Thread: Slope of 4 PVC sewer line under slab

  1. #1
    DIY Junior Member randym1954's Avatar
    Join Date
    Jan 2012
    Location
    Washington DC
    Posts
    2

    Default Slope of 4 PVC sewer line under slab

    I have dug my basement deeper and will have a toilet connecting to a 4 pvc sewer line under the slab that runs 45 to an ejector pit. I know the current rough-in does not meet code but, assuming it passes inspection, I am wondering if it is good enough as my contractor claims. On average the slope of the line is almost precisely per foot, but the slope varies. The first 10 is 0.17 per foot, the next 6 that is between two 45 degree turns is 0.41 per foot, the next 24 is 0.27 per foot, and the last 5 into the pit that begins with a 25 degree turn is 0.11 per foot.

    A drawing is attached.

    Should I insist that it be redone?

    Thanks.
    Name:  plumbing_slope.jpg
Views: 409
Size:  65.3 KB

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,192
    Blog Entries
    1

    Default

    It's up to the inspector; they like to see 1/4" per foot on 3" and 4"
    On 4", they sometimes let you get by with 1/8" per foot.

    The sections with more slope are not an issue.

  3. #3
    DIY Junior Member randym1954's Avatar
    Join Date
    Jan 2012
    Location
    Washington DC
    Posts
    2

    Default

    Thanks Terry. My objective is a trouble-free sewer line, not necessarily inspection approval. In your experience, do you think the system as currently designed is likely to be trouble-free?

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    My concern is that there can always be some movement, particularly if the groundwater level ever rises close to the level of the excavation. If the pipe is bedded in well it will probably be fine, but I would feel better knowing there is more pitch than required rather than less.

    There must have been a good reason for not placing the basin close to the bath to avoid all the underfloor piping.

Similar Threads

  1. Under slab sewer line fix in progress... are they doing it right?
    By kallisti5 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 09-22-2011, 09:57 AM
  2. Sewer line slope
    By coastalredwood in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 07-04-2008, 07:51 AM
  3. Sewer Line Under Slab - New Construction
    By Steve20A in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 05-31-2007, 05:09 PM
  4. Slab Over Sewer Line?
    By nicad2 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 04-04-2006, 12:49 PM
  5. Under slab sewer line repair
    By Slabhome in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 09-23-2004, 09:32 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •