    Default Tank air pressure for non bladder water tank

    I was wanting to get a experts view on how much air pressure needs to be added to a empty Water storage tank.

    After draining all of the water from the tank, How much Air pressure should I have in the tank ?

    And what percentage of the tank would have water , When the pump fills it and the pump turns off ?


    Thanks, Have a Happy New Year.


    P.S. Sorry for leaving out, Tank 30 feet above sea level, 120 Gal tank, 40/60 switch setting.


    DonL
    Last edited by DonL; 01-01-2012 at 10:04 AM. Reason: P.S.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    I am a DIYer, not an expert but from my experience maintaining my hydropnuematic tank, will add my two cents.

    Tank manufacturers have their own idea as to where the air level sits by how and where they locate the air volume control. Since it varies by manufacturer, I would have to say there is not one right answer for all scenarios. The theoretical ideal for max drawdown would have the tank nearly empty at kick-in. That however could become an issue if you have a softener or filter backwashing and the pump cannot keep up with the draw. Air may get interspersed in the stream and could blow resin or media into the head and into the drain.
    Last edited by LLigetfa; 01-01-2012 at 11:51 AM. Reason: typo

  3. #3
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    If you have an Air Volume Control (AVC), it doesn't matter how much air you add, because it wll come out untill the float on the AVC is up. Usually just draining the tank completely, and not adding any more air, will give you the correct amount.

    You can pre-charge a standard type tank if you remove the AVC, or pump the air up to 35 with a 40/60 switch, while the water level is above the AVC.

  4. #4
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    Quote Originally Posted by valveman View Post
    Usually just draining the tank completely, and not adding any more air, will give you the correct amount...
    Doing that on my WellMate tank results in very little drawdown. Over time the micronizer will increase the volume to what the AVC maintains but that is a slow process so anytime I drain the tank, I will use my air compressor to restore the air level to what the AVC does to maximize my drawdown.

  5. #5
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,662

    Default

    I forgot to mention that I did remove the AVC and plugged the ports.

    I never could get them to last , or work. On the Old Pump or the one I have installed now.

    The AVC did not have a float, It was mounted about ¾ of the way up from the bottom of the tank.


    Can I assume the tank should be ¾ full of water, or is that not correct ?
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  6. #6
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    My tank has the float-style AVC about 1/2 way up the side of the tank, so that's all the air that it could hold.

  7. #7
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    My understanding is there are two types of AVC. One style only lets air out and works in conjunction with a submersible and a bleeder/snifter. The other kind takes air in and works with a piston or jet pump. Any I've seen were about half way up the tank.

    The more air in the tank, the more drawdown. If the AVC is not working, the more air, the less often it needs to be topped up. If you don't have a softener or backwashing filter, I see no downside to having more air.

  8. #8
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,662

    Default

    Quote Originally Posted by cacher_chick View Post
    My tank has the float-style AVC about 1/2 way up the side of the tank, so that's all the air that it could hold.

    So how full is your tank with water ? When your pump shuts off ?
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  9. #9
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,662

    Default

    Quote Originally Posted by LLigetfa View Post
    If you don't have a softener or backwashing filter, I see no downside to having more air.

    I do have a water Softener.

    I don't see why that would mater, But I guess that it does ?
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  10. #10
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    I explained it in my first post but will try again with different words. Water flow through an obstruction is limited by the obstruction much more than air is through the same obstruction. If you've ever had a glass shot out of your hand at a sink that is spitting air and water, you'd understand what I mean.

    A softener backwash is flow limited by an orifice. On many softeners, they use power only to turn a clock through the various cycles. The rest is done with water pressure. If the power were to fail during the backwash, the well pump stops and the level in the pressure tank starts to drop. If the air is jacked so much that there is enough pressure in the tank after all the water has been expelled, it will be chased by a burst of air. The air behind the water will have a voilent boiling action in the resin tank which can drive the resin into the head and the drain if there is no top basket.

    I know this first hand because my WellMate precipitation tank is supercharged to provide drawdown that rivals a bladder tank. I have never had the misfortune of a power failure during a backwash, but the iron in my water wreaks havoc on the AVC and when it stops working, the air will pass through to the iron filter on every cycle. The greater flow rate on the iron filter will drop the level in the precipitation tank and blow media up into the head and down the drain.

  11. #11
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    490

    Default

    Don,
    Forget about all the other replies and listen to mine. I have been doing this for well over 20 years, I probably know more about what kinds of set-ups we have here than anybody else.

    For various reasons, all the tanks in our area have remained galv. hydro-pneumatc. Most everywhere else the bladder tank is the std.

    Here, an AVC is designed to use the suction port of a jet pump to suck in a tiny little wisp of air every time the pump starts. I don't like them because most either fail within a few months or even not work right brand new out of the box.

    If you don't have a schraeder valve on the side of your tank, get one. Turn the pump off (be mindful that by doing this you could lose the prime in the pump). Open a spigot somewhere close to the tank. Start adding air. I like to use a clip-on style chuck that allows you to add air hands-free. Add air until you see the water start to spurt out of the spigot. Hopefully your spigot is plumbed at a low point of the tank. Close the valve when the air starts sputtering out. Keep adding air for about 5 minutes or so. Remove the air chuck and turn on the pump. Hopefully once the pump pressures up the tank you'll have at least 1/2 air to water. If you get too much air, don't worry, it will naturally exit after a few days. You might hear it sputtering out.

    By doing this you can at least double the draw down of your 120 gallon tank and extend the time between draining.

    Good Luck.

  12. #12
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    I have a submersible pump with the bleeders in the well, so that every time the pump runs it sends a slug of air to the tank in front of the water. My air volume control releases excess air from the tank.

  13. #13
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,946

    Default

    Quote Originally Posted by Texas Wellman View Post
    Don,
    Forget about all the other replies and listen to mine. I have been doing this for well over 20 years, I probably know more about what kinds of set-ups we have here than anybody else.

    For various reasons, all the tanks in our area have remained galv. hydro-pneumatc. Most everywhere else the bladder tank is the std.

    Here, an AVC is designed to use the suction port of a jet pump to suck in a tiny little wisp of air every time the pump starts. I don't like them because most either fail within a few months or even not work right brand new out of the box.

    If you don't have a schraeder valve on the side of your tank, get one. Turn the pump off (be mindful that by doing this you could lose the prime in the pump). Open a spigot somewhere close to the tank. Start adding air. I like to use a clip-on style chuck that allows you to add air hands-free. Add air until you see the water start to spurt out of the spigot. Hopefully your spigot is plumbed at a low point of the tank. Close the valve when the air starts sputtering out. Keep adding air for about 5 minutes or so. Remove the air chuck and turn on the pump. Hopefully once the pump pressures up the tank you'll have at least 1/2 air to water. If you get too much air, don't worry, it will naturally exit after a few days. You might hear it sputtering out.

    By doing this you can at least double the draw down of your 120 gallon tank and extend the time between draining.

    Good Luck.
    Yes, yes and once again YES
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  14. #14
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    All fine and good, and I usually remove the air release valve on the plain tank associated with a submersible pump. Then I use a air inducer system ABOVE ground right next to the tank, and adjust the nipple length between the check valve with schrader valve and the bleed off valve to give a shot of air that does not 'overload' the tank.

    Then, one may still pressurize the tank with a compressor to a few pounds under cut in pressure to add much to draw down amount. ...And when you forget to add air with the AC, as most do or will from many times to time, You still do not end up with a water logged tank.

    But I start to think that a GOOD diaphragm tank is really the best way to go in the long run - but never a "bladder tank".

    2 interesting notes: One well I have makes water with much air in it, and so the tanks never water log without any air maker. Another well I have feeds a 3000 gallon tank, and flows to a 8 stage booster pump that feeds a plain 80 gallon pressure tank. I always wondered why it too, never water logged, until 2 of us with radios monitored the flow - turns out that at the outlet of the 3000g static tank there is a small SUCTION leak - lets air in only when the pump sucks from the tank, but no water out when static. Suction leaks are odd things that few discover. And in this case is a very good 'problem'.
    Last edited by ballvalve; 01-01-2012 at 09:35 PM.

  15. #15
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,662

    Default

    Quote Originally Posted by Texas Wellman View Post
    If you don't have a schraeder valve on the side of your tank, get one. Turn the pump off (be mindful that by doing this you could lose the prime in the pump). Open a spigot somewhere close to the tank. Start adding air. I like to use a clip-on style chuck that allows you to add air hands-free. Add air until you see the water start to spurt out of the spigot. Hopefully your spigot is plumbed at a low point of the tank. Close the valve when the air starts sputtering out. Keep adding air for about 5 minutes or so. Remove the air chuck and turn on the pump. Hopefully once the pump pressures up the tank you'll have at least 1/2 air to water. If you get too much air, don't worry, it will naturally exit after a few days. You might hear it sputtering out.

    I don't have a schraeder valve, but next time I drain my tank I will install one, and do as You suggest.

    I have been draining my tank about every 4 months and it seems to work fine. But maybe could do better.

    Every time that I have used an AVC, I end up having to drain the tank every 4 months anyway.

    I do like the larger tank, In case of a power failure I have a little more reserve.


    Thank You for your Input.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Pressure Tank Bladder?
    By Doozy8 in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 07-25-2011, 08:05 AM
  2. Pressure tank bladder
    By VA Rigger in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 10-27-2009, 07:41 AM
  3. Pressure Tank Bladder
    By VA Rigger in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 10-26-2009, 03:35 PM
  4. Bladder tank pressure
    By TheTank in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 09-24-2007, 06:32 AM
  5. Bladder pressure tank vs standard pressure tank
    By brown13 in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 06-06-2006, 07:18 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •