    Hello,

    I just had a new propane boiler installed which is working well, but I have one question/concern about the install.

    Attached is a photo of the exhaust vent. It is oriented horizontally, so the warm air blows out sideways. I have two concerns about this.

    One, it is somewhat noisy (like a hair dryer) and this seems to broadcast the noise across the property and can be heard from quite a distance, potentially annoying neighbors (though houses are fairly far apart here).

    Two, some of that warm air is being blown against the siding of the house, which I noticed this morning is warm and wet (even though it is dry and very cold outside).

    My first thought is, what about rotating the cap on this exhaust so it is vertical? The air would then blow upward toward the sky and downward toward the ground. Would there be a problem with this orientation?

    Are there other ways to resolve this, possibly by adding a bend or other configuration to the exhaust pipe?

    I will of course be asking the installer these same questions, but wanted to consult the expertise here on the boards.

    Thanks!
    Attached Images Attached Images  

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    With an opening pointing up/down, it's possible you could accumulate precipitation which could drain back to the unit. There are likely other terminators that might be put on that pipe, though. the installation manual may show some other variations or call the manufacturer.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member tray's Avatar
    Join Date
    Dec 2011
    Location
    west henrietta, ny
    Posts
    10

    Default

    Some manufactures require that the flue actually have a slight pitch down for condensation to run outside instead of back to boiler since non high eff equip have no drains. I would think vertical is proper, but either pipe term was twisted during assembly and never straightened, or there is a code bein avoided poss by turning it away from that regulator. check with your local gas and electric supplier

Similar Threads

  1. Bathroom exhaust fan vent flashing
    By Jwhitman in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 06-16-2013, 01:11 PM
  2. Boiler - Oil vs Propane
    By frank in ohio in forum Boiler Forum
    Replies: 6
    Last Post: 08-01-2011, 03:47 PM
  3. bathroom exhaust vent sizing
    By mchristo in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 11-25-2009, 07:25 PM
  4. Bathroom Exhaust Vent Size?
    By CTWeekendWarrior in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 09-30-2008, 06:28 AM
  5. Shared vent-exhaust stack
    By gmilton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 04-19-2006, 10:20 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •