    Default Shower drain re-venting question

    I recently relocated a shower in my master bath and now I need to tie the 2" drain into the 1 1/2" vent again. The vent stack is only 3 feet away but I can't go up above the subfloor anymore). So I only have 5 inches of space above the drain line to work with. Is 5 inches enough of a drop for a vent before I add a 90 and run it over to the original stack?

    Thanks,
    James

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    A vent line needs to be sloped so it doesn't fill up with water and close off the venting. Both drains and vent lines should have 1/4"/ft slope. Not sure I understand your full question or planned result. Maybe a picture or a diagram would help.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member se7en's Avatar
    Join Date
    Jan 2012
    Location
    Vancouver, BC
    Posts
    2

    Default

    Thanks, I understand the slope. The issue is, that normally the vent would go straight up off the drain pipe (either straight to the roof or take a 90 degree turn over to a vent stack that does go to the roof, and I'm looking for the minimum height the vent should come up off the drain pipe before that 90 degree turn....

    I'm trying to keep the vent pipe within the joist, so I can only come up about 5 inches before the 90 degree turn over to the vent stack. Is that acceptable?

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,193
    Blog Entries
    1

    Default

    The trap arm can be 60" long before the vent.
    It's best to revent at 42" above the floor.

    If the vent is being washed by a fixture lave a lav, then it can be lower then that for a while.

Similar Threads

  1. Shower and Toilet Venting Question
    By David1980 in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 01-03-2012, 05:02 AM
  2. New shower venting question
    By jwbr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 11-30-2010, 01:40 PM
  3. drain/venting question
    By rbird7282 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-01-2008, 05:32 PM
  4. Tub to Shower - Venting Question
    By chanle51 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 11-27-2006, 08:22 AM
  5. Venting/drain slope question
    By slb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-18-2005, 10:46 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •