Thread: dwv layout review

  1. #1
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default dwv layout review

    Hi, I'm looking for a little feedback on updating my dwv. I've attached 2 images, one is the floor plan, basically two stacked bathrooms and kitchen right next to the first floor bath room. Currently there are no vents for the shower, tub and laundry, there is no laundry sink, and the vent for the kitchen sink is about 6" below the the flood line instead of above. Also, there is a mix of cast iron, pvc and copper. I'm hoping to fix all of that. I'd like to start with just the layout out so assuming the correct pipe size, slope and connections how does this look?

    http://imageshack.us/photo/my-images/80/15448964.jpg/
    http://imageshack.us/photo/my-images/718/29139244.jpg/

    Thanks,
    Teeman

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,531

    Default

    IT looks good. We have to take your word for it that it is the best design, however.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    No way! So you're say that the venting would be correct? I mean, I know there is still a lot that I need to figure out ie sizes and fittings etc. but.. I read these type posts a lot and I don't think I've ever seen a " it looks good" as the first reply. Wait, you not joking with me right?

  4. #4
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    FYI this is what it looks like right now.

    Name:  untitled3.jpg
Views: 177
Size:  18.2 KB

  5. #5
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    So I've added the fittings. I assume everything needs the 1/4" per 4' slope, down for drains and up for vents?

    Should I use wyes and 45s for the combo y 1/8?
    The elbow at the bottom of the two sinks stack, what should I use there?
    thanks,

    Name:  dwv4.jpg
Views: 178
Size:  39.0 KB

  6. #6
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    Any issues with my fittings?

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,531

    Default

    Somebody must have coached you since the first drawing. Most of the vents only have to be 1 1/2" pipe, but 2" is okay. Combo or Y and 1/8 bends are equal.
    Licensed residential and commercial plumber

  8. #8
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    I have been doing a lot of reading and forum lurking for awhile now. For the vents, if most can be 1 1/2" which ones HAVE to be 2". I'm guessing that most of them can be 1 1/2" until a few merge together on the upper floor?

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,531

    Default

    Toilet vents normally have to be 2", and it depends on the fixture load when the merged 1 1/2" lines have to become 2".
    Licensed residential and commercial plumber

  10. #10
    DIY Junior Member teeman11's Avatar
    Join Date
    Mar 2006
    Location
    Pennsylvania
    Posts
    22

    Default

    So the toilet + shower vent on the first floor remains 2" and the toilet + tub/ shower on the second floor remains 2". The other vent stack is sinks, the one on far left is a kitchen sink which ties into the first floor bathroom sink, and then the second floor bathroom sink can all of that be 1 1/2"? Also, the laundry vent needs to be 2" right?

    Thanks,
    T

Similar Threads

  1. Basement Plumbing Layout Review
    By jpb123 in forum Plumbing Forum Discussion & Blog
    Replies: 9
    Last Post: 01-25-2012, 04:29 PM
  2. Distance from fixture to roof vent stack layout review (not distance from p-trap)
    By kmuddzy in forum Plumbing Forum Discussion & Blog
    Replies: 11
    Last Post: 12-01-2011, 10:21 AM
  3. Looking for a layout review
    By NH in forum Plumbing Forum Discussion & Blog
    Replies: 19
    Last Post: 11-28-2011, 05:28 AM
  4. AAV Layout for Basement 3/4 Bath- Please Review
    By nwbearcats98 in forum Plumbing Forum Discussion & Blog
    Replies: 6
    Last Post: 12-20-2005, 11:02 PM
  5. DWV Layout - Please Review
    By sjsmithjr in forum Plumbing Forum Discussion & Blog
    Replies: 12
    Last Post: 12-16-2005, 05:19 AM