    Hello. I've been lurking here for awhile, working on a complete bathroom renovation. I'm taking a double sink bathroom down to a single (for accessibility). I have the following in the wall behind where the vanity will go.

    Name:  IMG_20120213_214632.jpg
Views: 782
Size:  44.8 KB

    I cannot budge the brass fitting on the left which ran to the old sink. Have not tried the one on the right yet. I only need one connection, and the one on the left works best for the new vanity layout. The pipe above is the vent to the roof, and the one below goes straight down to the soil stack.

    What is the best way to disassemble this thing without breaking the (freshly painted) wall in the other room? Tried WD-40 with no luck. Torch to the female iron fitting the next step?

    Thanks.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    1. That is the wrong fitting in the first place.
    2. You will create a worse situation unless you remove that "cross" and install a sanitary tee.
    3, You need a bigger wrench.
    4. The elbow on the right is probably too "big" to rotate without damaging the wall on the backside.
    Licensed residential and commercial plumber

  3. #3
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by tev9999 View Post
    Hello. I've been lurking here for awhile, working on a complete bathroom renovation. I'm taking a double sink bathroom down to a single (for accessibility). I have the following in the wall behind where the vanity will go.

    Name:  IMG_20120213_214632.jpg
Views: 782
Size:  44.8 KB

    I cannot budge the brass fitting on the left which ran to the old sink. Have not tried the one on the right yet. I only need one connection, and the one on the left works best for the new vanity layout. The pipe above is the vent to the roof, and the one below goes straight down to the soil stack.

    What is the best way to disassemble this thing without breaking the (freshly painted) wall in the other room? Tried WD-40 with no luck. Torch to the female iron fitting the next step?

    Thanks.
    Use some heat. The line your discontinuing,I would not cap in the wall. I would turn it out of the wall with a 90 ell and install a cleanout.

    Goodluck and if any more questions just ask.

  4. #4
    DIY Junior Member tev9999's Avatar
    Join Date
    Feb 2012
    Location
    Detroit, MI
    Posts
    29

    Default

    Quote Originally Posted by Hackney plumbing View Post
    Use some heat. The line your discontinuing,I would not cap in the wall. I would turn it out of the wall with a 90 ell and install a cleanout.

    Goodluck and if any more questions just ask.
    Thanks. Replacing the cross does not sound like fun. It has been trouble free for 40+ years. What problems could leaving it cause?

    I'll attempt to remove the pipe on the right coming out of the elbow - it would interfere with the vanity drawers anyway. Can I then just put the appropriate size plug into the elbow? It should be far enough back to not interfere.

  5. #5
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by tev9999 View Post
    Thanks. Replacing the cross does not sound like fun. It has been trouble free for 40+ years. What problems could leaving it cause?

    I'll attempt to remove the pipe on the right coming out of the elbow - it would interfere with the vanity drawers anyway. Can I then just put the appropriate size plug into the elbow? It should be far enough back to not interfere.
    I agree it has worked for years and will continue until the rest of the pipe goes bad. Sure plug it......use some heat and it MIGHT come right out.

    Goodluck,let us know how it goes.

  6. #6
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,245

    Default

    You should also realize the WD 40 is not a penetrating oil. PB Blaster is a great penetrating oil, but I' not sure that is the answer to you problem. Best heed HJ's advice.

  7. #7
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    I would be inclined to sawzall it out using a metal 618 blade and then installing a santee with mission couplings.

    The cross is the wrong fitting, if you ever plan on snaking that line in the future.

  8. #8
    DIY Junior Member tev9999's Avatar
    Join Date
    Feb 2012
    Location
    Detroit, MI
    Posts
    29

    Default

    A sawzall I can manage. Would I just cut above and below the cross and put in PVC with Fernco couplers? Would the vent pipe be supported in the attic or do I have to worry about it dropping and taking the roof with it?

    In reality, what is the probability that a drain line feed by a single sink that has never had to be snaked in 40+ years, dropping vertically 2 or 3 feet before opening into a 4" soil pipe will need to be snaked in the next 40 years?

  9. #9
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default Did I say Fernco?

    I didn't say Fernco.
    The Fernco at the hardware store is an illegal fitting that shifts and deforms. No plumber would use one, nor would any inspector pass the job if one was used.

    You can use Mission, with the stainless shielding, or ProFlex with the shielding.

    And golly, of course we worry about the future, we're plumbers.
    I change oil in my car too. Ya know............just in case.

    I'm sure a "handyman" would look at this much differently. I know they do because I wind up fixing their mistakes.
    Of course I make money off their mistakes too, so I shouldn't feel too bad about it.


    ProFlex with the metal backing to prevent shifting of the pipes.

    The vent may not be supported. You can look on the roof and see how your vent is done. Sometimes the pipe is through the roof, inside a lead flashing. Many times the pipe will drop downward if it's not supported. Sometimes I just run plastic from the tee up. There is less weight to worry about that way. Pipe is pennies per foot.
    Last edited by Terry; 02-14-2012 at 11:06 AM.

  10. #10
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    None of the fittings in that galvanized system would be considered correct by todays standards. IMO its lasted 40 years and it will continue to work until the pipe fails. Dropping that cross with a cable is 1st yr stuff.

  11. #11
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    Again,
    you can use the old cross fitting and plug one end of it in the wall, or bring it out, but why leave it in the wall at this point?
    It's such a simple job where the wall open to make it easier for whoever owns the home in the next forty years.

    Of course, you can also just leave it like Hackney would too. I'm not a big fan of leaving fittings in the wall like that if you are converting to a single lav. hj, who is two decades older then me wouldn't leave it either.

    I guess hj and I, the old guys would have loved to replace the cross with a santee. It would make a slick way of doing it. And we love working with pipe and fittings.
    Hackney on the other hand, likes it the way it is. I guess that's the way it is with the younger ones.

  12. #12
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by Terry View Post
    Again,
    you can use the old cross fitting and plug one end of it in the wall, or bring it out, but why leave it in the wall at this point?
    It's such a simple job where the wall open to make it easier for whoever owns the home in the next forty years.

    Of course, you can also just leave it like Hackney would too. I'm not a big fan of leaving fittings in the wall like that if you are converting to a single lav. hj, who is two decades older then me wouldn't leave it either.

    I guess hj and I, the old guys would have loved to replace the cross with a santee. It would make a slick way of doing it. And we love working with pipe and fittings.
    Hackney on the other hand, likes it the way it is. I guess that's the way it is with the younger ones.
    You dont think other fittings are in that system? If the cross was the last fitting and the rest was pvc then I would say ,"sure change the cross". But its not,there are more fittings under the floor. He could clean that cross out good when he gets the nipples out and it would be good. Getting a cable to drop down the cross wouldn't be a big deal unless it was just time to replace it all.

    My first choice was for him to turn the other side of the cross out of the wall with a 90 and install a cleanout.

    Sanitary crosses are perfectly legal where I pipe it up for this application.

  13. #13
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    I like to overbuild and underpay. The minimum requirements are for minimal people.
    I would cut out the cross and put in a sani-tee with a cleanout underneath it.

  14. #14
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by cacher_chick View Post
    I like to overbuild and underpay. The minimum requirements are for minimal people.
    I would cut out the cross and put in a sani-tee with a cleanout underneath it.
    I would replace it all but the vent and if they had any money I'd replace that too.

    I'd also like to remind you the plumbing code is minimum requirements and I agree they are minimal people.
    Last edited by Hackney plumbing; 02-14-2012 at 05:57 PM.

  15. #15
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    Given that the cost of scrap metal is currently as high as it is, recycling that stuff would pay for what you need in PVC.

Similar Threads

  1. how to remove the band of lead around cast iron pipe?
    By calavera in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 01-23-2011, 07:33 PM
  2. How do I remove broken cast iron closet flange from PVC pipe
    By Morbius in forum Toilet Forum discussions
    Replies: 6
    Last Post: 09-01-2010, 03:19 PM
  3. propane gas; black iron & galvanized pipe; brass ball valves; dielectric couplings
    By greyhound1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 07-29-2010, 06:50 AM
  4. cast iron fitting installed in cast iron soil pipe
    By web_surfer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 06-10-2009, 06:20 AM
  5. Mixing brass valves with iron pipe for gas
    By jastori in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 11-10-2008, 08:07 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •