Most older boilers were grossly oversized. Many calculators are as much as 100% over the 'real' need. A better solution for this house would be to compare the actual oil used verses the heating degree-day for your location. No idea if that brand and model is good or not...
If a lot of the insulation/window upgrades were made after the last heating season, your new calcs may no longer be accurate.
Generally, there's no need to oversize a boiler to provide DHW unless it is a commercial situation where there's significant hot water useage all day long. It's generally run on a priority zone, and uses all of the boiler's output while heating the DHW, then reverts back to space heating when that's done. The homeowner will rarely notice that short gap.





Reply With Quote
At least I was able to use a two stage furnace, so it almost never runs in high fire mode.