Adding Glycol to snow melt system

Users who are viewing this thread

thompsonblake

New Member
Messages
7
Reaction score
0
Points
0
Location
Nova Scotia
Currently working on installing a closed loop snowmelt system for a driveway roughly 38x18. Using 3 loops (1 zone) at around 300 feet runs (3/4 HePex, 9 inch centres) Im adding this system to an existing boiler that does have enough BTUs to heat the system. Laying the pipe and building the headers is fairly straight forward and I have done countless times. However my journeyman has always handled the more detailed boiler work such as, pump size, heat exchanger, expansion tank size. More importantly i have calculated that i need a 40% glycol mixture but am not sure the best method for adding and maintaining the glycol in the system.

Any help would be appreciated but i guess I'm looking for the best method for adding glycol and maintaining glycol levels, and possibly a simple diagram boiler system.
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
possibly a simple diagram.


This is what they use down south of you. They work good.


Snow_Shovel.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
When I ran a system with antifreeze in it, when the techs filled it, they first determined how much they needed, then they had a hose bib on the suction side of the pump, put a hose on it and sucked the required amount of antifreeze in from the bottles, then turned on the autofill to fill it the rest of the way with water. So, if you figured the tubing was a long cylinder, figured its volume in cuin, then divide by 231, you'd have gallons.

Unless you run the external system off of a heat exchanger, that means adding the antifreeze to the whole system as well, so you need to figure that volume out, too. A heat exchanger is probably not a bad idea. Also, keep in mind that the antifreeze DECREASES the efficiency of heat transfer, so in effect, the boiler doesn't look as big as if you were using all water. This also may affect the spacing and lengths of your radiant loop(s). I don't remember that factor, but you should be able to find it if you search a bit...I think it was in the 10% range, but don't quote me.
 

thompsonblake

New Member
Messages
7
Reaction score
0
Points
0
Location
Nova Scotia
Thanks for your help Jim, i think the heat exchanger sounds best as well as i don't want to decrease the efficiency off the whole system by running glycol through it. Would a heat exchanger with a closed loop from the boiler on one side and the supply to my smowmelt headers on the other, be enough to heat the system properly? There are detailed installation instructions on the uponorpro tutorials page but they really only deal with systems that are strictly for snowmelt.
 