    Default Triangle Tube Prestige Excellence Boiler Use

    Looking at a TT Prestige Excellence 110 Boiler with integral 14 gal indirect fired tank.

    The cold water temp here is about 70 degrees, so, the unit's capacity would exceed 5 GPM under some conditions.

    Has anyone installed this unit for Domestic Hot Water use.

    The site is a 3 BR home (2 elderly residents) with measured flow rates shown in units of Gallons per Minute.

    MB Shower - 0.91 (new low flow head installed)
    MB North Sink - 1.20
    Kitchen Sink - 1.76
    West BR Tub - 4.29
    West BR Shower - 0.94 (new low flow head installed)
    West BR Sink - 1.30
    East BR Tub - 4.29
    East BR Shower - 0.93 (new low flow head installed)
    East BR Sink - 1.29

    Our actual usage is minimal: about 2 showers per day, bathtubs not in use, front loading washer.

    Thanks!

    -rb-

  2. #2
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    286

    Default

    The Excellence is a great idea, but should be sized first to the space heating load and then for the domestic hot water service. Properly sized to showers, big tubs and the number of bedrooms, but good point on the incoming water temperature.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    Does the boiler cold fire when needed, or does it maintain a minimum temperature all year long - I don't know on that unit? A conventional external indirect is easier to repair or replace if it ever fails, and, with the proper boiler, may be more ecconomical. A good indirect won't need the boiler to fire except after drawing hot from it, and if those draws are grouped around the morning shower, may only need to fire once during the day. If the boiler stays hot all the time, that's a waste of energy.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    286

    Default

    The Excellence is just that. Excellent. If it would fire at a lower minimum output and could be vented with 2 instead of 3" PVC -all that is really required- or with a nice concentric vent, I would install more of them, as they save space, fuel, improve comfort, are nearly silent in operation and save much in installation labor.

    The built-in indirect water heater is perfect for a two shower home - no big tubs, but one standard tub - no problem. The indirect is built of stainless steel and will likely never leak. Built in circulator and Honeywell 3-way zone valve for domestic priority without the often unnecessary mandate for primary/secondary piping makes it one of my favorites for retrofit combi-systems.

    Unfortunately, though the high efficiency condensing burner is nicely matched to the built-in indirect water heater, it is not necessarily the best match for every space heating application. I spend a full 50% of my time re-piping, changing radiation and controls for combi-heating systems that were designed by those without the necessary experience to assure the proper balance of both. In extreme cases entire boilers and water heaters have to be replaced with properly sized and piped systems.

    I know I have said before, not a DIY project.

    The addition of a tank vs. tank-less water heater has is it all over those Euro and Eastern rim tank-less water heaters of all kinds, as Americans do not live in 600sq.ft. nor take sponge baths at the sink. This unit will last longer, with less service and greater performance than any tank-less made today.

    Sizing to the heating load - or building the load to the unit - is the key to success (perfect comfort and low fuel bills).
    Last edited by BadgerBoilerMN; 12-18-2011 at 08:27 AM.

Similar Threads

  1. Replies: 49
    Last Post: Yesterday, 07:09 PM
  2. ControlLinks on Fire Tube Boiler
    By NickSTC in forum Boiler Forum
    Replies: 0
    Last Post: 09-12-2011, 07:04 PM
  3. Solo110 with smart40 indirect hot water heater triangle tube
    By Brian Morgan in forum Water Heater Forum, Tanks
    Replies: 1
    Last Post: 04-24-2009, 09:33 AM
  4. toto TCF670A vs BioBidet's Prestige BB-900
    By fred smith in forum Toilet Forum discussions
    Replies: 2
    Last Post: 05-21-2008, 09:31 AM
  5. red triangle on water meter
    By econguy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 01-01-2008, 07:01 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •