    Question weil mclain boiler with intermittent ignition

    My husband and I recently bought a home that uses a gas fired Weil McLain cast iron steam boiler with intermittent ignition. I was told that it should be partially drained every so often to remove the "brown" clogging sediment. Does anyone know how to do this? We don't know which valve to turn.

    Additionally, whenever the boiler starts up it makes a banging noise. Is this a problem? The noise also seems to have become louder after I mistakenly filled the test tube apparatus (indicating the water level) a little too much. Is there cause for concern? Does anyone have any suggestions on what to do AND how???

    Thanks.

    Stephanie

  2. #2
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Default

    GO TO THIS WEB SITE FOR HYDRONIC QUESTIONS

    http://www.heatinghelp.com/forum-cat.../THE-MAIN-WALL

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    Intermittent ignition is unrelated to any sludge or overfill and IS a real problem. If the banging noise is gas-explosions due to faulty ignition it's in fact a serious hazard. Have a pro deal with ignition issues.

    If the banging noise is condensed water flowing back from the radiators and "exploding" when it drips into a vertical pipe filled with superheated steam it's annoying, but not necessarily a problem, but it may be reduced by lowering system pressure and adjusting the air valves if somebody has been monkeying with it.

    Overfilling the boiler isn't likely to affect that issue one way or the other though, but draining it down to a proper level (about midway on the sight gauge) is still important. There's usually a triangle-shaped casting with a valve handle on it near the sight gauge for blowing sludge and draining down. See: http://www.youtube.com/watch?v=iDxofrGeeEw

    If the boiler is in decent shape it's probably worth hiring somebody to re-commission the system and show you how to adjust the air valves, drain down the sludge, etc. Many systems have been over-tweaked to higher than necessary steam pressures, which can aggravate radiator bang issues. People seem to do that when the air-valve on some radiator isn't venting right and they think it needs more pressure or something. (1/2-1 psi is plenty for a residential system.) If you want to learn to adjust and maintain it yourself, buy this book. Set up properly they're quieter, more efficient and more comfortable.

    There are plenty of youtube steam boiler maintenance vidis that may be a useful way to familiarize yourself with the system. (I haven't screened more than a couple of them- do your own searches, but there's plenty of DIY video out there that works better than 10,000 words and paper diagram.)

Similar Threads

  1. Old mclain weil boiler with electronic ignition slow to start
    By patzeram in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 11-19-2010, 02:41 PM
  2. Boiler Question: Weil Mclain
    By cgm55082 in forum Boiler Forum
    Replies: 5
    Last Post: 02-07-2009, 06:15 PM
  3. Intermittent ignition on W-M boiler, Beckett AF oil burner
    By Baltimore Lou in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 12-03-2008, 05:14 PM
  4. Weil mclain boiler not lighting
    By shluffer in forum HVAC Heating & Cooling
    Replies: 9
    Last Post: 11-25-2008, 04:25 AM
  5. Weil-McLain Ultra Boiler
    By jadnashua in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 09-23-2004, 06:48 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •