  1. #1
    DIY Junior Member thompsonblake's Avatar
    Join Date
    Jan 2012
    Location
    Nova Scotia
    Posts
    7

    Question Adding Glycol to snow melt system

    Currently working on installing a closed loop snowmelt system for a driveway roughly 38x18. Using 3 loops (1 zone) at around 300 feet runs (3/4 HePex, 9 inch centres) Im adding this system to an existing boiler that does have enough BTUs to heat the system. Laying the pipe and building the headers is fairly straight forward and I have done countless times. However my journeyman has always handled the more detailed boiler work such as, pump size, heat exchanger, expansion tank size. More importantly i have calculated that i need a 40% glycol mixture but am not sure the best method for adding and maintaining the glycol in the system.

    Any help would be appreciated but i guess I'm looking for the best method for adding glycol and maintaining glycol levels, and possibly a simple diagram boiler system.
    Last edited by thompsonblake; 01-20-2012 at 07:41 AM. Reason: typo

  2. #2
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    Quote Originally Posted by thompsonblake View Post
    possibly a simple diagram.

    This is what they use down south of you. They work good.


    Name:  Snow_Shovel.jpg
Views: 479
Size:  1.2 KB
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    When I ran a system with antifreeze in it, when the techs filled it, they first determined how much they needed, then they had a hose bib on the suction side of the pump, put a hose on it and sucked the required amount of antifreeze in from the bottles, then turned on the autofill to fill it the rest of the way with water. So, if you figured the tubing was a long cylinder, figured its volume in cuin, then divide by 231, you'd have gallons.

    Unless you run the external system off of a heat exchanger, that means adding the antifreeze to the whole system as well, so you need to figure that volume out, too. A heat exchanger is probably not a bad idea. Also, keep in mind that the antifreeze DECREASES the efficiency of heat transfer, so in effect, the boiler doesn't look as big as if you were using all water. This also may affect the spacing and lengths of your radiant loop(s). I don't remember that factor, but you should be able to find it if you search a bit...I think it was in the 10% range, but don't quote me.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Junior Member thompsonblake's Avatar
    Join Date
    Jan 2012
    Location
    Nova Scotia
    Posts
    7

    Default

    Thanks for your help Jim, i think the heat exchanger sounds best as well as i don't want to decrease the efficiency off the whole system by running glycol through it. Would a heat exchanger with a closed loop from the boiler on one side and the supply to my smowmelt headers on the other, be enough to heat the system properly? There are detailed installation instructions on the uponorpro tutorials page but they really only deal with systems that are strictly for snowmelt.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    This brochure might help decide what's needed http://www.taco-hvac.com/uploads/Fil...ry/200-2.3.pdf. Once you figure how many BTU's you need, and the working temps, you can size it properly.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Hot Water heat - Glycol? Other closed-system option?
    By LeBlanc in forum HVAC Heating & Cooling
    Replies: 26
    Last Post: 11-30-2009, 03:53 PM
  2. Adding Storage Tank To System?
    By Vietnam1947 in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 09-15-2009, 05:09 PM
  3. Adding a zone system...
    By GrantK in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 11-05-2007, 07:21 AM
  4. Waterheater/snow melt
    By jphillips in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 11-14-2006, 09:56 PM
  5. Adding to a Monoflow Heating System
    By angtort in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-08-2005, 04:44 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •