Thread: a plumber installed this for me -- was it done properly?

Hybrid View

  1. #1
    DIY Member Pickngrin's Avatar
    Join Date
    Sep 2005
    Location
    Massachusetts
    Posts
    48

    Default a plumber installed this for me -- was it done properly?

    Happy New Year. I had a plumber come to install a drain for a utility sink in my garage. This is what he did. I'm not a plumber, but I thought that the sink drain had to run into a vertical drain. The drain stack is behind that wall stud, to the left of the fitting that he installed. The copper pipe running through the drywall is the drain from the bathroom sink. I asked him about the angling of the drain and he said that it didn't have to be angled. That doesn't seem consistent with what I've read, but again, I'm not a plumber. He told me to make a little riser for the plastic sink out of 2 x 4. Is this OK or do I have a problem? By the way, I figured out not to use the sink on the other side of the wall (he did not install the sink itself) before the sink is attached, but he never bothered to tell me not to.
    Thanks.

    Name:  IMG_20111231_092345.jpg
Views: 305
Size:  35.5 KB
    Last edited by Pickngrin; 01-01-2012 at 02:29 PM.

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    2,676

    Default

    Looks like it was done by the lowest bidder. A sink drain needs to be 2", and it needs to be pitched to the main. It cannot be connected to the main stack without a vent if there are other fixtures draining into the stack above it.

    Next time you hire someone, insist that they get a permit and inspection done prior to paying.
    Are you sure he was a plumber?

  3. #3
    In the Trades Pipewrench's Avatar
    Join Date
    Mar 2011
    Location
    Jackson MS
    Posts
    35

    Default

    So did he just access th copper drain then put that tee in the line? I'm not sure what you're talking about on the 2x4 riser. I'm not crazy about the rubber fernco either. Looks terrible. I would have used a male and female fittings to make the transition to pvc for better support. Other than looking cheap it should work ok for a shop sink. Looks like your dryer vent is running along the floor there also. Is that gonna be in the way??? Good luck buddy

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    19,211

    Default

    The coupling he used is not approved for internal use - it needs to be a banded coupling. Plus, I don't think it would pass as it doesn't appear to be vented, reductions in size are not permitted, and a T is not the proper fitting to attach into a drain line, even if the rest was okay. while a permit may add some to the cost, it also ensures you get it done right the first time in most cases.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer

  5. #5
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,944

    Default

    Was the work done for less than $100?

  6. #6
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,173

    Default

    No it was not done properly. It could have been a little worse, but not much.

  7. #7
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,944

    Default

    I've been put in this situation before, where "doing it right" involves a considerable amount of money and effort to do it correctly.


    To do it correctly,


    Get to where that drain stack is, remove the tee and install a tee that is 2" by the size of that stack. From there, you either design the piping with incorporation of a wye with the ability to vent those fixtures individually or not.

    The work shows they just added a tee into an existing trap arm off the other fixture.


    To do the job correctly, there's considerably more money involved to do it right.

Similar Threads

  1. Toilet not flushing properly
    By paper123 in forum Toilet Forum discussions
    Replies: 3
    Last Post: 06-21-2011, 06:27 PM
  2. Dishwasher not draining properly
    By llmercll in forum Plumbing Forum Discussion & Blog
    Replies: 14
    Last Post: 02-08-2011, 08:24 PM
  3. Plumber installed our toilet to the pump??
    By tareko in forum Plumbing Forum Discussion & Blog
    Replies: 5
    Last Post: 02-03-2008, 05:55 PM
  4. Hack Plumber? ... Oops -NO a licensed plumber!
    By coyotehills in forum Plumbing Forum Discussion & Blog
    Replies: 57
    Last Post: 12-07-2007, 06:52 AM
  5. Toliets won't flush properly
    By PT100 in forum Toilet Forum discussions
    Replies: 4
    Last Post: 10-18-2005, 05:00 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •