Basement bath venting

Users who are viewing this thread

Sirapnav

New Member
Messages
1
Reaction score
0
Points
0
I'm installing a basement bath. My plan is to run the vent (3") up 8', then 90 across between the floor joist 20' to the outside, then striaght up.

Will that much horizontal distance cause problems? Thanks.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
In many codes, a bathroom can be vented with a 2" vent, if other vents are also present.

With that 2" vent, you would be allowed 1/3 the distance horizontal to the vertical.

Or you could increase the vent to 2-1/2" and run pretty much as long as you like.

I would say that the 3" will do just fine.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
vent

We don't know where you live, but if it is in a cold area, the outside pipe going up to the roof, (you don't intend to just stick the vent through the wall, I hope), can freeze closed, and that would create a problem.
 