I have a Bradford White MI TW 50 gl power vent tank.
Blower was making noise and had come apart. Replaced blower assy with factory parts.
Plugged in and ran fine. After tank was hot, blower would not shut off. Blower runs even though the burner is not on. 2" PVC vent pipe is not hot to the touch.
Any Ideas??
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Assuming (in lieu of evidence) that you wired it correctly, that would imply that the relay the powers the blower is stuck on (contacts welded, spring broken, something) or something even further back the control chain is fried.

In the meantime just letting it run is not a good option, since it's sucking heat out of the tank 24/7, blowing it out the vent.
 

Rexles

New Member
Messages
16
Reaction score
0
Points
0
Location
Holland, OH
Wiring was simple plug that could only be plugged in one way.
It seems the diaphram switch was not being pulled in when blower was running. I removed the blower and remounted it using silicone to seal around the base where it sets on the HW tank. One of the sheet metal screw holes was stripped out so I installed bigger screws. Plugged it in and it fired right up.
Evidently the lack of a good seal was enough to make the vacuum on the diaphram switch not pull in. The blower is controlled by the thermostat, and the gas valve is controlled by the vacuum switch on the blower unit.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Those air switches are very sensitive, when the diaphragm gets harder with age, the required vacuum climbs, and it still works when you 'suck on it'.

Odd, however, because if the diaphragm switch does not close, you shouldnt get gas to the valve, and the blower should power down.

Sequence-call for heat- blower starts- air switch senses vacuum from blower- igniter on- blower on. gas valve opens.
 
Last edited:

Rexles

New Member
Messages
16
Reaction score
0
Points
0
Location
Holland, OH
Those air switches are very sensitive, when the diaphragm gets harder with age, the required vacuum climbs, and it still works when you 'suck on it'.

Odd, however, because if the diaphragm switch does not close, you shouldnt get gas to the valve, and the blower should power down.

Sequence-call for heat- blower starts- air switch senses vacuum from blower- igniter on- blower on. gas valve opens.


You are correct on your sequence, however the blower is controlled by the thermostat and does not shut off until satisfied. The vacuum switch pulls in the gas valve and even if the gas valve does not open the blower continues to run. Tech at BW told me that over the phone and it was also proven true by standing there and watching it.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,538
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
shut it down

you would be wise to check the air switch, thermostat, relay
that tells the unit to shut off...
and whatever else they tell you could be the trouble...

the blower will run till it burns out, and it will certainly
cool down the heater and make it come on and re-heat...
costing you money....

shut it down, take it apart again and start over...
 

Rexles

New Member
Messages
16
Reaction score
0
Points
0
Location
Holland, OH
Evidently you failed to read my post correctly. It was fixed when I pulled off the blower assy and sealed it with silicone and screwed it down again with abigger screw that had stripped out. It is running the way it should.
you would be wise to check the air switch, thermostat, relay
that tells the unit to shut off...
and whatever else they tell you could be the trouble...

the blower will run till it burns out, and it will certainly
cool down the heater and make it come on and re-heat...
costing you money....

shut it down, take it apart again and start over...
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,538
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Evidently you failed to read my post correctly. It was fixed when I pulled off the blower assy and sealed it with silicone and screwed it down again with abigger screw that had stripped out. It is running the way it should.

Evidently you failed to read my post correctly.

I am so very sorry sherlock...... how silly of me old chap.....

evidently , these other two guys did not read your
post very well either.....

please stick your snooty nose up in the air for them too,

whould you please.

 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks