If the ground was connected properly then you should not get shocked even if the AC polarity was reversed.


Did you get it wired correctly ?
 

BobL43

DIY Senior Member
Messages
1,802
Reaction score
8
Points
38
Location
Long Island, NY
If the ground was connected properly then you should not get shocked even if the AC polarity was reversed.


Did you get it wired correctly ?
It may have been just capacitance building up voltage on the fridge's frame without any real conductance, or, on the other hand, a leakage current from the circuits in the fridge and enough to give a good tingle or more; still, can't be too safe without a gound to drain it away or trip a breaker if it was a real short to the frame from the hot.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I would have expected it to pop the breaker, just as soon as plugged in. Or it has no Proper Ground.

I think there is more to this picture.

I have some Popcorn.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
The electrician rewired the outlet. There is no ground wire and the wire is two insulated wires wrapped in a rubber/plastic type coating.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Originally Posted by ballvalve

Thats a harbor fright $1.99 tester, but they actually work, though not likely safely. I regret to admit I have several spread about in odd places where one need not hunt for the 'real' one.

Can't afford to buy new batteries for that price.

A Cat II is fine for around the house.

You don't even have to stand on them spare tires.

Whats terrifying is that they came WITH a battery and actually work.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
The electrician rewired the outlet. There is no ground wire and the wire is two insulated wires wrapped in a rubber/plastic type coating.

Ah. Old non-metalic cable without a ground. I found a bit of that in a house in Pasadena. I think the wire dated to the '40s or early 50's, to judge from the other elements that I saw.

There was a good bit of knob and tube in the house as well. Apparently there is quite a bit of that left in Pasadena and the towns around it. A real pain when combined with lath and plaster.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
It may have been just capacitance building up voltage on the fridge's frame without any real conductance, or, on the other hand, a leakage current from the circuits in the fridge and enough to give a good tingle or more; still, can't be too safe without a gound to drain it away or trip a breaker if it was a real short to the frame from the hot.

Sounds like you were correct Bob.

If there is no ground connection in the box then you would be measuring the device leakage.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
Request for more interpretation

I may be misreading the posts, but although the outlet has been rewired, can the fridge still shock someone?

Thanks,
Bill
 

BobL43

DIY Senior Member
Messages
1,802
Reaction score
8
Points
38
Location
Long Island, NY
I may be misreading the posts, but although the outlet has been rewired, can the fridge still shock someone?

Thanks,
Bill
It definitely is possible. Take a voltmeter and take an AC volt reading from the frame of the fridge to a ground connection (water pipe, or ground from another outlet that has a ground). If you can measure (hard for me to say how much voltage will give you a feelable shock) 24 volts or more, than you might feel a tingle if its just capacitance as I said above. If there is a real short circuit from the hot circuits in the fridge to its frame, then it will be dangerous. I guess your electrician must have checked this out for you in the name of safety?
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
@molo: Unless there was some connection between the fridge frame and one of the electrical conductors, it would not be possible for
anyone to get a shock from it. That is the root cause of the problem. If the receptacle was miswired (reverse polarity), it is all well and good
to correct that problem, but the fault in the fridge remains. If, for instance, there is a short between what is now the grounded conducter (neutral)
and the fridge frame, then at present there is no shock hazard; however, by simply reversing the power cord plug in the receptacle the fridge frame
would again become energized. More indirectly, any modifications to the circuit feeding that receptacle that alters the polarity (very common in ungrounded
house wiring systems, unfortunately) would also recreate the shock hazard. I am rather astonished that the electrician did not address the fridge wiring
problem, where the real problem lay. A receptacle with reversed polarity in an ungrounded wiring system is really a minor defect, and extremely common.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
It definitely is possible. Take a voltmeter and take an AC volt reading from the frame of the fridge to a ground connection (water pipe, or ground from another outlet that has a ground). If you can measure (hard for me to say how much voltage will give you a feelable shock) 24 volts or more, than you might feel a tingle if its just capacitance as I said above. If there is a real short circuit from the hot circuits in the fridge to its frame, then it will be dangerous. I guess your electrician must have checked this out for you in the name of safety?

Shouldn't the shell/handle be insulated from the current conducting components of the fridge (motor, wiring)? It seems a very dangerous design otherwise. The hinge on the freezer handle caused the original shock. Can this happen without a short in the fridge?
 

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
Shouldn't the shell/handle be insulated from the current conducting components of the fridge (motor, wiring)? It seems a very dangerous design otherwise. The hinge on the freezer handle caused the original shock. Can this happen without a short in the fridge?
Can this happen? Yes

Can this happen without something being wrong with either the fridge or the circuit it is plugged into? No.
 

Bobelectric

Electrical Contractor
Messages
39
Reaction score
0
Points
6
Location
Eighty Four,Pa. 15330
I can't understand the replys to this tread. Sounds like repair guy f*** up. Refers don't bond to frame. A circuit with an adapter to plug into a non grounding receptacle.Hot frame.
 