    Default Combing 24v and 120v systems on one thermostat

    Here's my situation: I manage an older semi-commercial building, one part of which has hot water heating (radiators) as well as regular a/c with a compressor outside and an air handler in the attic. The a/c system runs on the usual 24 volts, but the hot water thermostat is 120v (the thermostat starts and stops a water pump on the boiler). The thermostats are next to each other on the wall.

    The problem is that sometimes the systems get crossed up and people end up turning on the heat and the a/c at the same time. In addition, I'd like things to be configured such that when the boiler circulation pump is turned on, the attic air handler comes on to help circulate the heat more evenly.

    Is there any reason I couldn't configure a regular 24 volt thermostat (like a Honeywell FocusPro) to control both systems and hook up a relay such that when the thermostat called for heat, it would turn on the fan and also trigger the 120 volt boiler pump circuit? This would make it impossible for the two systems to be on at the same time.

    Thanks for any advice.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The contacts or switching circuit in the thermostat may not be rated for that much current. More importantly,the 24v transformer in you system is typically rated at 40 VA, and ONE relay coil uses most of that.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Properly engineered, yes it could work. You might need to upgrade the 24vac transformer, and, if you used a double pole relay, you could just need one relay, to turn both the 120 and 24vac stuff on. Now, whether it would be an approved installation, I'm not sure, but technically, it could be done.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    I once installed a larger 24V transformer in my furnace so I could add a 120V relay for a fan in an exhaust-heat exchanger, and that worked fine. Just take the time to add up all the numbers and be sure the transformer can provide what is needed overall and that the thermostat and relay/s can handle their respective loads.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

Similar Threads

  1. Floor warming... 120V mat vs. 240V thermostat
    By Fistor in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 10-15-2009, 02:01 PM
  2. two heating systems off of 1 thermostat?
    By g_eakin in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 11-17-2008, 12:05 PM
  3. heated 120v floor and thermostat wiring
    By Andrew M in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 08-07-2007, 07:32 PM
  4. Should mains be 110v or 120v?
    By dgold in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 07-25-2007, 07:43 AM
  5. 120V Thermostat Change Out
    By NY98M3 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 11-22-2006, 11:45 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •