    Default Question from Montreal #1

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  3. #3
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default Questions and Answers - Waterproofing in Montreal Building the perfect Shower

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  4. #4
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default Wrong test plug type for Kerdi Line flood Test

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  5. #5

    Default

    Can't be sure what you are trying to accomplish there John . Test the waterproofing or the plumbing pipes in the same time .

    No leaks where present at the Fernco attachment or at the plumbing connections , done at a prior date , before shower flooding .

  6. #6
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  7. #7
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    No. Not in CA. This drywall screw pattern wasn't for seismic at all. In this case, these were all non-load bearing walls set within a cinder block foundation. I was just surprised that they had a separate special inspection for the drywall screw pattern, but didn't care to see something like a flood test.

    As to the no-hub connection: As I mentioned in the other thread, you are doing it wrong. That connection should be tested with the DWV test. This is done by capping everything off and using either a 10' stand pipe or can often be done filling all plumbing with water to the highest roof plumbing vent. Then you and the inspector look for leaks. All plumbing connections need to be tested like this. The flood test is a separate test and does not accomplish the testing of the no-hub connection.

    What Roberto is testing with is fine as long as it holds. The other type is really only needed with a traditional shower in order to install below the weep holes. There should be a separate plumbing test regardless, but I know this often gets overlooked when installing say only a shower drain compared to a new addition or a new plumbing layout.

  8. #8
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  9. #9

    Default

    Quote Originally Posted by nukeman
    As to the no-hub connection: As I mentioned in the other thread, you are doing it wrong. That connection should be tested with the DWV test. This is done by capping everything off and using either a 10' stand pipe or can often be done filling all plumbing with water to the highest roof plumbing vent. Then you and the inspector look for leaks. All plumbing connections need to be tested like this. The flood test is a separate test and does not accomplish the testing of the no-hub connection.

    What Roberto is testing with is fine as long as it holds. The other type is really only needed with a traditional shower in order to install below the weep holes. There should be a separate plumbing test regardless, but I know this often gets overlooked when installing say only a shower drain compared to a new addition or a new plumbing layout.
    Thanks for the specifics . I am a tile guy , not a plumber , so I limit my testing to my waterproofing , assuming the rest of the plumbing installation is tested and done respecting the codes .

  10. #10
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    It is done differently in different areas, but you are still not testing that connection, so I'm not sure why you criticize Roberto for doing the same. Unless you do a 10' water column, you aren't really testing that connection.

    Edit: I'm not a plumber either (engineer), but I typically do everything myself (plumbing, electrical, HVAC, etc.). I want to make sure everything is right, so I study codes and do all of the inspections.
    Last edited by nukeman; 01-05-2014 at 09:17 AM.

  11. #11
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  12. #12

    Default

    Quote Originally Posted by johnfrwhipple
    I'm not impressed the new guy wants to start a thread with my name in it. Pretty bad forum in my book.
    Like I said , John , I thought it is the proper way IMO to exchange opinions , not over other members threads , especially when nothing we discuss is relevant to it .

    My bad , if having your name in thread's title offends you . I will inquire the moderators to rename it .

  13. #13
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,986
    Blog Entries
    5

    Default More answers for Roberto

    Post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-15-2014 at 03:33 PM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  14. #14
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    The problem is the fact that your flood tests are only done with 1"-2" of water. This is not enough head to test that connection. It is just like DWV piping should never be full of water, but is still needs to be tested with a minimum of a 10' water column. Unless you plug the drain and re-do the full (or isolated to that section) test on the DWV system, you aren't testing that joint in the eyes of the plumbing code. As such, either test plug accomplishes the same thing: allows the flood test to be performed, but does nothing to test the no-hub joint.

    So, if Roberto is showing half-steps or incomplete steps, you are guilty of the same as neither plug actually tests the connection in this configuration.

    All of the personal attacks are getting old. The fact is that no-one has all of the answers. You should be open to other people's opinions as you might just learn something new. You don't have to be a "pro" to know the codes or what the manufacturer recommends. Where what you do really comes in to play is with feedback as to which systems work and which ones don't since you have the opportunity to use multiple methods. Feedback based on this is helpful to everyone (such as the shear testing).

  15. #15

    Default

    Quote Originally Posted by johnfrwhipple View Post
    By now the thread is long since crawled by goggle. Likewise this one. Leave them be. If you want to chat with me - use this thread. It's yours. has your name on it. Much better this way.
    No chatting necessary . You have your ways , which seem to change at different steps of a discussion , and I have my ways .

    Besides the misleading thread's name -- Never requested any waterproofing answers -- , no problem from my end .

    On a last note , deleting or removing answers from a different thread , really , makes it hard to follow .

Similar Threads

  1. AS3740 Waterproofing Showers
    By johnfrwhipple in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 03-31-2014, 06:43 AM
  2. Replies: 15
    Last Post: 01-08-2014, 09:18 AM
  3. Replies: 1
    Last Post: 05-30-2013, 08:16 PM
  4. waterproofing under tub
    By tbb2 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 01-11-2013, 05:11 PM
  5. Waterproofing a free standing tub surround. A look at various waterproofing options.
    By johnfrwhipple in forum Shower & bathtub Forum & Blog
    Replies: 0
    Last Post: 08-01-2011, 08:23 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •