    Default Electrical Boiler

    We are in upstate NY where electricity is cheap.
    We are planning to change out the boiler in our bungalo and have choosen to go with an electric boiler.
    This way we can remove the dilapitated chimney and simplify installation.

    The boiler we are leaning to is a Slant Fin Monitron EH24M2 which is listed at 100amps at full load. It is also 82,000btu on single phase.
    My husband wants to go with #2 Romex wire on a 100amp breaker for the installation.
    Since we only want to do this once, I thought I'd get the opinion of the folks on this site.

  2. #2
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    Is the current boiler gas? oil? What do you pay per kwh of electricity vs. how much per therm of gas or gallon of oil?

    On the heat strips for my heat pump (on 100A breaker), I used #2 THHN copper (I could have used #3, but the place that I got it from only had #4 and #2 by the foot). Having individual conductors in conduit was easier than trying to fight with larger SE cable (often aluminum). I would probably use THHN or similar, but cable might be cheaper.

    Before you go down this road, there are a few things to check:
    1. cost of operation. How does electric compare to other sources? How might the price of electricity change in the future compared to other fuels?

    2. Can your current electrical service handle an additional 100A load? If it wasn't installed with the assumption that an electric furnance/boiler would be installed, it is probably undersized for the load. You would then need a service upgrade to handle the additional load.

    3. There are many types of boilers and you may find something that will ease the chimney issue and installation and not require going to electric

    4. This is a good time to look at the size of boiler that is really needed. There are some calculations that can estimate the need, but the more accurate method is to look at how much fuel you used during a heating season along with your location to see what the real heat load is. Your old boiler may have been greatly oversized (often the case) and you may be able to go much smaller (save on initial costs as well as operating costs).

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    My father used to live in Fairport, where the elecric rates were quite inexpensive (Niagra Falls generates a lot of electricity cheaply). He ended up with a heatpump system. While it got cold there, it didn't need to run the resistance heater that often. This may end up a better deal for you than an electric boiler...a heat pump gives you more heat than straight reistance heaters do plus, it would give you a/c for the hot, sticky days in summer when you want it. If you don't have ductwork, there are ductless systems that work quite well with at least some room layouts, or high velocity ducts that care fairly easy to retrofit.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    As has been pointed out be sure that your service will carry the load.

  5. #5
    DIY Junior Member technogirl74's Avatar
    Join Date
    Dec 2010
    Location
    ny
    Posts
    17

    Default

    We had the service redone after the tropical stroms that ripped through.
    200 amp service.

    We are going with the electric boiler as we can get one for a really really good price.

    JW Electric, were not asking how to do it but do you forsee any problems with going with #2 romex / SER cable
    and putting it on a 100 amp breaker?

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    2 copper NM-B or 2 SE-R copper is good for 95 amps. As long as the boiler ampacity is below 76 amps then installing it using #2 with a 100 amp breaker will be fine.
    If the heating elements are rated at more than 48 amps and the boiler does not have an ASME stamp on it then the maximum ampacity cannot exceed 60 amps. If the boiler does not have an ASME stamp and the elements are rated more than 48 amperes the load has to be divided into loads that does not exceed 60 amps. This can be done inside the control panel of the boiler by having fuses or breakers that subdivide the loads.

    Once again please do a service load calculation to be sure that it will handle the new load. Remember that the boiler is to be figured at 125% of its ampacity.

  7. #7
    DIY Junior Member technogirl74's Avatar
    Join Date
    Dec 2010
    Location
    ny
    Posts
    17

    Default

    JW,

    Not exactly following you on your post.
    This much I know.
    The 200 amp service to the house is for a future home we plan to build.
    Right now the bungalo has 2 bedrooms, a kitchen/bath and small open room.
    Stove is on propane.
    Only lights and a small fridge.
    Hot water is from a 30 gal electric heater.

    According to the installation instructions the boiler has "heater ampres @240 is 100"
    I spoke with technical assistance and they said that it has three elements and at full load it will be about 92amps.


    http://www.slantfin.com/index.php/pr...al/monitron-eh

  8. #8
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    What are your electric rates?

  9. #9
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by technogirl74 View Post

    The boiler we are leaning to is a Slant Fin Monitron EH24M2 which is listed at 100amps at full load. It is also 82,000btu on single phase.
    My husband wants to go with #2 Romex wire on a 100amp breaker for the installation.
    Since we only want to do this once, I thought I'd get the opinion of the folks on this site.
    #2NM is not nearly enough. This unit is a 100A DRAW.
    You need 1/0cu at least.

    IMO, unless you electricity is almost free you'd be nuts to go with an electric unit this big.

  10. #10
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Hereabouts all the inspectors allow #2 cu for 100 amps

    But I can save her a ton of money with a few water heater in series [unless they are making steam] I heat my house with 2 water heaters with 4500 and 5500 watt elements set up to run both together. Been running fine for 10 years. If she is comparing against propane, cheap electric wins hands down. If against practially free nat gas, then thats the way to go.

    I am lucky to have an OLD grandfatherd in seasonal rate schedule of 6 to 8 cents per KW.

  11. #11
    DIY Junior Member technogirl74's Avatar
    Join Date
    Dec 2010
    Location
    ny
    Posts
    17

    Default

    Thanks for the replies guys.
    The boiler is to replace a propane fangled mess we have right now.
    We need something to get us through the year and something that will be able to handle the "new" home we plan to build in the future.
    In that home we are going to go with a new propane boiler but have the piping done so that we can switch between the electric boiler and propane boiler.

  12. #12
    DIY Junior Member technogirl74's Avatar
    Join Date
    Dec 2010
    Location
    ny
    Posts
    17

    Default

    Quote Originally Posted by ballvalve View Post
    Hereabouts all the inspectors allow #2 cu for 100 amps

    But I can save her a ton of money with a few water heater in series [unless they are making steam] I heat my house with 2 water heaters with 4500 and 5500 watt elements set up to run both together. Been running fine for 10 years. If she is comparing against propane, cheap electric wins hands down. If against practially free nat gas, then thats the way to go.

    I am lucky to have an OLD grandfatherd in seasonal rate schedule of 6 to 8 cents per KW.
    Ballvalve,

    Can you send me a diagram of what you have.
    I've heard about using electric water heaters but read that the recovery rate is not so good.

  13. #13
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    At ANY per kwh rate with the seasonal heating required anywhere in NY state heat pump technology would pay for itself. If you're already committed to the electric boiler concept, size the boiler to minimum of what you need now, and when you graft on the new dream house do the financial analysis on what a variable-speed air source heat pump (ductless or ducted), or a ground source (geothermal) system would deliver. But doing that financial analysis NOW may make even more sense.

    You may be able to cut your heating costs by maybe a third to half by going to electricity, but why stop there? Propane is currently the most expensive heating fuel possible where electric rates are cheap (at about the national average or higher pricing on electricity your electric boiler might be more expensive), and heating with a heat pump in cheap-electricity-land will be something like 1/4 the cost of heating with propane, maybe even less. Even with the prospect of a future lower price on propane locally as the Marcellus & Utica shale gas fields are developed, it's doubtful that it'll ever approach heat-pump technology on a BTU/$ basis, even if the price of electricity doubles.

    And with heat pumps you also get air-conditioning to take the sticky edge off the hazy heat of July.

    With any heating system it's important to get a good handle on the size needed, and you may not need anything like 62000BTU to keep a 1500-2000 square foot bungalow warm (even at -25F outdoor temps you might see in Saranac or other higher-cooler place.) If you've gone through at least a heating season or two on propane and know your annual fuel use it's possible to get a fairly good handle sizing based on fuel use, heating degree-day data for your zip code, and the nameplate efficiency on the propane boiler. (My at -25F the heat load on my ~2200' bungalow w/1500' of semi-conditioned insulated basement is still well under 50,000BTU/hr.) If you don't have that information, "manual-J" type heat loss calculation would get you there.

    Even a single 1.5-2 ton ductless mini-split heat pump would likely handle the shoulder season heating loads, at an operational cost a third that of an electric boiler, and it's contribution to the mid-winter heating would be at ~half-cost relative to the electric boiler. Geo would even be a bit better, but would usually be a much higher up-front cost unless subsidiesed. (A 2-ton mini split is ~$5KUSD, installed, in my neighborhood, but 2-ton geo runs ~$15-20K, often more.)

  14. #14
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by ballvalve View Post
    Hereabouts all the inspectors allow #2 cu for 100 amps
    For electric heat with a 100A draw? I don't think so.

  15. #15
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Quote Originally Posted by Speedy Petey View Post
    For electric heat with a 100A draw? I don't think so.
    Obviously it depends on the distance. And the wire and its temperature rating of insulation. It goes as high as 130 amps.


    http://www.thelenchannel.com/1amps.php

    As to water heaters, you can buy 30 gallon rigs for $195, do a little rewiring and get both elements on, so you have a 9 or 11,000 watt unit. Just interconnect them until you get the BTU's you need. Or buy a commercial unit with several elements and anodes.

    Here is a USA made rig with multiple choices of current inload - gold plated elements, and 60 to 150 amp current draw;

    http://www.americanwaterheater.com/p...df/lchde40.pdf

    I find it very hard to believe you need a 100 AMP RIG.... Is your bungalow 4000 square feet with no insulation, built on an iceberg?
    Last edited by ballvalve; 01-21-2012 at 01:34 PM.

Similar Threads

  1. Removing Boiler Plug from a Steam Boiler
    By dsorkin in forum Boiler Forum
    Replies: 2
    Last Post: 12-16-2011, 09:20 AM
  2. Replies: 7
    Last Post: 11-20-2011, 01:38 PM
  3. Bit of an electrical Gremlin on an older boiler system.
    By Doherty Plumbing in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 08-04-2010, 09:42 PM
  4. Electrical Engineer allowed to do Electrical work?
    By willijimon in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 03-05-2009, 05:08 PM
  5. Back boiler & oil boiler to twin copper cylinder
    By sheen in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 12-07-2006, 04:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •