    Default CSV1W Back Pressure Question

    I talked to a well guy after I installed a CSV1W. He seemed a little confused and concerned about the back pressure situation since the relief valve is moved to after the CSV. I told him that I researched it and hadn't seen any talk about busted pipes after installing one and he said he guessed it should be ok. But now I'm curious. Does anyone here know of busted pipe issues after installing a CSV?

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,175

    Default

    The amount of backpressure from any CSV is determined by the size of pump you have. Average backpressure is between 90 and 150 PSI. All backpressure does is make your pump think it is in a deeper well, so it can pump less water when you need it to do that. Even 150 PSI of backpressure is no different for the pipe than setting the pump at 340’ deep, which is very common for pumps. Even 160# poly pipe can easily handle this, so any other kind of pipe that would normally be used down the well will have no problem.

    Backpressure is something that needs to be addressed when using a CSV, especially if the pump is greatly oversized. Even then the backpressure will only be a concern if your pump is designed for setting at 500’ or 700’, as with something like a 10 GPM, 3HP.

    It is not unusual for a pump guy to be confused or concerned if he/she has never used a CSV. However, this is just his/her first step into becoming educated on the subject, and learning a better way to install pump systems. As you said, research does not show any problems with the CSV. Being this is our 19th year in business, that is saying a lot.

    The pump people you need to worry about are the ones who say a CSV doesn’t work, or that they love the Variable Speed Pump systems, also known as VSP, VFD, or just “Constant Pressure Pumps”. These people are either greatly behind in the learning curve, or just blatantly out to get as much of your money as they can, as often as they can. People who sell pumps don’t love the variable speed type pumps because they last a long time and save the homeowner money. Just the opposite is true. A little research will prove this as well.

  3. #3
    DIY Junior Member ehuddle's Avatar
    Join Date
    Oct 2011
    Location
    weatherford, tx
    Posts
    16

    Default

    Thanks. He just got me a little concerned.

  4. #4
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Don't be concerned, put a pressure gauge before the CSV, and KNOW what you have. If its well under the pipes rating and the pipe is not 40 year old galvanized, your safe. It will also tell you when your pump is getting tired, as the max pressure will drop- if you invest in a good gauge.

    Doctors dont get concerned about blood pressure - they measure it.

    WIKA makes great gauges.
    Last edited by ballvalve; 12-30-2011 at 10:19 AM.

Similar Threads

  1. Pressure Gauge Going Back and Forth
    By Doozy8 in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 07-07-2011, 05:20 AM
  2. Pressure Testing Back to Gas Meter
    By jgwalter in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 05-28-2011, 08:58 AM
  3. csv1w question
    By spylake farms in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 10-23-2008, 06:30 AM
  4. back pressure valve
    By johnastephens in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 09-07-2008, 06:36 AM
  5. Bleed back question
    By dad in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 10-14-2006, 05:35 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •