Thread: 14/3 strange usage

  1. #1
    DIY Junior Member MrBillyd's Avatar
    Join Date
    Feb 2012
    Location
    Scottsdale
    Posts
    10

    Default 14/3 strange usage

    I am in the middle of demo and rebuild of 40 feet of softit removal and raising all of my ceiling up to 8ft.
    The house was built in 79.
    I have been re working the existing wiring so I can reinstall all the dry wall.
    I found two strange usages of 14/3.
    The home builder ran 14/3 for two different circuts instead of running 2 14/2.
    So, instead of running 80 feet across the house with 2 14/2 he ran one 14/3 and shared the N.
    In the living room the red hot wire goes thur a light switch to control a plug.
    The black controls the other 4 outlets, garage lighting, door opener, utility rm lights, kitchen, hallway and entry way lights.
    (Today I ran 2 new 14/2 feeds removing garage's 5 items, and another removing the utility and kitchen.)

    Another situation they did this was in the kitchen, (same idea but with 12 awg wire) Red wire feeds the disposal, black the dishwasher and the counter outlets.
    Does this type of shared N still happen today?

    Also, I just bought a GFI outlet as my kitchen does not have one. Can you use a GFI with a circuit that has a shared N ?
    Or will turing on the disposal trigger a GfI on the other circuit?

    Thanks
    Bill

  2. #2
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by MrBillyd View Post
    .... instead of running 80 feet across the house with 2 14/2 he ran one 14/3 and shared the N....
    Another situation they did this was in the kitchen, (same idea but with 12 awg wire) Red wire feeds the disposal, black the dishwasher and the counter outlets.
    Does this type of shared N still happen today?
    It is called a Multi-wire Branch Circuit. Yes they are legal, common, and still used today.

    Also, I just bought a GFI outlet as my kitchen does not have one. Can you use a GFI with a circuit that has a shared N ?.....

    Thanks
    Bill
    You can, but knowing how and where in the circuit to hook them up is a bit tricky. How brave are you?

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,683

    Default

    It's common to see kitchen split receptacles fed from a ganged breaker.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    You have to be careful with the neutrals. I was once baffled for a while by a GFI trip...someone had tied some whites together in a box where a receptacle was fed from the GFI load side. That neutral from a different "hot" leg added an unbalanced flow back to the GFI and tripped it.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    The shared neutral is ONLY legal when the two "hot" legs are on different sides of the incoming service. If they are on the same side, the amp loads on the neutral are added together instead of subtracted.
    Licensed residential and commercial plumber

  6. #6
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by hj View Post
    The shared neutral is ONLY legal when the two "hot" legs are on different sides of the incoming service. If they are on the same side, the amp loads on the neutral are added together instead of subtracted.
    Explain this in detail HJ. Thanks for the post. I'm taking it as when you install the breakers for the two circuits(one 14/3 or 12/3 etc) one breaker should be on one side of the panel and the other breaker should be on the opposite side,corresponding to the two incoming feeds from the utility co.

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Hackney plumbing View Post
    Explain this in detail HJ. Thanks for the post. I'm taking it as when you install the breakers for the two circuits(one 14/3 or 12/3 etc) one breaker should be on one side of the panel and the other breaker should be on the opposite side,corresponding to the two incoming feeds from the utility co.
    The breakers should be installed side by side so a handle tie will cause both breakers to turn off at the same time. This is a requirement of the new NEC.

    If using a multi-wire circuit and you are a DIYer it would be a real good idea to use a two pole breaker for this circuit. This way you can’t go wrong.



    look at the bus bars of the CH panel. You can see that one breaker straight across form the other would be on the same leg but two breakers side by side would land on two legs of the panel.
    When installing a multi-wire circuit it is important to be sure that the breakers land on opposing legs so the unblanced load is carried on the neutral. If both breakers are on the same leg the current adds on the neutral which will cause the insulation of the neutral to melt.

  8. #8
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    I see that when the breakers are aligned horizontally they would share the same leg of the supply but when installed "stacked" vertically directly above and below each other they are on seperate legs. The panel alternates. So let me get this straight about the principle of it.......since both circuits share the neutral and the neutral is the return path of a.c. current,the shared neutral would be the return path for both circuits and thats an overload aka "A house fire" LOL

    What I really dont understand is why installing the breakers on different legs of the panel would prevent that.... I guess it's balanced that way? Thats the part I strugggle wit I think.

    Thanks for your time. I dont plan on doing any wiring but its nice to learn. By the way,if this is such an issue why is it a new code? Seems like it would have been code long ago seeing it can burn houses down.
    Last edited by Hackney plumbing; 02-21-2012 at 09:44 AM.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    You really don't have 120vac coming into the house, it's 240vac across the transformer with a 'neutral' connected half-way across the coil. If you connect between that half-way point and the either end, you get 120vac. One reason you may not get exactly the same voltage on one leg verses the other is that the neutral might not be perfectly centered. So, when one leg is going positive, the other leg is going negative, and half-way between them is a zero potential. If using vector math, the direction of the current vectors from each leg going back through neutral are exactly opposite - when added together, they equal zero.

    If you do this and both feeds are on the same branch, both their current vectors are pointing exactly in the same direction, and with vector math, they add, so you now have double the current verses zero if done right. Since no one leg can exceed the max designed for that wire as protected by the CB, it can never exceed the wire's capacity, and if balanced, could be zero (probably doesn't happen too often).
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Seems like a no brainer that the bars alternate, other wise how could one obtain 240 volts on a double breaker?.... the lightest glance at a panel will show you that.

  11. #11
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by ballvalve View Post
    Seems like a no brainer that the bars alternate, other wise how could one obtain 240 volts on a double breaker?.... the lightest glance at a panel will show you that.
    Yeah that makes sense but what doesn't make sense to me is why installing the breakers on separate legs of the 120 will keep the neutral from being overloaded. Its still only one neutral coming back to the main panel.

  12. #12
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    The two legs are opposite in polarity, you could say. When #1 is going positive (towards +120v), the other (#2) is heading negative (towards -120v). The neutral remains in the middle. As #1 goes positive, the current for it will go one direction on the neutral, while the current to #2 will go the opposite direction on the neutral.

    If the loads are exactly the same, the current on the neutral will cancel out (no net current). In the other extreme, you have the full load on 1 side and none on the other. In that case, the current on the neutral is equal to the current on that hot (the one with the load). So, if they are on opposite legs, you can't run into a situation where the neutral will carry more than either one of the hots.

    Jim mentioned how it works, but maybe this will make it a little more clear.

  13. #13
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Jim mentioned I really dont have 120 coming into the house but if I measure the voltage at an outlet thats what I get. How is that possible if I do not have 120 coming into the house?
    Last edited by Hackney plumbing; 02-21-2012 at 01:23 PM.

  14. #14
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    You have 240 V coming into the house with a neutral. The neutral splits the voltage in two. If you measured the voltage between the two hots feeding the house, you see 240v. If you measure between each hot and the neutral, you get 120v. Say your panel is all 120v circuits, half of the house is on one side of the incoming line and the other half of the house is on another.


    Maybe it is easier to think about in terms of batteries. Say you have two 6v batteries. Connect the + of one to the negative of the other. If you now measure the voltage between the + of one battery and the - of the other, the voltage is 12v, right? This is how you can think about the supply to the house. Now if you measure between the + and - of either battery, each is still 6v (this is like your 120v circuits). So 240v = 2 batteries, 120v = 1 battery. Some 120v circuits are on battery #1, and the rest are on battery #2.

    Now with the house voltage, the + and - flip back and forth. So, when circuits on battery #1 are + compared to neutral, the circuits on battery #2 are - compared to neutral.

  15. #15
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by nukeman View Post
    You have 240 V coming into the house with a neutral. The neutral splits the voltage in two. If you measured the voltage between the two hots feeding the house, you see 240v. If you measure between each hot and the neutral, you get 120v. Say your panel is all 120v circuits, half of the house is on one side of the incoming line and the other half of the house is on another.


    Maybe it is easier to think about in terms of batteries. Say you have two 6v batteries. Connect the + of one to the negative of the other. If you now measure the voltage between the + of one battery and the - of the other, the voltage is 12v, right? This is how you can think about the supply to the house. Now if you measure between the + and - of either battery, each is still 6v (this is like your 120v circuits). So 240v = 2 batteries, 120v = 1 battery. Some 120v circuits are on battery #1, and the rest are on battery #2.

    Now with the house voltage, the + and - flip back and forth. So, when circuits on battery #1 are + compared to neutral, the circuits on battery #2 are - compared to neutral.
    Oh ok.....My power meter and main panel box is outside. I have both 120 and 240 coming into the house depending on what appliance your checking at.

    I found this info on multibranch.

    .................................................. .................................................. .................................................. .................
    By David Herres

    The following article was written when NEC 2005 was in force. NEC 2008 contains one significant Code change. Instead of only certain sensitive multiwire branch circuits, now all multiwire branch circuits must be protected by a double-pole breaker, not two single-pole breakers. In all cases, two single-pole breakers, linked by a listed device, are equivalent to a double-pole breaker.
    Another important NEC 2008 change is that the ungrounded and grounded conductors of each multiwire branch circuit must be grouped by wire ties or similar means in at least one location within the panelboard or other point of origination. An exception provides that the requirement for grouping does not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious.

    The very concept of a multiwire branch circuit, sharing a neutral between two circuits, appears designed to throw apprentice electricians into severe anxiety and disapproval.

    It would seem obvious that two hot legs, both loaded close to maximum, would heat their shared neutral to such an extent that it would glow red hot as it passed through all that flammable material present in the walls of a wood frame building. Wouldn't it be best to call it "a multicircuit branch wire" and ban it forever?

    Savvy electricians know otherwise and indeed the careful NEC allows a multiwire branch circuit if used properly. Actually such an arrangement, besides being Code compliant, has a few advantages and efficiencies which make it an attractive option. But there are some severe drawbacks as we shall see, and it may be that the outraged apprentices are right.

    The whole idea is that the two hot wires have to be connected to different phases. Then, the neutral carries only the unbalanced current, the difference at any moment, between the more heavily loaded leg and its lighter colleague. In a single-phase circuit the neutral carries the most current when one leg is fully loaded (just under the amount that would trip the circuit breaker) and the other leg is not loaded at all. Then, as the amount of current flowing through the other leg increases, the neutral cools down. When both legs are equally loaded the two return flows in the neutral cancel and it is like the white wire is not there. In a run of conduit there is actually less heat than if the same two loads were on separate two-wire circuits. Besides saving wire, it is sometimes possible to use smaller conduit and on long runs voltage drop can be significantly lower. Additionally, 12-3 type NM is easier to install because it is round. There is definitely money to be saved.

    Before considering the downside of these circuits that claim to eliminate a redundant neutral, let's see what NEC 2005 has to say.

    The first mention is in Article 100-I Definitions. (Its presence there indicates that multiwire branch circuits are going to appear in more than one place in the Code. In fact, requirements are in eight locations.) "Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system."

    The main concept embodied in this definition is that the ungrounded conductors have to have voltage between them; that is they cannot be connected to the same leg. If they were connected to the same leg, the apprentice's worst fear would be realized - the shared neutral's ampacity would soar. Most electrical mistakes resulting in overloads will trip out the circuit breaker providing warning that something is wrong. But a misfed multiwire branch circuit will silently heat the neutral until it either burns clear inside an enclosure or ignites flammable building material resulting in property loss or worse.

Similar Threads

  1. spike in ng usage
    By trw888 in forum Water Heater Forum, Tanks
    Replies: 16
    Last Post: 11-19-2009, 08:58 PM
  2. Pump Usage
    By sapruitt in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 08-09-2008, 03:42 PM
  3. well usage
    By rbig in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 03-16-2008, 04:45 PM
  4. How to reduce my KWH usage?
    By ffmedic7 in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 08-29-2006, 10:58 AM
  5. Greywater usage
    By citykid in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-29-2006, 03:32 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •