What would cause a gas furnace to draw too many amps?

Users who are viewing this thread

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Exactly what do you mean by too many amps? As in it blew a fuse??? That is a short circuit, look for burned transformer, overheated motor, etc.
 
Messages
951
Reaction score
6
Points
18
Location
Midwest
Can the blower turn freely? I had a bearing failure in one many years ago, it seized. Interestingly, it didn't trip the breaker, and the blower motor didn't burn out...which was good because I couldn't find replacement bearings and had to rebuild it from parts I scavenged off another similar old blower that a shop had removed when replacing a unit. I think I handed the shop owner a couple of bucks for the old unit, other than that the repair was free.

Anyway, I'm assuming blower because it is the biggest amp draw. The second biggest user would be the induced draft fan.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; The second biggest user would be the induced draft fan.

It may be the "second biggest draw", but it still a "Very small" one. We would have to know what he means by "excessive amps" and how he determined it.
 

kailor

Member
Messages
34
Reaction score
0
Points
6
Location
Huntsville, Alabama
Merry Christmas everyone! I'm helping my sister-in-law with this issue. I'll try to find out what the amp draw was according to the repairman. No one available til Tuesday. She said they got the furnace running but did not know how long it would last. Right now, I've very limited information. Thanks for your inputs thus far.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If the voltage was marginal (say in a brown-out), and things were 'on the edge' of accepability, it could draw excessive current and trip or blow a safety device. When I had my air handler/a-c unit installed, I installed a low-voltage cutout device. I think it was made by IDS. It's about the size of a deck of cards, has some controls on it to set the desired operating range, some LED indicators, and an internal relay to disable operation if the power is outside of parameters you set. No idea if it has saved my system, but it also has a time-out after power outages to prevent operation immediately after power reapplication when it can fluctuate radically for a few moments or so, thus further protecting things while the voltage is all wacky until it stabilizes. The internal motors probably would be okay, but the unit has at least a couple of circuit boards, and not asking them to operate until the power is stable is probably a good thing.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Merry Christmas everyone! I'm helping my sister-in-law with this issue. I'll try to find out what the amp draw was according to the repairman. No one available til Tuesday. She said they got the furnace running but did not know how long it would last. Right now, I've very limited information. Thanks for your inputs thus far.

Sounds to me that the service man, was blowing a little smoke. Maybe not.

It is very disturbing how they take advantage of the unknowing. Maybe he spoke the truth. who am I to judge.


If she called because of a blown fuse, then Jim's answer makes more sense than mine.


Have a happy Holiday.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
The blower motor was bad.

We appreciate that you came back and gave us the outcome. Sounds like the service man knew what was up but just didn't explain it very well. Motors do go bad, and hopefully this did not cost you too much...maybe an arm and just one leg, not both!!!
 