral to the hot leg at that outlet.
If that 2 pole breaker had a 1000 watt load on each pole of the breaker, the 2 loads would wind up being in series with each other fed by 240 volts, and the neutral would be handling little, if any current.
If one breaker had 1000 watt load on it, and the other pole of that breaker had a 250 watt load on it, then the neutral would be carrying the current for 750 watts at 120 volts 6.25 amps. If the 250 watt load was disconnected, then the Neutral would be carrying the full 1000 watt current at 120 volts 8.33 amps
I am definitely not a pro plumber, but I am a pro crastinator
That is because the WH is a 240v device. If it also needed 120v for something, it would also need a neutral to create a 120v source.
Correct. The timer and such usually take 120v. This is true of many 240v circuits (such as a range). Pure 240v circuits (like a WH) only need the 2 hots and a ground.
I am definitely not a pro plumber, but I am a pro crastinator
The older ciruits had 2 hots and a Neutral for the Dryer power
most likely using 10/3 kleenex without ground. The new dryers (and ranges) are supposed to be wired with nn/3 (nn= proper sized conductors) plus ground kleenex and a 4 prong plug and receptacle.
The ground on the old stuff was added to the frame of the dryer by the installer to a "safe" (not really) water pipe nearby
I am definitely not a pro plumber, but I am a pro crastinator
I think I'm ready to wire YOUR house now.....LOL Just kidding thanks for the tips.
My house was built in 2000. I'll be removing my panel cover and making sure any multibranch circuit is done with a double pole breaker.
Last edited by Hackney plumbing; 02-21-2012 at 02:35 PM.
Maybe this will help...
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer
America is in the dark ages with electricity. Europe, even Africa wires all for 240V and the timers and controls [DUH!] in appliances are built for 240V. Now you are outlet wiring with 16 and 18 gauge wire and don't need a neutral.
When copper was cheap and the US made it all, the copper lobby won. We all lost.
Notice that at least the Americans are smart enough to sell electric water heater timers that have a [MAGIC!] clock that runs on 240V, so you need not pull in another totally unneeded wire. Imagine the audacity of making a 240V lightbulb!
The one difference being that most of the electricity that we see in our houses is 110v, yes, and that is a lot easier to let go of it if gets you than is 220v.
I have a vague memory from the late '60's when I lived on an airforce base in Britain. I was very young. I seem to remember a TV show explaining the workings of a GFI outlet and saying that they would becoming a standard. But it could have been a few years later in the states.
IN a perfectly balanced split feed, the neutral is not carrying any current. It is "alternating current" and the two lines are 180 degrees out of phase, so when one's black wire is "+" the other's is "-" so they cancel each other out. The neutral takes care of any imbalance.
Licensed residential and commercial plumber
I have heard, but do not know if it is fact, that homes in Australia only have a single 240 volt wire coming into the houses. The return to the generator is done with a "ground connection" into the earth.
Licensed residential and commercial plumber