Thread: Multiple Hot Water Heaters

  1. #1
    Advanced DIYer Offbalance's Avatar
    Join Date
    Jan 2012
    Location
    Snohomish, WA, USA
    Posts
    5

    Default Multiple Hot Water Heaters

    Hey everyone -
    I have a question on multiple HWHs installed in my residence. When I bought the house it had two 40 gallon electric HWHs plumbed in series. It's a large house, and we have two teenage kids and relatives that visit for long periods. We have always enjoyed the voluminous amounts of hot water.

    The HWHs were Rheem, with S/Ns of 1191****** (the house was built in 1992, so that makes sense). In 2000, I did some remodeling and at that time attempted to check/replace the anodes, dip tubes, etc., but was unable to break them open. This summer, the second HWH in the series failed with rusty water leaking out the top electrode. I simply removed it from the circuit, and have been relying on the first heater. This setup seems to be working fine (provided, of course, that I get to the shower every morning before my daughter).

    During the recent winter storm we had an extended power outage, and I decided I want to put a second HWH back in the circuit. I plan to wire the second HWH to my garage electrical subpanel where my generator transfer switch is located so I can have at least some hot water during the next extended power outage. I am considering the GE 9-year electric 50 gallon from HD as it seems the best value for what you get. I would then replace the first HWH in the series within a year or so, as the budget allows, with a similar one under the assumption that it will probably fail soon as well.

    Before I jump into this, I have a few questions:

    1. Is it better to plumb two tanks in series rather than get one larger tank? It seems an 80 gallon tank costs more than two 40s or 50s.
    2. Is plumbing them in series (vs parallel) the right way to go?
    3. Is it OK to have two HWHs of different sizes (40+50) plumbed in series?
    4. Am I correct in wiring the second one to the generator transfer switch so that if I lose power and am running off backup power I don't have to run through 40 gallons of cold water before I get hot water?
    5. We have propane F/A furnaces, one of which is next to the HWHs. Should I consider propane for the second HWH? This would be nice in a power loss situation, but I have not had very good luck with propane HWHs in the past. And I have had to replace the propane valves on the furnaces, fireplaces, etc. on a fairly frequent basis around here. And I haven't heard too good of stories about the new gas HWH FVIR thingamajigs.
    6. Are there other considerations I should consider?

    Thanks all for your input.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    The size of the two tanks wouldn't matter if run in series.
    The elements are the same wattage. The electrical panel won't know the difference.

    Having two tanks means you have twice the recovery. A single 80 gallon has one element working at a time.
    With two tanks, you can double that.

    Of course, you also have more exterior space with two tanks that need insulating. Most of the time we would just install a single eighty.
    Twenty years from a water heater? That's pretty darn good.
    Last edited by Terry; 01-29-2012 at 09:07 PM.

  3. #3
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    The tanks should be identical in everyway for a parallel configuration.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    1. With two heaters in series you get TWICE the input wattage, compared to a single heater.
    2. It is the way I ALWAYS install them
    3. In series each heater is independent. They can be any sizes and even a mix of gas and electric.
    4. it would be the smart thing to do with two electric heaters
    5. i have had a propane heater for over 12 years and have had to do ZERO maintenance to it.
    Licensed residential and commercial plumber

  5. #5
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    If you buy the cheap HD variety, change the anode or at least check its length. Most are 1/2 the length possible. Remove the plastic drain and put in a ball valve, I got one cross threaded that would have flooded a house.

    http://fierychill.com/catalogsearch/result/?q=anode

    I would use the .90 magnesium. You could cut off the original one and drop it into the heater.

    And you need a impact wrench to get out the old rods, but for stuck elements, a good chisel and hammer can break the rust if you have good geometry.

    Better have a BIG genset to run a water heater.
    Last edited by ballvalve; 01-30-2012 at 10:13 AM.

  6. #6
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Speaking of generators running water heaters,After a hurricane we had I changed my 4500 watt element out for a 1500 w to heat my water once a day. I just direct wired it to the element and let it run until the bottom of the tank got hot. Works great.

  7. #7
    DIY Senior Member Runs with bison's Avatar
    Join Date
    Aug 2009
    Location
    Midwest
    Posts
    892

    Default

    Quote Originally Posted by Terry View Post
    The size of the two tanks wouldn't matter if run in series.
    The elements are the same wattage. The electrical panel won't know the difference.

    Having two tanks means you have twice the recovery. A single 80 gallon has one element working at a time.
    With two tanks, you can double that.
    Would it be best (greatest effective recovery rate/volume) to set the second tank a few degrees higher in set point than the first tank? If you set them the same then for the first several minutes only the elements on the first tank will run. But if the second is set incrementally higher, its thermostat should kick in much sooner. In effect you reduce the lag for the second tank starting its heating cycle.

  8. #8
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    To get the maximum stored water out of your water heater,pipe the incoming line to the drain valve location. Install an alternate drain. Beware of thermal stacking if you pipe the cold to the bottom as this chance increases.

    This also allows you to bypass the 5/8 dip tube common to residential tank water heaters,this allows a higher flow rate. Make use of this extra top inlet for an extra anode rod.

  9. #9
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Actually, you could have just wired the element to 120 volts and had a 2250 watt heater. I do it regularly for low use, shop type units.... and the elements last forever.

  10. #10
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by ballvalve View Post
    Actually, you could have just wired the element to 120 volts and had a 2250 watt heater. I do it regularly for low use, shop type units.... and the elements last forever.
    That would have tripped my rig. I used a 1500 w

  11. #11
    Advanced DIYer Offbalance's Avatar
    Join Date
    Jan 2012
    Location
    Snohomish, WA, USA
    Posts
    5

    Default

    My genset will handle the 4500 Watt elements, but probably not if both fridges, the septic pump and the furnace all decide to start at the same time, so I may put the HWH on a separate transfer switch.

    And yes, Mr. Ballvalve, I had already planned to replace the cheesy plastic drain with a real ball valve as I have always done before. I'll check the anode rod tomorrow, and order one if necessary.

    Thanks everyone for your input!

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    quote; I'll check the anode rod tomorrow, and order one if necessary.

    The only time I would check my anode rod was after the tank was taken out., My replacement for a "spent" anode rod is a 3/4" brass plug.
    Licensed residential and commercial plumber

  13. #13
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by hj View Post
    quote; I'll check the anode rod tomorrow, and order one if necessary.

    The only time I would check my anode rod was after the tank was taken out., My replacement for a "spent" anode rod is a 3/4" brass plug.
    Is that because you have the best anode rod and or water heater in the world or is it that you have good water?

  14. #14
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    Quote Originally Posted by ballvalve View Post
    Actually, you could have just wired the element to 120 volts and had a 2250 watt heater. I do it regularly for low use, shop type units.... and the elements last forever.

    Not quite. A 4500 W element that is designed for 240v, will see 1125 W when connected to 120v. For a fixed resistance, when you cut the volts in half, you also cut current by half. This results in 1/4 the power.

    If you wired the top/bottom elements in parallel and used 120v, then you would get 2250 w from the two elements.

  15. #15
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    I notice 4500 watt elements run on 208 volts give 3500 watts, therefore your math works.

    So that makes Hackneys removal of the element unneeded, and explains my lifetime elements.

    Maybe HJ has his anodeless heaters hooked up to 120 volts.

    This link does not work, but it and several other 'expert forums' also use the 2250 wattage on half voltage.

    http://en.**********.com/q/Electrica...er-element.htm
    Last edited by ballvalve; 01-31-2012 at 12:41 PM.

Similar Threads

  1. Multiple problems with water heater(maybe)?
    By bcdudley in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 01-19-2012, 05:32 PM
  2. Help! Multiple hot water problems.
    By ForrestGump in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 05-03-2008, 04:59 AM
  3. multiple water-heater instalation
    By rrich4814 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-19-2008, 03:43 PM
  4. Multiple Water Heaters Anyone??
    By John Aull in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 19
    Last Post: 04-01-2006, 03:06 AM
  5. Multiple water heaters needed
    By Habitat.pat in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-29-2005, 11:18 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •