    Default Wire size

    My house was built in 79. I am removing my 30 year old stove/double oven combo.
    The wire that is being fed from the 50amp breaker is about 80 feet long.
    The markings say Stabiloy Type SE XHHW 300volts to ground 3CDRS 6 AL
    My new situation will be an Induction Cooktop on one breaker and seperate double oven.
    The cook top takes a 50amp breaker and the double oven takes a 40amp breaker (per the spec sheets)
    I am pulling another feed which will be 6/2

    Which wire should I put on my 40amp breaker?
    My 30 some year old AL wire has been on the 50amp circuit without issue.
    If the 6/2 could handle the load on the Induction cook top better, then I would swap them

    Bill

  2. #2
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    6 SE AL is only rated for 40A.
    Often double ovens are not straight 240V and would need three conductor plus a ground. Are you sure 6/2 will work for the oven?

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    It is probably 6/2 entrance cable which, in the old days, used the outer wrapping for the neutral and ground. Both the oven and cooktop need a 120/240 circuit because of the control wiring. Good call going with induction cooktop. For a long time reasonably priced and available ones were nonexistent. Fortunately, my original one lasted long enough for new 36" models to become available.
    Last edited by hj; 02-21-2012 at 07:23 AM.
    Licensed residential and commercial plumber

Similar Threads

  1. Ground wire size
    By Giles in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 02-17-2011, 11:41 AM
  2. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM
  3. Wire size question
    By jparrie in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 10-20-2008, 04:46 PM
  4. Intermixing wire size
    By Mr_Magoo in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 08-13-2008, 03:17 PM
  5. Wire Size / Fixture Attachment
    By OscarG in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 08-21-2007, 01:48 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •