    Quote Originally Posted by Melissa2007B View Post
    This is an Aprilaire 360 Humidifier and it uses water mixed through a regulator, to come out no more than 140 degrees. Good unit. Saves hauling water to tabletop units every day and the cleaning mess.
    Okay, I see now. This is not connected to a furnace and uses hot water as the heat source. So you can't go with cold water for the the feed.

    Link I found online says it uses up to 6 gallons of water/hour so I could see it causing a lot of short cycles.

    The online version of the manual says that the feed water should be 140 F maximum. It doesn't say anything about mixing it with cold water.

  2. #17
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Exclamation

    Just to correct one point, the T&P valve will open at 210 degrees
    212 degrees is the boiling point of water at sea level, these type of safety devices are to open at least 2 degrees
    below that point, but with your house water pressure at 60 to 90 psi the boiling pressure is much higher then that
    If the water temperature ever got that high over 210 degrees when you open a faucet and the pressure drops
    the super heated water at the top of tank will instantly flash to steam and 2 micro seconds later you have
    Space Shuttle CHALLENGER and then your house follows into the street

    PS a note water heater and boiler safety devices are all designed to work or fail at the lowest set point to save
    lives and or property
    Last edited by MACPLUMB 777; 01-17-2012 at 08:09 PM.

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  3. #18
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    Normally, a WH has a decent convection current that keeps all of the water in the tank relatively consistent with no use. But, if you get certain special conditions, it might stratify. This effect is often used with salt water and fresh water to produce very hot water in one layer to store energy.

    Just like your car's radiator doesn't boil at maybe as much as 240-250-degrees because it is under pressure, the water in the WH won't, at least until it is released to a low enough pressure. If it ever did get that hot (it shouldn't if the safety valve is working and the discharge pipe is not blocked), it would be very dangerous to both life, limb, and property.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #19
    DIY Senior Member Runs with bison's Avatar
    Join Date
    Aug 2009
    Location
    Midwest
    Posts
    892

    Default

    Quote Originally Posted by MACPLUMB 777 View Post
    but with your house water pressure at 60 to 90 psi the boiling pressure is much higher then that
    If the water temperature ever got that high over 210 degrees when you open a faucet and the pressure drops
    the super heated water at the top of tank will instantly flash to steam and 2 micro seconds later you have
    Space Shuttle CHALLENGER and then your house follows into the street.
    Well, not quite...when you open the valve the pressure in the tank would still be about the same, but it would begin flashing in the line on the way to the fixture as the pressure dropped through the line. You would get water first until the hot water reached the faucet, then it would start sputtering water and steam and then blow wet steam pretty hard. At 90 psig the saturated water temp would be close to 330 F. That would provide enough enthalpy to boil something like 10-15% of the water coming out of the tap. Volume wise that is tremendous so it would be a noisy nasty jet of steam and boiling water! But the tank itself would still be liquid full or nearly so other than some steam bubbles forming at the hot water tap.

    Fixtures are restrictive enough that most of the pressure drop is taken there. There would be an hellacious amount of energy in that tank though, so that if it ruptured a large volume of steam would flash off and cook anyone in its path. If my back of the envelope numbers are correct a 50 gallon tank of saturated water at 90 psig would liberate something over 1500 cu. ft. of steam at Denver's altitude.

  5. #20
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Default how old is the heater??

    none of these other astute fellows has asked how old the heater was ,
    or how long ago it was installed.....or who installed it for you
    or how much damage was done to your home.....??

    if you have high water pressure you probably should have
    a thermal expansion tank at the very least on your heater
    and you should change out the T+p valve....

    if you have a FLOOR DRAIN the pressure relief valve pipe
    should be piped and inserted directly into the drain... as long
    as it does not stop up , it will prevent flooding in the future..
    or pipe it to the laundry drain

    I just left a job that sears did with no pan, no drain, no nothing
    with the t+p pipe just going down to the slab floor....

    if something has just recently been installed like this and it was
    done by a plumber, and they did not offer you these options,
    their insurance company should be on the hook for the damages....


    if you had a hack from Sears or Lowes
    install the heater recently, then its on you..

  6. #21
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by master plumber mark View Post
    none of these other astute fellows has asked how old the heater was ,
    or how long ago it was installed.....or who installed it for you
    or how much damage was done to your home.....??

    if you have high water pressure you probably should have
    a thermal expansion tank at the very least on your heater
    and you should change out the T+p valve....

    if you have a FLOOR DRAIN the pressure relief valve pipe
    should be piped and inserted directly into the drain... as long
    as it does not stop up , it will prevent flooding in the future..
    or pipe it to the laundry drain

    I just left a job that sears did with no pan, no drain, no nothing
    with the t+p pipe just going down to the slab floor....

    if something has just recently been installed like this and it was
    done by a plumber, and they did not offer you these options,
    their insurance company should be on the hook for the damages....


    if you had a hack from Sears or Lowes
    install the heater recently, then its on you..
    I personally would never insert a relief line INTO a floor drain. The floor drain could back up and clogg the relief pipe. Not likely to clogg it but possible depending on what backed up from the drain.

    If a hack from sears or lowes installed the heater she would be golden as far as liability coverage......wouldn't you think MASTER Mark? Those guys are licensed and bonded,they are just plumbers subcontracting through the store.

  7. #22
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Cool here is a Typical SEARS installation in town

    Quote Originally Posted by Hackney plumbing View Post
    I personally would never insert a relief line INTO a floor drain. The floor drain could back up and clogg the relief pipe. Not likely to clogg it but possible depending on what backed up from the drain.

    If a hack from sears or lowes installed the heater she would be golden as far as liability coverage......wouldn't you think MASTER Mark? Those guys are licensed and bonded,they are just plumbers subcontracting through the store.

    anything you can do to keep a flood from happenning is very wise.....

    if you can insert the t+p down slightly into a floor drain,
    I would suggest you do it.. I am not talking about cramming it down into
    the bottom of the trap here....

    the odds of a floor drain backing up and stopping up the t+p pipe is
    close to impossible, or you can always give it an air gap of an inch above
    the drain .
    ...... whatever you feel is best....

    this is a common practice and it should be done over just putting the t+p
    into the water heater pan and pipeing it over to a drain... the pan can be
    over-whelmed by the sheer volume from the t+p ...
    I know this from one I was involved in just last week
    My own personal experience with a flooded pan


    I dont know when or whom did the work, or how long ago it was done either
    so everyone will be heading for the hills looking for a rock to hide under if
    she trys to turn it into her insurance.....that you can depend on....

    here is one we tore out from Sears just on tuesday...this unit is about two weeks old...basically brand new..

    there is no pan, no floor drain, no thermal expansion tank, the shut off valve cannot be gotten to behind the heater... this Sears unit also had the crapppy honeywell valve on it.

    this was installed by a SEARS sub-contractor....
    so would Sears have to pay the bill if the t+p valve
    flooded this home ??? yes or no??

    do you think would it have been wiser to pipe the t+p
    over to the laundry drain about 5 feet over ?????

    so what would you do to think
    would make this a better install.????.

    click to enlarge.
    .. aint this something to be proud of??




  8. #23
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    From what I hear, the rules on terminating the T&P valve's outlet have changed in the recent code books, so check carefully when installing a new WH. I gather from comments here that people don't think much of the Taco WAGS valve, but personally, I think it is a good idea - if water builds up to about 1/2" in the drain pan, it shuts both the WH and the water supply off...unless the tank has a catastrophic split, no floods. It's totally mechanical, no power (except the built-in switch to control the WH firing), and uses the same tech as the autoinflaters on a lifevest used in airplanes - a disk disolves when wet and a SS spring closes the water valve.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  9. #24
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Thumbs down wags and taco

    Quote Originally Posted by jadnashua View Post
    From what I hear, the rules on terminating the T&P valve's outlet have changed in the recent code books, so check carefully when installing a new WH. I gather from comments here that people don't think much of the Taco WAGS valve, but personally, I think it is a good idea - if water builds up to about 1/2" in the drain pan, it shuts both the WH and the water supply off...unless the tank has a catastrophic split, no floods. It's totally mechanical, no power (except the built-in switch to control the WH firing), and uses the same tech as the autoinflaters on a lifevest used in airplanes - a disk disolves when wet and a SS spring closes the water valve.

    the Wags is a one shot wonder,
    once it gets wet, its over and you have to intsall a new one
    I dont even know what they are worth, but they are not too popular

    the t+p valve could barely weep a small stream and
    trip this mechanism to go off.....

    as far as the code goes, pipeing the t+p to the floor drain
    is ok as long as their is an air gap...or it is laying on top the drain..

    at least a dozen times we have gone out to homes where the water
    heater was on the second floor and the t+p pipe was hanging in
    mid air 5 inches above a 3 inch pvc cup that was used as a floor drain.
    Normally, they are sunk and flush at the floor level so the pan could go into it also...
    ..
    the t+p blew and half the water hit the drain
    and the other half sprayed everywhere and flooded the home.
    I feel its best to err on the side of caution and have that pipe
    inserted into the drain and zipped tied off so it cant move.

    I do whatever I think is best for the situation
    that is presented to me to protect the property
    from serious damage.
    ..


  10. #25
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    It takes about 1/2" of standing water to trigger a WAGS, but as far as I know, yes, once triggered, it must be replaced. In theory, it could be reset, but I've not looked into it. A little weeping into a pan should not be enough to trigger it unless the drain is plugged and it accumulates. What's worse, replacing it or maybe thousands of dollars of damage if it leaks all over. Plus, if the tank leaks faster than the fill, the burner could create other problems...but, if it is disabled, all's better. Think of it as an insurance policy.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #26
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    I use 1.5" sch 40 pvc for my pan drains with a combination wye&1/8 bend near the outlet of the pan with a 2' stub of pipe vertical. I pipe the relief line indirect no more than 6" into this vertical riser off the pan drain.

    The thermocouple adapter that the wags valve uses is useful for trouble shooting water heaters under load.

  12. #27
    DIY Junior Member ST1300Rider's Avatar
    Join Date
    Jan 2012
    Location
    South Carolina
    Posts
    23

    Default How to prevent massive H20 leaks...FloodStop Valves.

    I am very sorry to hear of your flood.

    I had one w/a washer that kept filling.

    The thing going forward is how to prevent these super unknowns.

    I use FloodStop valves(electric ball solenoid) on all my critical interior needs(fridge; eBidet and whole whouse water filter in my closet) and I don't worry about those...

    FWIW...here is the link.


    http://www.safehomeproducts.com/shp2...9&menupage=975


    It uses a sensor plate and when a drop of H20 hits it...it closes the water supply to "x"...ending the flood.

    Hope it helps and again; sorry to hear about your dilemma.

  13. #28
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Default that is a nice alarm valve

    those look pretty nice.... for 150 bucks that is not too bad
    just put the sensor plate down in the bottom of the pan.
    and it has an alarm and shut off...

    this is much, much better than a wags valve...


  14. #29
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,397

    Default

    Quote Originally Posted by master plumber mark View Post
    this is much, much better than a wags valve...

    And what happens if this occurs while the power is off? Nothing...the water still flows. WAGS, it stops. Do you have any personal experience with a WAGS valve that jaded your thought? I've not used either, so am only looking at the 'features'. I'd really like to know.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  15. #30
    Homeowner
    Join Date
    Jan 2010
    Location
    Alabama
    Posts
    1,174
    Blog Entries
    1

    Default

    Quote Originally Posted by jadnashua View Post
    And what happens if this occurs while the power is off? Nothing...the water still flows. WAGS, it stops. Do you have any personal experience with a WAGS valve that jaded your thought? I've not used either, so am only looking at the 'features'. I'd really like to know.

    I agree the wags valve is the most reliable way to stop the water flowing to a water heater incase of a leak.

Similar Threads

  1. Problem with whole house pressure relief valve? Need advice from a pro. :)
    By Patriot_RAM in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 01-13-2012, 11:22 AM
  2. Check valve on main line and toilet solution for condo flooding?
    By Flooded out in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 11-26-2010, 06:36 PM
  3. Low Bathtub Pressure? The rest of the house has great pressure.
    By adayinthelife in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-27-2010, 03:50 PM
  4. Changing water pressure on house pressure regulator.
    By kskier in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 04-30-2010, 09:20 AM
  5. Flooding
    By Cookie in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 04-17-2007, 05:16 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •