    Default Basement bath venting

    I'm installing a basement bath. My plan is to run the vent (3") up 8', then 90 across between the floor joist 20' to the outside, then striaght up.

    Will that much horizontal distance cause problems? Thanks.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    In many codes, a bathroom can be vented with a 2" vent, if other vents are also present.

    With that 2" vent, you would be allowed 1/3 the distance horizontal to the vertical.

    Or you could increase the vent to 2-1/2" and run pretty much as long as you like.

    I would say that the 3" will do just fine.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default vent

    We don't know where you live, but if it is in a cold area, the outside pipe going up to the roof, (you don't intend to just stick the vent through the wall, I hope), can freeze closed, and that would create a problem.