Thread: Weil-Mclain - Honeywell controller issues

  1. #1
    DIY Junior Member dayers1109's Avatar
    Join Date
    Nov 2011
    Location
    cincinnati
    Posts
    2

    Default Weil-Mclain - Honeywell controller issues

    I installed a used Weil-McLain 68 oil-fired boiler. The problem is the unit wants to fire and run whenever I power it on - through the breaker. The thermostat is off and it still runs. I even disconnected the thermostat wires and it will still fire and run when I flip the breaker on. I've checked the controller - its a honeywell but I can't find anything with a model number on it - and the transformer clicks back and forth if I arc the thermostat terminals. When it fires - the pumps don't run, unless I have the thermostat wired back up and set to run. I've turned the unit from vertical to horizontal and that doesn't do anything either - I was wondering if it mattered. Any help I can get (before it gets too cold!!) would be greatly appreciated.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    It may be set to constantly maintain a temp between the min/max, and when cold, is not up to the minimum, so it probably is just doing what it should, turning on to raise the water temp to the minimum. Double-check the aquastat wiring.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    What jadnashua said. On a number of boilers the burner is controlled only by the aquastat setting, and the circulator pump is controlled by a zone-relay (sometimes integral to the boiler's controls that will also inhibit the circulator even during a call for heat when the boiler temp drops below the low-limit aquastat.)

  4. #4
    DIY Junior Member dayers1109's Avatar
    Join Date
    Nov 2011
    Location
    cincinnati
    Posts
    2

    Default

    Thanks Gents - I'll just set the low temp way down and see if that works. Im still thinking that if the thermostat is set to 'off' that it shouldnt fire at all. I'll take a look at the aquastat wireing as well and let you know.

Similar Threads

  1. Weil-McLain GV4 quits
    By Cruisinfanatic in forum Boiler Forum
    Replies: 1
    Last Post: 08-28-2011, 12:49 PM
  2. Boiler Question: Weil Mclain
    By cgm55082 in forum Boiler Forum
    Replies: 5
    Last Post: 02-07-2009, 06:15 PM
  3. Weil McLain Ultra boilers
    By therinnaiguy in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 03-04-2008, 08:59 AM
  4. Weil-Mclain future
    By olrob in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 02-28-2008, 12:11 PM
  5. Weil-McLain Ultra Boiler
    By jadnashua in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 09-23-2004, 06:48 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •