    Must all range outlets be 50 amp plugs with 6 gauge or larger wire, or may I use 8 gauge wire if I have a range that has a maximum draw of 38 AMPS? Using thhn copper in conduit for the run, about 30 feet.

    I would guess the answer is what will the next guy plug into it, or is there a dedicated 40 amp plug-cord set?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,408

    Default

    Can't help on the gauge, but keep in mind any new wiring should be for a four-wire plug: two hots, neutral, and ground. Only when you are reusing an existing 3-wire circuit can you keep it, not on a new one. this may affect the size of the conduit you use.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Using #8 THHN copper you could use a 50 amp breaker and receptacle but if you wanted to you could use a 40 amp breaker and receptacle.

    I doesn’t matter what “might” happen with someone else all that matters is what you are connecting at the time.

    The one thing I always teach to the inspectors that take my class is that they are inspectors not expect-ors so what might happen does not matter.

  4. #4
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Apparently there is such a thing as a 40 amp plug and cord, according to this offered by whirlpool: http://www.ajmadison.com/cgi-bin/ajmadison/PT220.html

  5. #5
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    Quote Originally Posted by ballvalve View Post
    Apparently there is such a thing as a 40 amp plug and cord, according to this offered by whirlpool: http://www.ajmadison.com/cgi-bin/ajmadison/PT220.html
    that is a 3 wire plug, not a 4 wire. (just so you are aware if you didn't notice)

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    #8 wire is marginal for your range, but if you use it, then connect it to a 40 amp breaker, regardless of the amp rating of the receptacle.
    Licensed residential and commercial plumber

  7. #7
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by ballvalve View Post
    Apparently there is such a thing as a 40 amp plug and cord, according to this offered by whirlpool: http://www.ajmadison.com/cgi-bin/ajmadison/PT220.html
    That is true. Standard NEMA receptacles for 120/240 appliances are 30 amp and 50 amp. Of course, you can use a 20 amp, or 40 amp, breaker as the appliance dictates. Wiring must be sufficient for the receptacle used, not just for the breaker.

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Gentlemen

    The breaker is installed to protect the conductors not the receptacle. It would be perfectly legal to install a 40 amp breaker and a 50 amp receptacle for a range Table 210.21(B)(3).

    What would not be legal would be to install a 50 amp breaker and a 40 amp receptacle.

    Many AC units throughout this nation are wired with less than a 60 amp conductor and overcurrent device that land in a 60 amp no-fuse disconnect legally.

  9. #9
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by jwelectric View Post
    Gentlemen

    The breaker is installed to protect the conductors not the receptacle. It would be perfectly legal to install a 40 amp breaker and a 50 amp receptacle for a range Table 210.21(B)(3).

    What would not be legal would be to install a 50 amp breaker and a 40 amp receptacle.
    Absolutely correct. I have never wired up a 40A recpt for a range. Never. Not once.

    Many AC units throughout this nation are wired with less than a 60 amp conductor and overcurrent device that land in a 60 amp no-fuse disconnect legally.
    That's different, they don't plug in. ;-)

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    A receptacle and a cord cap is nothing more than a means of disconnect. Other than the physical shape of the two there is no difference between a receptacle and a no-fuse disconnect

Similar Threads

  1. "Wet" changing electric water heater elements.
    By ballvalve in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 10-08-2010, 11:01 AM
  2. Is there a plumbing equivalent to Richter's "Practical Electrical Wiring" book?
    By jadziedzic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 05-14-2010, 01:32 PM
  3. Electric motor wiring ?
    By WV Hillbilly in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 12-19-2008, 08:23 AM
  4. Clamping Range of 2" FERNCO
    By bcs001 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-09-2007, 01:55 AM
  5. Electric "table top" water heater.
    By Robert Ragaini in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 03-03-2006, 09:01 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •