Thread: Grounding Whirlpool Tub Motor and Heater - Bonding Panel to Electric Water Heater

  1. #1
    sea-bee chuck b's Avatar
    Join Date
    Jan 2011
    Location
    levering, michigan
    Posts
    72

    Default Grounding Whirlpool Tub Motor and Heater - Bonding Panel to Electric Water Heater

    Hello! Installing the above. Water comes from a well which supplies our small seasonal cottage through a pvc pipe into the cottage which transitions to copper by the expansion tank. I then progress to a sediment filter, water softener and then an electric water heater. The water heater is bonded to the electric panel, which is grounded to two stakes in the ground (not cement rebar). The water heater also has a jumper between the hot and cold pipes.
    Question: I noted that the water heater has a bonding clamp attached to the cold water side copper pipe. Is that the correct side for that. Then it travels to the electrical panel for bonding/grounding.
    Question: When I ground the whirlpool water heater and motor, can I just bond them both ( 2 separate clamps & 2 separate 20-amp circuits GFCI protected) to 2 clamps on the cold water side of the bathtub plumbing (cold is best right), or do I need to go all the way with both copper wires to the grounding rods? Guessing that the cold water lines are grounded via the bonding at the water heater which travels to the panel and subsequently to the grounding rods. Also, do I use the same gauge copper wire as the circuits they ground, i.e. 12 gauge for 20-amp circuit for grounding to pipes or do I use heavier gauge say a #10 copper wire? Thanks.
    Last edited by chuck b; 02-05-2012 at 06:10 AM.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    For the tub you are not grounding but you are bonding. This bond will be required to be a #8 and hit anything metal in the area of the tub and nothing is required to go to the rods

  3. #3
    sea-bee chuck b's Avatar
    Join Date
    Jan 2011
    Location
    levering, michigan
    Posts
    72

    Default

    Thanks. Even though the copper pipes transition to pvc and not to a cement in floor pipe ground like homes with a city water supply? Guessing that the metal bathroom bond does continue with an effective "bond" since there is a jumper cold to hot at the water heater, and then to the electrical panel. Am I making sense?

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    NO
    What you are doing at the tub is making the water in the tub and the metal objects around the tub at the same potential.

    Grounding has nothing to do with it.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    quote;

    NO
    What you are doing at the tub is making the water in the tub and the metal objects around the tub at the same potential.


    That is a matter of semantics. You can "bond" the metal all you want, but if it does not have a path back to "ground" it will not protect in case of a malfunction of the electrical system, and it could become "energized" without tripping the circuit breaker.
    Licensed residential and commercial plumber

  6. #6
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by hj View Post
    quote;
    NO
    What you are doing at the tub is making the water in the tub and the metal objects around the tub at the same potential.


    That is a matter of semantics. You can "bond" the metal all you want, but if it does not have a path back to "ground" it will not protect in case of a malfunction of the electrical system, and it could become "energized" without tripping the circuit breaker.
    popcorn time again
    I am definitely not a pro plumber, but I am a pro crastinator

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by hj View Post
    Quote Originally Posted by jwelectric View Post
    NO
    What you are doing at the tub is making the water in the tub and the metal objects around the tub at the same potential. Grounding has nothing to do with it.
    That is a matter of semantics. You can "bond" the metal all you want, but if it does not have a path back to "ground" it will not protect in case of a malfunction of the electrical system, and it could become "energized" without tripping the circuit breaker.
    HJ
    The purpose of bonding all metal around things such as whirlpool tubs, hot tubs, swimming pools, fountains, and other bodies of water is not to open the overcurrent device.

    The purpose is to form an equipontentail plane where the water contained inside the unit and any metal or concrete surrounding the equipment is at the same potential.

    This is like the Faraday cage in this link.
    http://www.youtube.com/watch?v=Dd40ASbGte0

    Notice that the man the air craft and the power line are at the same potential and there was nothing connected back to the source in order to open the overcurrent device.

    The equipment grounding conductor installed with the circuit supplying the pump motor is what will open the overcurrent device not the bonding of all metal and the water.

Similar Threads

  1. Baseboard electric heater & switch distance from whirlpool bathtub?
    By chuck b in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 01-27-2012, 11:50 AM
  2. Bonding Water Heater
    By chuck b in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 07-01-2011, 06:02 PM
  3. bonding/grounding and pex
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 10-23-2009, 05:39 AM
  4. whirlpool tub motor grounding
    By lee polowczuk in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 10-12-2007, 10:41 AM
  5. Grounding, bonding, potential??
    By hammerslammer in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 08-21-2007, 09:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •